shrines
Your Parameters are not set correct,, the RS485 is independent of the drive Parameters, here is what you need for your VFD Parameters,Do a Factory ReSet, ( Default settings ) then use these Parameters
How do you have your VFDs input power wired, and what country,Photo of this will eliminate this part,
Huanyang Mactec54
PD000=0 for Parameter unlock ( 1 ) for Parameter Lock
PD001=0 (1 For Remote Control)
PD002=0
PD003=400
PD004=400
PD005=400
PD007=20
PD008=220
PD009=15
PD010=8
PD011=120 (Minimum Setting 120)
PD13= 08 is for Factory reset, Only use this to set VFD to Factory Default Settings
PD014 Accel=12 ( Adjust to suit)
PD015 Deccl=12 (Adjust to suit) ( PD15 is ignored IF PD26=1 Then the Spindle will Coast to a Stop)
PD141=220 ( Motor Rated Voltage ) (120 for VFD Rated for 120v )
PD142=9 ( Motor Max Amps) (Set for your motor Amp Rating 2.2Kw Spindle 9 amp Max)
(Set for your motor Amp Rating 1.5Kw Spindle 7 amp Max)
PD143=2 ( Motor Number of Poles)
PD144=3000 (Max Motor RPM) =3,000= (24,000)
PD002=1 ( For Remote Pot use )
PD70=0
PD72=400
PD73=120