    I have a Journeyman 325 with Dynapath Delta 20 control that I bought a few years ago. It was functional up until mid-December last year; good one day, the following day could not get the drives to start up using the Reset button on control. I am running power from a 10HP RPC that came with the machine from previous owner, where the outputs are about 240V for the two pass-through legs, and about 265V for the generated leg. This machine has the input power separated between control and servo cabinet, so that the control cabinet uses the two 240V pass-throughs and the servo cabinet sees all three legs, entering through the 3-phase input circuit breaker on the machine. It appears that the 3-phase breaker is tripping immediately at startup of the machine, which would seem to be the reason the servos won't start from the Reset function.

    The circuit beaker is a shunt-trip unit, with a couple of wires running 24V from "somewhere" to the shunt coil. My main questions are these:
    -- What is the normal state of the shunt-trip coil when in operation, energized or non-energized? My assumption is that it should not be energized, but that is just that - an assumption.
    -- What is the immediate upstream source for the 24V that feeds the shunt-trip coil? My documentation for this machine is not as complete as I would like.

    The power being supplied appears to be over the tolerance for the machine specs, at least for the generated leg, and I need to address that. It may be the cause for the problem, but I would like to eliminate as many ancillary components as possible from the list. Replacing the circuit breaker is about a $600 exercise, from what I've gotten from electrical distributors, so not an easy experiment. Any help appreciated --

    Similar Threads:


  2. #2
    Member machinehop5's Avatar
    Join Date
    Aug 2009
    Location
    United States
    Posts
    1570
    Downloads
    5
    Uploads
    2

    Default Re: J325 with Dynapath 20 - control OK, servos won't start

    ...may want to check your VFD for dead short with meter. or try disconnecting the VFD than see if, the breaker trips



  3. #3
    Member
    Join Date
    Sep 2014
    Posts
    4
    Downloads
    0
    Uploads
    0

    Default Re: J325 with Dynapath 20 - control OK, servos won't start

    Quote Originally Posted by machinehop5 View Post
    ...may want to check your VFD for dead short with meter. or try disconnecting the VFD than see if, the breaker trips
    Thanks for the response -- At the risk of sounding like an idiot: I assume you are referring to a VFD within the Tree system(?) My input power is coming into the Tree from a rotary phase converter. If this is an onboard VFD, is it labeled as such on the typical Tree schematics?



  4. #4
    Member machinehop5's Avatar
    Join Date
    Aug 2009
    Location
    United States
    Posts
    1570
    Downloads
    5
    Uploads
    2

    Default Re: J325 with Dynapath 20 - control OK, servos won't start

    ...yes, the Variable Frequency Drive aka Spindle Drive is the only thing besides the Coolant Pump that is 3 PH.

    Attached Files Attached Files


  5. #5
    Community Moderator Jim Dawson's Avatar
    Join Date
    Dec 2013
    Posts
    5717
    Downloads
    0
    Uploads
    0

    Default Re: J325 with Dynapath 20 - control OK, servos won't start

    Energized trips the breaker. I have the same thing on one of my machines as a safety lockout, trips the breaker if the panel door is opened with out setting the bypass lockout. In my case I just disconnected it.

    Jim Dawson
    Sandy, Oregon, USA


  6. #6
    Member
    Join Date
    Sep 2014
    Posts
    4
    Downloads
    0
    Uploads
    0

    Default Re: J325 with Dynapath 20 - control OK, servos won't start

    Thanks to both Jim Dawson and Machinehop5 -- I have yet to get back to this machine for additional troubleshooting, but your information is useful. The schematic Machinehop5 posted is indeed the one I have, and now I have at least some idea of what to try for the next steps.



Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

J325 with Dynapath 20 - control OK, servos won't start

J325 with Dynapath 20 - control OK, servos won't start