    Default Okuma LB-15 w/ OSP5000L-G Alarm Code 108

    Howdy everyone,

    Having an issue with an Okuma LB-15 lathe with OSP5000L-G control unit. Was wondering if anyone had ever encountered similar.

    The machine boots fine; however it displays alarm code 108. I understand that's commonly an emergency stop code, however I've confirmed that the emergency stop on the control panel is in working condition (by taking the front panel off and doing a continuity test on it). The emergency stop is not engaged and the alarm code does not go away on reset.
    I figured it might be a bad relay in such an old machine, so I dug through the diagrams and found that relay CR3A switches the bit referred to by the alarm code book that sets the alarm. I tested the relay and can confirm that the coil and contacts are operating properly.

    I've heard it's possible that a module that's no longer present had been e-stopped before being disconnected. Is it actually the case that such a thing would not be normally resettable? And if so, what's a possible solution?

    Thanks!



  2. #2
    Ourindar's Avatar
    Join Date
    Jun 2019
    Posts
    2
    Downloads
    0
    Uploads
    0

    Default

    Just wanted to give an update to this thread in case anyone else ever had a similar issue.

    I fixed the issue, and the machine no longer gives the alarm code.
    The bar feeder interface connects to a circular Amphenol connector port on the left side panel of the machine, underneath the serial, parallel, and 110V out ports. After consulting a bar feeder electrical diagram, I bridged pins R and S of the connector with a jumper wire. These are the emergency stop pins for the bar feeder interface (and presumably anything else that connects on that side).



  3. #3
    Operator11's Avatar
    Join Date
    Jul 2019
    Posts
    5
    Downloads
    0
    Uploads
    0

    Default

    Hello, i have some questions to you and i think that you maybe can help me. Please contact with me by email dariusimaitis@gmail.com



Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

Okuma LB-15 w/ OSP5000L-G Alarm Code 108

Okuma LB-15 w/ OSP5000L-G Alarm Code 108