    Default VFD output fluctuates, no max speed

    I’ve had my VFD running my spindle with manual speed control (panel potentiometer) for a while with no issue. I thought it would be useful to control the spindle speed using my Centroid Acorn controller 0-10V output.

    But, the speed fluctuates randomly and won’t go higher than about 20%. I’ve attached a video showing the behavior at 18,000 RPM (max) setting on the controller. Connections are per the attached diagram from Centroid.

    VFD is a Simphoenix E500 running an HQD 2.2kW spindle. I bought the hardware from https://www.automationtechnologiesinc.com/ and they have been helpful in verifying all VFD settings. The issue doesn’t seem to be with the Acorn, I have measured a steady 10.2V output at full RPM setting.



    Similar Threads:
    Attached Files Attached Files


  2. #2
    Member
    Join Date
    Jun 2005
    Location
    USA
    Posts
    1730
    Downloads
    0
    Uploads
    0

    Default Re: VFD output fluctuates, no max speed

    This type behavior is often caused because the wire size running from the Acorn to the VFD is to small of a gauge limited current. Make sure you have at least 22 AWG. The longer that cable normally require one wire gauge larger like 24 AWG. I have a VFD and acorn and had this problem

    Russ



  3. #3
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: VFD output fluctuates, no max speed

    Quote Originally Posted by kmagyoyo View Post
    I’ve had my VFD running my spindle with manual speed control (panel potentiometer) for a while with no issue. I thought it would be useful to control the spindle speed using my Centroid Acorn controller 0-10V output.

    But, the speed fluctuates randomly and won’t go higher than about 20%. I’ve attached a video showing the behavior at 18,000 RPM (max) setting on the controller. Connections are per the attached diagram from Centroid.

    VFD is a Simphoenix E500 running an HQD 2.2kW spindle. I bought the hardware from https://www.automationtechnologiesinc.com/ and they have been helpful in verifying all VFD settings. The issue doesn’t seem to be with the Acorn, I have measured a steady 10.2V output at full RPM setting.

    Sounds like Parameters not set correct, it should not be able to run at that speed.

    What Parameters have you set??

    Is the Voltage the same at the VFD Drive input 10.2v??

    Mactec54


  4. #4
    Member
    Join Date
    May 2018
    Location
    United States
    Posts
    85
    Downloads
    0
    Uploads
    0

    Default Re: VFD output fluctuates, no max speed

    24” wire to VFD from Acorn is a pair of 16 AWG wires so I don’t think it’s a voltage drop issue. Possibly shielding?

    I too suspect a parameter is out of whack but I have triple checked with what Simphoenix recommends.

    Parameters are set as follows (300 Hz spindle):

    F0.04= 300
    F0.05=10
    F0.06=10
    F0.11=0
    F0.12=300
    F0.13=220
    F1.00 =0
    F1.01 =10V
    F1.03=0
    F1.04 =300
    F1.08=11 ( Terminal X1 as a Run)
    F1.14=8 ( Inverter Fault signal Output)

    The Simphoenix manual shows 3 wires to the VFD 10V input, but I suspect that is in the case of a remote potentiometer rather than a 0-10V DC supply from the controller.




  5. #5
    Member cncmakers001's Avatar
    Join Date
    Jul 2011
    Location
    China
    Posts
    475
    Downloads
    1
    Uploads
    3

    Default Re: VFD output fluctuates, no max speed

    Is it similar to below spindle speed problem?
    How to correct actual speed of spindle

    http://cncmakers.com/cnc/controllers/CNC_Controller_System/CNC_Retrofit_Package.html


  6. #6
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: VFD output fluctuates, no max speed

    Quote Originally Posted by kmagyoyo View Post
    24” wire to VFD from Acorn is a pair of 16 AWG wires so I don’t think it’s a voltage drop issue. Possibly shielding?

    I too suspect a parameter is out of whack but I have triple checked with what Simphoenix recommends.

    Parameters are set as follows (300 Hz spindle):

    [FONT="]F0.04= 300[/FONT]
    [FONT="]F0.05=10[/FONT]
    [FONT="]F0.06=10[/FONT]
    [FONT="]F0.11=0[/FONT]
    [FONT="]F0.12=300[/FONT]
    [FONT="]F0.13=220[/FONT]
    [FONT="]F1.00 =0[/FONT]
    [FONT="]F1.01 =10V[/FONT]
    [FONT="]F1.03=0[/FONT]
    [FONT="]F1.04 =300[/FONT]
    [FONT="]F1.08=11 ( Terminal X1 as a Run)[/FONT]
    F1.14=8 ( Inverter Fault signal Output)

    The Simphoenix manual shows 3 wires to the VFD 10V input, but I suspect that is in the case of a remote potentiometer rather than a 0-10V DC supply from the controller.
    No, you don't need to worry about 3 wires, the 3rd wire is if the Board requires a 10v supply, and yours does not.

    Are the 0-10v wires Twisted pair??

    Simphoenix would not know what your spindle needs, I'm surprised that you did not damage the spindle with no minimum speed setting

    Try these settings not a lot of difference but it only takes (1) Parameter not set or be incorrectly set, to cause problems

    Mactec54

    F0.00=1 (F0.00=3 Keypad Potentiometer Control) (F0.00=1 0-10v Remote control)

    F0.01=300

    F0.02=1001 (F0.02=1 Run/Stop Keypad Control) (F0.02=1001 for Remote Terminal Control)

    F0.03= 120

    F0.04=300 (Max Motor Frequency)

    F0.05=5 To 8 (Adjustable Acceleration)

    F0.06=5 To 8 (Adjustable Deceleration)

    F0.07=1 (S-Curve for Acceleration and Deceleration)

    F0.12=300 (Motor Rated Frequency)

    F0.13=220 (Motor Rated Volts)

    F1.03=120

    F1.04=300

    F2.00=50

    F2.01=2

    F2.07= 100% (VFD Max Amps Match Spindle Max Amps Adjust Percentage to Suite)
    (If VFD Amps are More Than the Spindle Then the Percentage Must Be Adjusted to Suite)

    F2.19=1 (Number of Pole Pairs)

    F3.13=150%

    Mactec54


  7. #7
    Member
    Join Date
    May 2018
    Location
    United States
    Posts
    85
    Downloads
    0
    Uploads
    0

    Default Re: VFD output fluctuates, no max speed

    0-10V wires are not twisted pair, just 16 AWG stranded primary wire. Should they be twisted?

    Here’s the spindle nameplate (why do these forums always turn pics sideways??):

    VFD output fluctuates, no max speed-9c0cd22b-b458-4b34-91e6-ed57a234bb40-jpg

    Attached Thumbnails Attached Thumbnails VFD output fluctuates, no max speed-9c0cd22b-b458-4b34-91e6-ed57a234bb40-jpg  


  8. #8
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: VFD output fluctuates, no max speed

    Quote Originally Posted by kmagyoyo View Post
    0-10V wires are not twisted pair, just 16 AWG stranded primary wire. Should they be twisted?

    Here’s the spindle nameplate (why do these forums always turn pics sideways??):

    VFD output fluctuates, no max speed-9c0cd22b-b458-4b34-91e6-ed57a234bb40-jpg
    Either Twisted pair (like the Snip) or shielded and the shield terminated correctly.

    Not sure why the photos are sideways I don't have that problem.

    Attached Thumbnails Attached Thumbnails VFD output fluctuates, no max speed-cable-png  
    Mactec54


  9. #9
    Member
    Join Date
    May 2018
    Location
    United States
    Posts
    85
    Downloads
    0
    Uploads
    0

    Default Re: VFD output fluctuates, no max speed

    Problem solved.

    I noticed that when I moved the 0-10V wire while the spindle was running, the speed would change. I have chased EMI issues all along while building this machine, so I suppose I should have guessed that first.

    I twisted the wires and the speed is rock solid. Also adjusted the minimum input voltage…for whatever reason it’s not 0V at minimum speed from the Acorn. Actually it’s 3.6V so when I set the F1.00 to 3.6 I get the exact minimum frequency output of 100 Hz (to achieve specified 6,000 RPM minimum spindle speed).

    Thanks @mactec54, I did tweak a few of the settings as you suggested. I didn’t change F2.19 (currently at F2.19=2) and all seems to run fine. The spindle nameplate states 2 poles but the use of “pairs” is confusing. Should I still change that setting?



  10. #10
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: VFD output fluctuates, no max speed

    Quote Originally Posted by kmagyoyo View Post
    Problem solved.

    I noticed that when I moved the 0-10V wire while the spindle was running, the speed would change. I have chased EMI issues all along while building this machine, so I suppose I should have guessed that first.

    I twisted the wires and the speed is rock solid. Also adjusted the minimum input voltage…for whatever reason it’s not 0V at minimum speed from the Acorn. Actually it’s 3.6V so when I set the F1.00 to 3.6 I get the exact minimum frequency output of 100 Hz (to achieve specified 6,000 RPM minimum spindle speed).

    Thanks @mactec54, I did tweak a few of the settings as you suggested. I didn’t change F2.19 (currently at F2.19=2) and all seems to run fine. The spindle nameplate states 2 poles but the use of “pairs” is confusing. Should I still change that setting?
    Yes 2 Pole =1 Pair this needs to be set correct 4 Pole=2 Pair your spindle is 2 Pole so needs to be set to (1)

    Your spindle being air cooled just keep a check on the temperature at low speed as your minimum may be too low (100Hz) for an air-cooled spindle.

    Mactec54


  11. #11

    Default Re: VFD output fluctuates, no max speed

    Quote Originally Posted by kmagyoyo View Post
    Problem solved.

    I noticed that when I moved the 0-10V wire while the spindle was running, the speed would change. I have chased EMI issues all along while building this machine, so I suppose I should have guessed that first.

    I twisted the wires and the speed is rock solid. Also adjusted the minimum input voltage…for whatever reason it’s not 0V at minimum speed from the Acorn. Actually it’s 3.6V so when I set the F1.00 to 3.6 I get the exact minimum frequency output of 100 Hz (to achieve specified 6,000 RPM minimum spindle speed).

    Thanks @mactec54, I did tweak a few of the settings as you suggested. I didn’t change F2.19 (currently at F2.19=2) and all seems to run fine. The spindle nameplate states 2 poles but the use of “pairs” is confusing. Should I still change that setting?
    Did you figure out why you were getting voltage something other than 0 volts ? I am getting 1.2 ish volts with the spindle stopped, then when I start the spindle, the voltage is only 1.4 ish where it wants 1.66 in the spindle bench test, if I enter 1.5 in the first option, the rest land correctly. Not sure what is going on.



Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

VFD output fluctuates, no max speed

VFD output fluctuates, no max speed