Hi,
This is a common problem and most newcomers to the field are flabbergasted at the (electrical) power required to drive a spindle motor and evenMy biggest concern is how to operate it's 2 speed 3 phase motor on single phase power. The motor is rated at 2.5hp/4.5hp
more preplexed at why it seems that VFDs require something like twice the input power compared to the motor that its supposed to drive.
You can get 2hp and 3hp single phase motors (230V) but they are big, double and more the size of a three phase motor of the same power and they have
VERY demanding start up input current. They are really expesive to boot.
I would suggest rather than replace the three phase motor with single phase you should follow up the idea of a RPC or a VFD.
VFD's can be supplied by single phase (230V) power but 2.2 kw or 3hp is about the practical limit. Even such a device could consume 20-30A from
a single phase supply and you will have to have a dedicated circuit with heavy duty wiring and fusing/circuit breakers to do it.
The upshot is that VFD's are high speed switching devices and the distortion caused by the extremely discontinuous current demand results
in power factors as low as 0.5. That means that you could put in 1kW but only get 'effectively' 500W out. For low power devices such as hobby
machines such a low power factor is acceptable, after all we still don't use that much electricity.
In an industrial situation such a low power factor means expensive power bills and also the the power supply is 'polluted' by such a device. The
corrective procedure for VFD's, RPC's and big servo drives is the use of line reactors. They are big iron core coils, not dissimlar to a big
transformer, on the input side of the device. A good line reactor will increase the power factor to 0.8 to 0.9 ( 1.0 is the unobtainable pefect goal)
which saves money and prevents the power supply company getting on your case.
If you wish to use a VFD you will need one probably 4-5 kW. It would ideally be fed with three phase AC input but they will work, with a sufficent
de-rating, with single phase (230V) input. You will almost certainly be required to fit a big kick-arse line reactor otherwise your single phase supply
is going to blow up. You will need a dedicated circuit with an absolute minium of 30A, but better to have your electrician install wiring and breakers
to accomodate a 50A circuit.
Most necomers dissmiss the idea of having the power company install a three phase connection to your workshop as too expensive.
When you consider the cost of an outsized VFD, the cost of installing a 50A circuit and breakers and the cost of a good line reactor then suddenly
the cost of a three phase supply does not seem so extravagent any more.
I live in New Zealand and so the numbers I quote hereafter refer to NZD and the electrical standards are determined by NZ Standards. Having
said that, similar standards apply throughout the world, after all 'is it safe' is the same question asked everywhere.
When my house was rewired recently I investigated having a three phase supply. It was going to cost $1500, whereas the single phase supply cost
$680. The kicker was that if I wanted three phase I had to guaruntee a minimum supply period of five years and a minimum monthly energy
demand.
I reasoned that the single phase pole fuse and aerial lead-in are rated to 80A, and the power-meter and isolation breaker are rated to 63A which
meant I could have a dedicated 50A circuit if I was prepared to turn off things like my electric oven and hot water when I want to use my mill,
that would be adequte. I settled for a single phase supply which had no monthly energy demand requirement because I use very little electricity
overall.
To sum up, yes you can run your lathe with a single phase supply IF you are preapred to have a very heavy duty single phase circuit installed and equip
it with an out-sized VFD and line reactors.
The question is does the single phase solution cost as much, or worse, more than having three phase installed?
Craig