    i have a vfd huanyang HY02D243B
    Is it possible to switch off the inverter otherwise when unplugging the power ?
    with a particular setting ?

    Thanks
    best regards


    Iwan

    Similar Threads:


  2. #2
    Member CitizenOfDreams's Avatar
    Join Date
    Nov 2012
    Location
    USA
    Posts
    1267
    Downloads
    4
    Uploads
    0

    Default Re: huanyang vfd on/off

    The inverter is always "on" as long as it has AC power. The Stop mode turns off the output transistors, but the bus voltage is always on.



  3. #3
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: huanyang vfd on/off

    Quote Originally Posted by vanova View Post
    hi,
    i have a vfd huanyang HY02D243B
    Is it possible to switch off the inverter otherwise when unplugging the power ?
    with a particular setting ?

    Thanks
    best regards


    Iwan
    No there are no settings that can do that.

    You can't use a Plug to Turn the Power 0FF to the VFD Drive this is a big No as this will damage the VFD Drive

    It must be switched 0FF before you unplug it, meaning the outlet / receptacle has to have a switch to turn the power to the VFD Drive 0ff before you can unplug it, this can be done also with the Breaker for that circuit, Never unplug when it is Powered up

    Same goes for Powering it up, if you are Plugging it in then the Power must be 0FF before you Plug it in, you then can Switch / Turn it 0N

    Mactec54


  4. #4
    Member
    Join Date
    May 2010
    Location
    switzerland
    Posts
    6
    Downloads
    0
    Uploads
    0

    Default Re: huanyang vfd on/off

    Quote Originally Posted by mactec54 View Post
    No there are no settings that can do that.

    You can't use a Plug to Turn the Power 0FF to the VFD Drive this is a big No as this will damage the VFD Drive

    It must be switched 0FF before you unplug it, meaning the outlet / receptacle has to have a switch to turn the power to the VFD Drive 0ff before you can unplug it, this can be done also with the Breaker for that circuit, Never unplug when it is Powered up

    Same goes for Powering it up, if you are Plugging it in then the Power must be 0FF before you Plug it in, you then can Switch / Turn it 0N

    Thanks for your repply,
    i'm little bit confuse ,, but just for resume i can use a Breacker (for power switch) and be sure that te VFD is on STOP mode before switching OFF the breacker ?

    huanyang vfd on/off-vfd-png



  5. #5
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: huanyang vfd on/off

    Quote Originally Posted by vanova View Post
    Thanks for your repply,
    i'm little bit confuse ,, but just for resume i can use a Breacker (for power switch) and be sure that te VFD is on STOP mode before switching OFF the breacker ?

    huanyang vfd on/off-vfd-png
    The word you used in your post Plugging, is I think is where the confusion came from, Plugging means you are plugging something into a power outlet.

    Are you using 3Phase or Single-Phase supply??

    That is a 3 Pole Breaker, you need a Ground / Earth wire (PE) also for the VFD Drive and the Spindle.

    The spindle must use a 4 wire Shielded cable Between the VFD Drive and the Spindle.

    Normally if you are using 3Phase Power supply you would use a minimum of a Main Power Supply Disconnect in your machine cabinet, the Breaker would be used after the disconnect, then an EMI Power Filter then the VFD Drive

    Attached Thumbnails Attached Thumbnails huanyang vfd on/off-disconnect-switches-3-png   huanyang vfd on/off-disconnect-switches-4-png   huanyang vfd on/off-vfd-drive-wiring-png  
    Mactec54


  6. #6
    Member
    Join Date
    May 2010
    Location
    switzerland
    Posts
    6
    Downloads
    0
    Uploads
    0

    Default Re: huanyang vfd on/off

    Quote Originally Posted by mactec54 View Post
    The word you used in your post Plugging, is I think is where the confusion came from, Plugging means you are plugging something into a power outlet.

    Are you using 3Phase or Single-Phase supply??

    That is a 3 Pole Breaker, you need a Ground / Earth wire (PE) also for the VFD Drive and the Spindle.

    The spindle must use a 4 wire Shielded cable Between the VFD Drive and the Spindle.

    Normally if you are using 3Phase Power supply you would use a minimum of a Main Power Supply Disconnect in your machine cabinet, the Breaker would be used after the disconnect, then an EMI Power Filter then the VFD Drive
    I use 3 Phase supply,
    sorry for the confusion, I speak french,,,
    is this diagram correct? (better than words )

    and do you have suggestion for EMI filter, i use a 380v 2,2kw Spindle ?

    huanyang vfd on/off-cnc-wiring-jpg



  7. #7
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: huanyang vfd on/off

    Quote Originally Posted by vanova View Post
    I use 3 Phase supply,
    sorry for the confusion, I speak french,,,
    is this diagram correct? (better than words )

    and do you have suggestion for EMI filter, i use a 380v 2,2kw Spindle ?

    huanyang vfd on/off-cnc-wiring-jpg
    The switch would be the first in line before the Breaker if you have this mounted in a cabinet, the Main 400v supply would normally have a Breaker in the service Panel, then the Main Power supply would go to your machine Cabinet

    EMI Power Filters you can find in most electrical supply companies, or Ebay has them also a 380/400v 12A to 20A should be all you need the TDK Lambda being one of the better EMI Filters there are some used on Ebay as well buy with caution

    Don't forget your Neutral and Earth wires

    Attached Thumbnails Attached Thumbnails huanyang vfd on/off-emi-power-filter-2-png   huanyang vfd on/off-emi-power-filter-3-jpg   huanyang vfd on/off-3phase-panel-png  
    Mactec54


Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

huanyang vfd on/off

huanyang vfd on/off