You do have it set for a 2pole motor I assume?
If not, this could be the issue.
Hello everyone,
So i have a problem with controlling my VFD with mach3 BOB
This is the BOB in question: https://www.vallder-rs.com/en/c/300/...s-board-detail
This is the VFD in question: https://www.vallder-rs.com/en/c/436/...nverter-detail ( its 1.5kw one)
Min spindle speed is 6000 and max 24000 rpm.
I connected everything correctly and configured everything correctly i am sure of it.
When i start the spindle at min speed it starts speeding up and stops at 6000 for a second and again starts speeding up to around 12000 and stops there.
When i change speed in mach3 to 12000 ( through S12000 command) it starts slowing down for some reason.
I think i found the problem but do not know how to solve it.
To connect the mach3 BOB to VFD i use 3 VFD screw terminals called FV , GND COM and S1 respectively. S1 is used for starting the spindle and FV is used for +10V analog.
The voltage between S1 and COM GND is 12.3V without anything connected. Voltage between FV and COM GND is 0V as it should be.
I have 4 wires running from BOB to VFD : +10V , GND , relay COM , relay NO.
the problem is that GND and relay COM have to go the same point of VFD ( GND COM);
On BOB without connecting it to VFD 0-10V analog outputs correct voltage for all given S commands.
When i start the spindle on 6000 relay activates and spindle starts speeding up the voltage somehow gets transfered over to FV from S1 and gets higher then it should be, to around 4V between FV and GND COM.
The way to solve this is obviously to isolate GND from relay COM, but i do not know the way to do it.
If this post is confusing i will record a video to demonstrate what is the problem.
Thanks in advance for your responses.
Similar Threads:
You do have it set for a 2pole motor I assume?
If not, this could be the issue.
CNC, Mechatronics Integration and Custom Machine Design
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
The Breakout Board needs 12v or more for the PWM 0-10v to be correct, the VFD Drive +10v is not enough
If you are using Mach3 then you will may have to play with the Pulley Ratio 100Hz PWM setting is also a good starting number
You need the Breakout Board 0-10v working correct before you connect it to the VFD Drive
Do you have a PDF VFD Manual you can post
Mactec54
Last edited by mactec54; 07-06-2021 at 06:09 PM. Reason: added more content
Mactec54
This is my take on it:
If you're using voltage for speed control:
It looks to me as though the voltage 0-10v goes into FV
The ground goes into GND
If you're using a PID frequency:
It's FI & GND..... (pulse/direction?)
The connection marked 10v looks to be an output to send power to a potentiometer for stand alone control of FI and GND.
connect S1 to relay for M3
connect S2 to nothing for M4
Change 1 to low and 1 to high in Mach3. One of them will go on and one will go off when called for M3/M4. Depending on which direction you want to run, swap these over until it's correct.
S1/S2 will be + voltage..... COM will be - voltage.
That's how I would do it anyway but I can't guarantee this is all correct.
Hello,
Did you solve the issue you have with this VFD?
I bought the same from Vallder but I use a USB Mach3 controller instead of the one you use.
However, I deal with a similar problem. VFD works ok through panel commands, however, I can't make it run through terminals. I can see frequency changing on the VDF screen, but the motor is not running. As far as I understand, it seems that start/stop is failing as there is no current on motor leads.