    Default Huanyang VDF E.o.L.A/E.o.L.d Error

    Hello guys,

    I am new to the group and I am facing an issue with my new huanyang VFD

    The spindle is: 400Hz, 24000 rpm, 1.5Kw, 8A, 110V. 3phases 2 poles

    VFD MODEL: HY01D511B, 110V-110V, 1.5KW, 13A


    The first time I tried to run the spindle, the spindle turned for like 15 minutes and then stops, VDF shows E.o.L.A error

    I tried these settings before:

    PD001 = 1
    PD002 = 1
    PD003 = 400 = Main frequency
    PD004 = 400 = Base frequency
    PD005 = 400 = Max operating frequency
    PD006 = 3.0 = Intermediate frequency
    PD008 = 110 = Max voltage
    PD009 = 7.5 = Intermediate voltage
    PD010 = 4 = Min voltage
    PD011 = 120 = Frequency lower limit
    PD070 = 1 = Analog input
    PD072 = 400 = Higher analog frequency
    PD141 = 110 = Rated motor voltage
    PD142 = 7 = Rated motor current [motor says 8A] – Setting won’t go any higher than 7
    PD143 = 2 = Number of motor poles
    PD144 = 3000

    After these parameters, I got others which are a bit similar to the first ones but I now get the E.o.L.d error

    PD001 = 1
    PD002 = 1
    PD003 = 400
    PD004 = 400
    PD005 = 400
    PD006 = 3.0
    PD007 = 20
    PD008 = 110
    PD009 = 7.5
    PD010 = 4
    PD011 = 120
    PD014 = 10
    PD015 = 10
    PD070 = 1
    PD072 = 400
    PD073 = 120
    PD120 = 100
    PD141 = 110
    PD142 = 7
    PD143 = 2
    PD144 = 3000

    Can anyone help me to ensure I have the right parameters set.

    Thank you.

    Similar Threads:


  2. #2
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang VDF E.o.L.A/E.o.L.d Error

    Quote Originally Posted by 00chris View Post
    Hello guys,

    I am new to the group and I am facing an issue with my new huanyang VFD

    The spindle is: 400Hz, 24000 rpm, 1.5Kw, 8A, 110V. 3phases 2 poles

    VFD MODEL: HY01D511B, 110V-110V, 1.5KW, 13A


    The first time I tried to run the spindle, the spindle turned for like 15 minutes and then stops, VDF shows E.o.L.A error

    I tried these settings before:

    PD001 = 1
    PD002 = 1
    PD003 = 400 = Main frequency
    PD004 = 400 = Base frequency
    PD005 = 400 = Max operating frequency
    PD006 = 3.0 = Intermediate frequency
    PD008 = 110 = Max voltage
    PD009 = 7.5 = Intermediate voltage
    PD010 = 4 = Min voltage
    PD011 = 120 = Frequency lower limit
    PD070 = 1 = Analog input
    PD072 = 400 = Higher analog frequency
    PD141 = 110 = Rated motor voltage
    PD142 = 7 = Rated motor current [motor says 8A] – Setting won’t go any higher than 7
    PD143 = 2 = Number of motor poles
    PD144 = 3000

    After these parameters, I got others which are a bit similar to the first ones but I now get the E.o.L.d error

    PD001 = 1
    PD002 = 1
    PD003 = 400
    PD004 = 400
    PD005 = 400
    PD006 = 3.0
    PD007 = 20
    PD008 = 110
    PD009 = 7.5
    PD010 = 4
    PD011 = 120
    PD014 = 10
    PD015 = 10
    PD070 = 1
    PD072 = 400
    PD073 = 120
    PD120 = 100
    PD141 = 110
    PD142 = 7
    PD143 = 2
    PD144 = 3000

    Can anyone help me to ensure I have the right parameters set.

    Thank you.
    Messing with fire, Parameters are incorrect, do not run it with the Parameters set like this, I will give you some to change this
    PD006
    PD009
    PD0010

    Check the wiring at the spindle plug that they have good connections, all 3 Phases must be connected, and each wire is protected from each other

    Do you have the Ground connected the 4th pin must be connected and the 4th pin has Continuity to the spindle body

    Input wiring to the VFD Drive need a Photo to check that that is correct, you must be connected to R and T plus Ground for single Phase Use on this VFD Drive

    Mactec54


  3. #3
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang VDF E.o.L.A/E.o.L.d Error

    Quote Originally Posted by 00chris View Post
    Hello guys,

    I am new to the group and I am facing an issue with my new huanyang VFD

    The spindle is: 400Hz, 24000 rpm, 1.5Kw, 8A, 110V. 3phases 2 poles

    VFD MODEL: HY01D511B, 110V-110V, 1.5KW, 13A


    The first time I tried to run the spindle, the spindle turned for like 15 minutes and then stops, VDF shows E.o.L.A error

    I tried these settings before:

    PD001 = 1
    PD002 = 1
    PD003 = 400 = Main frequency
    PD004 = 400 = Base frequency
    PD005 = 400 = Max operating frequency
    PD006 = 3.0 = Intermediate frequency
    PD008 = 110 = Max voltage
    PD009 = 7.5 = Intermediate voltage
    PD010 = 4 = Min voltage
    PD011 = 120 = Frequency lower limit
    PD070 = 1 = Analog input
    PD072 = 400 = Higher analog frequency
    PD141 = 110 = Rated motor voltage
    PD142 = 7 = Rated motor current [motor says 8A] – Setting won’t go any higher than 7
    PD143 = 2 = Number of motor poles
    PD144 = 3000

    After these parameters, I got others which are a bit similar to the first ones but I now get the E.o.L.d error

    PD001 = 1
    PD002 = 1
    PD003 = 400
    PD004 = 400
    PD005 = 400
    PD006 = 3.0
    PD007 = 20
    PD008 = 110
    PD009 = 7.5
    PD010 = 4
    PD011 = 120
    PD014 = 10
    PD015 = 10
    PD070 = 1
    PD072 = 400
    PD073 = 120
    PD120 = 100
    PD141 = 110
    PD142 = 7
    PD143 = 2
    PD144 = 3000

    Can anyone help me to ensure I have the right parameters set.

    Thank you.
    PD006=260

    PD007=20

    PD008=110

    PD009=71.5

    PD010=5.5

    PD120= 100 to 120

    Most of your problem I think is wiring or you Power supply to the VFD Drive, it should have run with the Parmeter's you had set in the first lot.

    What is your spindle manufacture as others have been have trouble with one of the spindle brands??

    PD007 and PD010 work together as does PD006 and PD009, the V/Hz ratio must match, when using these Parameters, they can be left at Default and can still run your spindle ok

    Mactec54


Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

Huanyang VDF E.o.L.A/E.o.L.d Error

Huanyang VDF E.o.L.A/E.o.L.d Error