Thread: Huanyang P2 vfd 1.5kw RS485 setup

  1. #21
    Member
    Join Date
    Dec 2013
    Posts
    121
    Downloads
    4
    Uploads
    0

    Default Re: Huanyang P2 vfd 1.5kw RS485 setup

    Quote Originally Posted by mactec54 View Post
    There is part of your problem you need 2 Relays ( 1 ) for FWD and ( 1 ) for REV
    You can see this in your manual

    DI1 K1 FWD

    DI2 K2 REV

    COM

    These are the connections you need for FWD and REV

    You will have some parameters to set as well

    I see you are using a different terminal reference X2 have you changed the VFD Drive you are using

    That Breakout Board is not going to do what you need, you want one with 2 Relays on
    very true but i just did another trick that worked
    the relay on that bob luckily is a spdt relay, they used 2 pins only, all i needed is to use the 3rd pin
    which means when the relay is off it can be a fw or a rev state to the vfd, not the perfect solution but it worked as it should, now m3 and m4 does work
    thanks a lot for your help



  2. #22
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang P2 vfd 1.5kw RS485 setup

    Quote Originally Posted by Graphicman View Post
    very true but i just did another trick that worked
    the relay on that bob luckily is a spdt relay, they used 2 pins only, all i needed is to use the 3rd pin
    which means when the relay is off it can be a fw or a rev state to the vfd, not the perfect solution but it worked as it should, now m3 and m4 does work
    thanks a lot for your help
    Are yes they are all like that, having a NO / NC contact, so yes when one side is open the other side would be closed, the only problem with that is it is, live in one direction at all times not very safe to be like this you need total isolation or the spindle could start unexpectedly

    Mactec54


  3. #23
    Member
    Join Date
    Dec 2013
    Posts
    121
    Downloads
    4
    Uploads
    0

    Default Re: Huanyang P2 vfd 1.5kw RS485 setup

    Quote Originally Posted by mactec54 View Post
    Are yes they are all like that, having a NO / NC contact, so yes when one side is open the other side would be closed, the only problem with that is it is, live in one direction at all times not very safe to be like this you need total isolation or the spindle could start unexpectedly
    is true, luckily that vfd does turn on without a direction, the relay has to work at least for one time then it is either fw or rev until it is off, so far so good i will keep an eye on it, if it did anything abnormal i will add another relay
    thanks



  4. #24
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang P2 vfd 1.5kw RS485 setup

    Quote Originally Posted by Graphicman View Post
    is true, luckily that vfd does turn on without a direction, the relay has to work at least for one time then it is either fw or rev until it is off, so far so good i will keep an eye on it, if it did anything abnormal i will add another relay
    thanks
    It won't be a problem with the VFD, only the control software where you can get unexpected starts from

    Mactec54


  5. #25
    Member
    Join Date
    Dec 2013
    Posts
    121
    Downloads
    4
    Uploads
    0

    Default Re: Huanyang P2 vfd 1.5kw RS485 setup

    Quote Originally Posted by mactec54 View Post
    It won't be a problem with the VFD, only the control software where you can get unexpected starts from
    I have not ran any programs yet, but how do you think the unexpected start would come from?
    it has to be a fault on the code right?



  6. #26
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang P2 vfd 1.5kw RS485 setup

    Quote Originally Posted by Graphicman View Post
    I have not ran any programs yet, but how do you think the unexpected start would come from?
    it has to be a fault on the code right?
    No nothing to do with code EMI noise can turn it on cause false triggers or even when you load your control software, what you basically have is a jumper across the VFD run Terminal and any voltage above 0 can start the spindle this will come from the PWM to analog side of the control or EMI Noise from the VFD Drive

    Mactec54


Page 2 of 2 FirstFirst 12

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

Huanyang P2 vfd 1.5kw RS485 setup

Huanyang P2 vfd 1.5kw RS485 setup