What is your PD 071 (Analog Filtering) set to? Try increasing it.
speed shown on VFD display does not match that set on UCCNC.
- UCCNC set to 6,000 RPM - VFD Display fluctuates constantly from 10,300 up to 10,900 then down. ( Analog voltage on board 2.62V)
- UCCNC set to 12,000 RPM - VFD Display fluctuates constantly from 14,200 up to 15,200 then down. ( Analog voltage on board 4.87V)
- UCCNC set to 24,000 RPM - VFD Display without fluctuation 22,812 ( Analog voltage on board 9.33V)
The 10V supply from the VDF reads out 9.97V at the controller board (UB1), so did a little experiment and provided 10.2V by independent PS. This didn't really helped.
- UCCNC set to 24,000 RPM - VFD Display without fluctuation 23,028 ( Analog voltage on board 9.46V)
The VFD I have is HY02D223B coupled to a 400Hz spindle 220v - 2.2W water cooled.
PD settings on the VFD:
Jumper set on connection 1 & 2 for remote terminal control
PD001 1 PD002 1 PD003 400 PD004 400 PD005 400 PD007 20 PD008 220 PD009 15 PD010 11 PD011 100 PD014 10 PD015 10 PD041 8 PD052 1 PD070 0 PD072 400 PD073 100 PD120 100 PD141 220 PD142 9 PD143 2 PD144 3000
What could be causing this variation in speeds?
Thanks in advance!
Similar Threads:
What is your PD 071 (Analog Filtering) set to? Try increasing it.
PD 071=20
Tried 30,35,40,50 and no real change, issue remains.
I also tried having a dedicated shielded cable for the 10v, 0v, and analog signal from controller board to vfd but issue remains. Thought it was a noise issue because of how the speed increases then decreases then increases and so on.
I checked the settings on UCCNC for the PWM frequency and was set to 400 hz while the manual for the bob (ub1) recommeneded 1524 hz so I used this value. This change helped getting ride of the variable speeds. When set to 12,000 on uccnc, vfd now reads 15144 then goes up to 15 162rmp for a second then down to 15 144. This small variation is acceptable but how can i tweak the settings to get 12 000 rpm at the vfd when that value is set on uccnc?
Last edited by Phil_Par; 07-12-2022 at 09:09 PM.
Hello. Did you ever figure this out?
I'm having the same issue and was hoping for a pointer...
I'm starting to believe its a bad VFD, but everything is running as it should other then the speed.
Local control, the speed is steady as a rock. Remotely, its fluctuating nearly 2,000rpms.
Thanks
Thread: https://www.cnczone.com/forums/spind...ng-speeds.html
My Build: http://www.cnczone.com/forums/diy-cnc_router_table_machines/113711-my_build_-_many_thanks.html
Hi Mac, thanks.
I have some new cabling coming and will tidy up my wiring a little better.
I'm currently using two shielded 18/4 cables. One dedicated to relay, one dedicated to speeds.
My VFD outputs 9.98v
From your pointers above, I'll try changing some of the settings.
Particularly, PD71 and the frequency setting to 100hz.
My Build: http://www.cnczone.com/forums/diy-cnc_router_table_machines/113711-my_build_-_many_thanks.html
Do you have the shields clamped to the Ground Plane, any unused wires in a cable have to be Grounded at both ends or you can have interference problems, so you would be better to use just the (1) cable and correctly terminate the Shield, a P-Clip is better than a saddle which you can make yourself, but must clamp tight around the shield
PD071 is a Filter and does not have anything to do with 100Hz setting it has a setting range from 0-50 and changes the response time
The setting of this parameter is related to the analog responding speed. The higher the value of PD071 is set, the lower the analog responding speed will be. default is 20 and is not normally needed to be changed
Mactec54