The AMC have an internal jumper that will configure the Enable active hi or low.
In the default condition you can use a N.C. contact.
The AC neutral and all DC commons normally have their own common terminal strip but these should have a conductor connected to the star point ground block.
An important thing is to ground or bond motor frames and moving parts of the machine to this block.
The siemens PDF is a good ref for the bonding practice.
http://www.automation.siemens.com/do.../emv_r.pdf?p=1
Ground Practices
If you read section 6 of the sieimens PDF, they advise a common current recommendation of grounding both ends of a shielded cable when proper bonding practice is observed.
Al.