    Hi Dan,

    I loaded ver 16 and tried with different frequency addresses (0000 and 0001) and there are no changes. No rpm control. And I even tried to turn off frequency resolution and checked multiple coils. But no luck again.

    Today was a busy day and tomorrow I may try to use different computer.

    Still don't understand where the problem is. Is it that we have frequency register address wrong, or is it something else? I think that register address should be 0000h for 0001h register number. Is there something in the UCCNC that may be wrong set (checked spindle setting and PWM is checked, spindle pulley is not checked)?

    Thanks,
    Milosh



  2. #142
    Member
    Join Date
    Mar 2010
    Location
    America
    Posts
    813
    Downloads
    0
    Uploads
    0

    Default Re: New MODBUSEZ SetUp Plugin For UCCNC

    Hi Milosh,

    The settings I previously posted should of worked. The frequency resolution box needs to be checked for the WJ200, and frequency needs to be sent as a single holding register per manual and settings above will do this. The Wj200 Modbus parameter settings are easily found with a google search so I'm assuming these are set correctly.

    99.9% of times when helping trouble shoot ModbusEZ or Huanyang plugin the RS485 converter was the problem. This can be checked easily with a free or trial Serial Port Monitor and see if WJ200 is reading and replying. I post a link for a trial version SPM below.

    https://www.eltima.com/products/serial-port-monitor/


    Dan



  3. #143
    Registered
    Join Date
    Sep 2006
    Location
    Canada
    Posts
    32
    Downloads
    0
    Uploads
    0

    Default

    Quote Originally Posted by Dan911 View Post
    Hi Milosh,

    The settings I previously posted should of worked. The frequency resolution box needs to be checked for the WJ200, and frequency needs to be sent as a single holding register per manual and settings above will do this. The Wj200 Modbus parameter settings are easily found with a google search so I'm assuming these are set correctly.

    99.9% of times when helping trouble shoot ModbusEZ or Huanyang plugin the RS485 converter was the problem. This can be checked easily with a free or trial Serial Port Monitor and see if WJ200 is reading and replying. I post a link for a trial version SPM below.

    https://www.eltima.com/products/serial-port-monitor/


    Dan
    Hi Dan,

    I don't think adapter is an issue. It works with other computer under mach. WJ200 setting is unchanged as well. Only difference between this setup and old one is uccnc and modbus driver.

    Thanks,
    Milosh



  4. #144
    Member
    Join Date
    Mar 2010
    Location
    America
    Posts
    813
    Downloads
    0
    Uploads
    0

    Default Re: New MODBUSEZ SetUp Plugin For UCCNC

    Could you post the settings/brains used for Mach3, that will certainly make easier to match.

    Dan



  5. #145
    Member ger21's Avatar
    Join Date
    Mar 2003
    Location
    Shelby Township
    Posts
    35538
    Downloads
    1
    Uploads
    0

    Default Re: New MODBUSEZ SetUp Plugin For UCCNC

    I don't think adapter is an issue. It works with other computer under mach.
    Lot's of other have found the same to be true. For whatever reason, the adapters would work in Mach, but not UCCNC.

    Gerry

    UCCNC 2017 Screenset
    [URL]http://www.thecncwoodworker.com/2017.html[/URL]

    Mach3 2010 Screenset
    [URL]http://www.thecncwoodworker.com/2010.html[/URL]

    JointCAM - CNC Dovetails & Box Joints
    [URL]http://www.g-forcecnc.com/jointcam.html[/URL]

    (Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management)


  6. #146
    Member
    Join Date
    Mar 2010
    Location
    America
    Posts
    813
    Downloads
    0
    Uploads
    0

    Default Re: New MODBUSEZ SetUp Plugin For UCCNC

    Using posted settings the snip pic below shows what plugin is sending to Serial Port on UCCNC startup.


    01 05 00 00 00 00 cd ca

    01 = Modbus address

    05 = Modbus function (write to single coil)

    00 00 = Hi/lo coil being written to.

    00 00 = what's being written to coil (off)

    cd ca = checksum

    ///////////////////////////////////////////////////////////

    Write to VFD for frequency


    01 06 00 01 20 8d 01 af

    01 = Modbus address

    06 = Modbus function (single holding register)

    00 01 = hi/lo register being written to.

    20 8d = hi/lo what's being written to register 00 01 (20 8d hex = 8333 decimal) 8333HZ = 5000rpm

    01 af = checksum



    So if I seen what was working I could decipher where the problem is.

    Attached Thumbnails Attached Thumbnails New MODBUSEZ SetUp Plugin For UCCNC-startup-jpg  


  7. #147
    Member
    Join Date
    Mar 2010
    Location
    America
    Posts
    813
    Downloads
    0
    Uploads
    0

    Default Re: New MODBUSEZ SetUp Plugin For UCCNC

    Quote Originally Posted by ger21 View Post
    Lot's of other have found the same to be true. For whatever reason, the adapters would work in Mach, but not UCCNC.
    Hi Gerry,

    I think the converter is barely working in Mach3 like it's barley working in UCCNC. He is able to turn spindle on/off with UCCNC.

    Where the problem is is when using the plus / minus or slider like in your screenset for override some of these cheap converters can't handle the speed the plugin is sending many different frequency's at.

    Dan

    A Serial Monitor dump view will show this.



  8. #148
    Registered
    Join Date
    Sep 2006
    Location
    Canada
    Posts
    32
    Downloads
    0
    Uploads
    0

    Default Re: New MODBUSEZ SetUp Plugin For UCCNC

    Hi Dan,

    Thanks for the link. Here are some snapshots of the port. Beside rs232 to rs485 (com1). I have as well usb to rs485, so I tried with this one as well (com4).

    COM1

    New MODBUSEZ SetUp Plugin For UCCNC-com1-monitoring-session-jpg

    and COM4

    New MODBUSEZ SetUp Plugin For UCCNC-com4-monitoring-session-jpg

    Just to be seen if there is any difference.

    Attached are two files saved from monitoring program.


    Milosh

    p.s. It is not a problem to order some confirmed converter. Any suggestions?

    Attached Files Attached Files


  9. #149
    Member
    Join Date
    Mar 2010
    Location
    America
    Posts
    813
    Downloads
    0
    Uploads
    0

    Default Re: New MODBUSEZ SetUp Plugin For UCCNC

    Hi Milosh,

    When you start a session with serial monitor could you please just check dump view for pics?

    The zip file you attached won't extract says file corrupt so I can't load.

    Thanks,
    Dan



  10. #150
    Registered
    Join Date
    Sep 2006
    Location
    Canada
    Posts
    32
    Downloads
    0
    Uploads
    0

    Default Re: New MODBUSEZ SetUp Plugin For UCCNC

    Here it is Dan,

    New MODBUSEZ SetUp Plugin For UCCNC-com4-monitoring-session-jpg

    and here is the file

    Please change the extension to SPM.

    Thanks
    Milosh

    Attached Files Attached Files


  11. #151
    Member
    Join Date
    Mar 2010
    Location
    America
    Posts
    813
    Downloads
    0
    Uploads
    0

    Default Re: New MODBUSEZ SetUp Plugin For UCCNC

    Hi Milosh,

    Thanks! Your snip tells a lot, not owning a WJ200 I don't have the opportunity to read response from the wj200 and can only go by manual and others.

    Your RS485 converter is working perfectly and you can see every line written to vfd it is responding to.

    The Wj200 is accepting the on/off byte array (05) but it is NOT accepting the holding register for frequency(06). Once we determine why I'm absolutely sure we can make it work. According to manual frequency is sent with a single holding register but obviously not working, I can give you a few things to try, but if your able to provide a Serial Port Monitor dump view like the 1 you just posted with UCCNC with Mach3 it will take away any guessing to where problem is when able to see what works.

    Thanks,
    Dan



  12. #152
    Member
    Join Date
    Mar 2010
    Location
    America
    Posts
    813
    Downloads
    0
    Uploads
    0

    Default Re: New MODBUSEZ SetUp Plugin For UCCNC

    Ok...lets put aside how Mach3 is working and look at Serial Port data you posted and manual.

    ModbusEZ sent holding register to set rpm to 5000 "01 06 00 01 20 8d checksum"

    VFD responded with "01 86 22 checksum"............... 86 function and 22 code.


    I think to resolve this is in your parameter settings with WJ200. See attached pic and following post.

    Dan

    Attached Thumbnails Attached Thumbnails New MODBUSEZ SetUp Plugin For UCCNC-exception-jpg  


  13. #153
    Member
    Join Date
    Mar 2010
    Location
    America
    Posts
    813
    Downloads
    0
    Uploads
    0

    Default Re: New MODBUSEZ SetUp Plugin For UCCNC

    I think changing parameter setting to "A001 = 2" or leave A001 = 3 and look at b031 parameter and change to 3 or 10. I took some snips from WJ200 manual and highlighted important values.

    You can also post Mach3 settings that been working for me look at so I can guide you to those matched settings.

    Attached Thumbnails Attached Thumbnails New MODBUSEZ SetUp Plugin For UCCNC-a001-jpg   New MODBUSEZ SetUp Plugin For UCCNC-b031-jpg   New MODBUSEZ SetUp Plugin For UCCNC-manual1-jpg   New MODBUSEZ SetUp Plugin For UCCNC-f001-jpg  



  14. #154
    Registered
    Join Date
    Sep 2006
    Location
    Canada
    Posts
    32
    Downloads
    0
    Uploads
    0

    Default Re: New MODBUSEZ SetUp Plugin For UCCNC

    Dan,

    You and I are thinking same thing. I connected to the VFD via Hitachi software and was able to set the rpm. It was good - it means that VFD is not faulty. Then I changed one of the parameters and saved it and then put back the same parameter and saved it and tried. And I have control of the rpm. YES. I am able to control the RPM.

    At the end of this story, as you mentioned, something changed in the VFD and by simply uploading setup file everything started to work.

    Dan, you are the MAN. First, big thank you for writing this driver, and then thank you very much for walking me through this and helping me to find a solution.

    Milosh

    p.s. Dan you' got a PM

    BTW is a nice setup of WJ200.

    Last edited by yham; 06-27-2018 at 11:12 PM.


  15. #155
    Registered
    Join Date
    Oct 2014
    Posts
    41
    Downloads
    0
    Uploads
    0

    Default Re: New MODBUSEZ SetUp Plugin For UCCNC

    Does anyone actually have modbusez working with a delta VFD-M inverter (3HP)? It seems to do nothing for me. I've set Pr. 0 to 3 (RS485), Pr.1 to 3 (rs485), pr 88 to 01 (bus address), pr 89 to 1 (COM speed 9600), pr 92 to 03 (MODBUS RTU-8N2 protocol), pr. 157 to 1 (using modbus communication). On the modbus ez software, it sets to single holding register, on/off address 2000, freq address 2001, spindle on cw 0012 (according my manual), spindle on ccw 0022, spindle off 0001. I'm using a CH340T USB serial adapter( JBtek USB to RS485 Converter Adapter from Amazon). COM2/9600/8N2 on the port setting. Windows 10 recognizes the USB converter just fine.

    I'm not sure where the prolem is. It could be the physical cable (I tested the two pins from the VFD and there was a DC voltage of about 4.5V between the two leads). It could be the VFD config, or modbusez itself. I've used the serial port monitor software and could not see modbusez doing anything during start up or after with the port.

    Right now, I have it working fine with the traditional +10V PWM. I just hope to set the freq via modbusez and get the actual RPM back into the software. I'm not sure if modbus is suitable to be completely integrated into the safety circuit.

    Last edited by javabugz; 09-16-2018 at 07:53 PM.


  16. #156
    Member
    Join Date
    Mar 2010
    Location
    America
    Posts
    813
    Downloads
    0
    Uploads
    0

    Default Re: New MODBUSEZ SetUp Plugin For UCCNC

    Quote Originally Posted by javabugz View Post
    Does anyone actually have modbusez working with a delta VFD-M inverter (3HP)? It seems to do nothing for me. I've set Pr. 0 to 3 (RS485), Pr.1 to 3 (rs485), pr 88 to 01 (bus address), pr 89 to 1 (COM speed 9600), pr 92 to 03 (MODBUS RTU-8N2 protocol), pr. 157 to 1 (using modbus communication). On the modbus ez software, it sets to single holding register, on/off address 2000, freq address 2001, spindle on cw 0012 (according my manual), spindle on ccw 0022, spindle off 0001. I'm using a CH340T USB serial adapter( JBtek USB to RS485 Converter Adapter from Amazon). COM2/9600/8N2 on the port setting. Windows 10 recognizes the USB converter just fine.

    I'm not sure where the prolem is. It could be the physical cable (I tested the two pins from the VFD and there was a DC voltage of about 4.5V between the two leads). It could be the VFD config, or modbusez itself. I've used the serial port monitor software and could not see modbusez doing anything during start up or after with the port.

    Right now, I have it working fine with the traditional +10V PWM. I just hope to set the freq via modbusez and get the actual RPM back into the software. I'm not sure if modbus is suitable to be completely integrated into the safety circuit.
    javabugz, post a link to your manual, I'm sure I can get you going or help determine where your trouble is.

    Dan



  17. #157
    Registered
    Join Date
    Oct 2014
    Posts
    41
    Downloads
    0
    Uploads
    0

    Default Re: New MODBUSEZ SetUp Plugin For UCCNC

    The manual can be found here https://www.automatedpt.com/wp-conte...ser-Manual.pdf

    Here is a page on the VFD from the manufacturer website https://www.deltaacdrives.com/delta-vfd022m21a/

    I updated the serial driver and was able to see activities from UCCNC (write) to the COM port but no response from the VFD. I suspect I got the wrong pins out for the signal. Initially, I was using the two center pins (SG+ and SG-) but I probably need to use pin 5 and 6. The output uses RJ12 plug and I did not have any on hand so I used RJ11 phone jack. Apparently, that's probably wrong.

    Does modbusez deal with writing error codes or reading error codes from the VFD? I'm not sure what the VFD would do if there is a fault in one of the motor (which would trigger an e-stop on my machine).



  18. #158
    Member
    Join Date
    Apr 2014
    Posts
    215
    Downloads
    27
    Uploads
    0

    Default Re: New MODBUSEZ SetUp Plugin For UCCNC

    it is not recommended to control the start and stop via modbus. Yes it can be done, but consider if you loose communication how will you stop the drive. It is better to have a hardwired run/stop control. FWD, REV & RPM can all be controlled via modbus fine.

    Have you checked your wiring, is the RJ11/RJ12 plug made off ok. Have you flipped the wiring around from +/-?
    Have you got termination resistors installed (120ohm or greater at each end)

    Nothing jumps out at me, but I'm no modbus expert.

    Some of the USB <> modbus devices have been reported as being defective (on occassion) and a new one normally sorts out the issue.... sometimes....

    You can read whatever you want error code wise, however you must remember that modbus is a MASTER + SLAVE protocol, ie, the master (PC in this case) will ask the slave for whatever it wants in a loop to fill the registers of the uccnc modbus plugin. The drive will not "TELL" the PC anything.... the PC will just read the data..... thats why I suggest (each to their own, as I know this has been discussed before at length) to use a hardwired link for run/stop

    Id wire it as SG+/SG- as when you look at the picture of the drive on 2-2 it shows 5&6 are reserved pins (for the remote display option?)



  19. #159
    Registered
    Join Date
    Oct 2014
    Posts
    41
    Downloads
    0
    Uploads
    0

    Default Re: New MODBUSEZ SetUp Plugin For UCCNC

    Thanks, robertspark. You are right about the SG+/SG- signal. I was able to get the communication going after replacing the usb adapter. I guess I'll be returning the faulty one. The serial port monitor shows communication R/W between the two but does not seem to activate the spindle. When doing a M3, I can hear the VFD fan started but spindle does not turn on.

    I attached a session dump (txt) file

    Attached Files Attached Files
    Last edited by javabugz; 09-17-2018 at 08:41 PM.


  20. #160
    Member
    Join Date
    Mar 2010
    Location
    America
    Posts
    813
    Downloads
    0
    Uploads
    0

    Default Re: New MODBUSEZ SetUp Plugin For UCCNC

    Hi Javabugz,

    I see from the serial monitor data you posted your using multiple registers set in Modbus configure and in ModbusEZ manual shows to use single holding. I also see using multiple register it's sending 00 00 for frequency.That would be why you hear VFD click on but not spinning. I'm fairly certain something is not configured correctly.

    If your able to post a screen pic of your Modbus EZ settings and post your .pro file in UCCNC I will be able to get to the bottom and narrow down your problem a lot quicker.

    Dan



Page 8 of 10 FirstFirst ... 5678910 LastLast

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

New MODBUSEZ SetUp Plugin For UCCNC

New MODBUSEZ SetUp Plugin For UCCNC