Need Help! problem with Huanyang 4kw vfd


Results 1 to 6 of 6

Thread: problem with Huanyang 4kw vfd

  1. #1
    Member
    Join Date
    May 2010
    Location
    Denmark
    Posts
    2
    Downloads
    0
    Uploads
    0

    Question problem with Huanyang 4kw vfd

    Hi
    i have a problem with my 4kw VFD with is a 4kw 18000rpm spindle
    i can fine get the spindel to 18000 rpm and 300hz
    but if i set the mach3 to 9000 rpm the the vfd is showing 174.5hz and not 150hz
    and i have measured the pwm signal to 5v

    now i have use two days and i cant find the error

    /kenneth

    Similar Threads:


  2. #2
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: problem with Huanyang 4kw vfd

    Quote Originally Posted by tkoc View Post
    Hi
    i have a problem with my 4kw VFD with is a 4kw 18000rpm spindle
    i can fine get the spindel to 18000 rpm and 300hz
    but if i set the mach3 to 9000 rpm the the vfd is showing 174.5hz and not 150hz
    and i have measured the pwm signal to 5v

    now i have use two days and i cant find the error

    /kenneth
    What Parameters have you set in the VFD Drive

    What is your spindle spec's

    Max RPM=
    Amps=
    Voltage=
    Max Hz=

    Mactec54


  3. #3
    Member
    Join Date
    May 2010
    Location
    Denmark
    Posts
    2
    Downloads
    0
    Uploads
    0

    Default Re: problem with Huanyang 4kw vfd

    spindle
    Voltage: 220VAC
    Current: 10A
    Frequency: 0-300Hz
    Speed: 0-18000rpm

    PD001=1
    PD003=300
    PD004=300
    PD005=300

    PD007=20

    PD008=220
    PD009=15
    PD010=8
    PD011=40
    PD014 Accel=12
    PD015 Deccl=12
    PD141=220 ( Motor Rated Voltage )
    PD142=10
    PD143=2
    PD144=3000



  4. #4
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: problem with Huanyang 4kw vfd

    Quote Originally Posted by tkoc View Post
    spindle
    Voltage: 220VAC
    Current: 10A
    Frequency: 0-300Hz
    Speed: 0-18000rpm

    PD001=1
    PD003=300
    PD004=300
    PD005=300

    PD007=20

    PD008=220
    PD009=15
    PD010=8
    PD011=40
    PD014 Accel=12
    PD015 Deccl=12
    PD141=220 ( Motor Rated Voltage )
    PD142=10
    PD143=2
    PD144=3000
    Is your Spindle Air cooled or Water Cooled ???


    PD014= you seem to have a high setting for this normally you can go as low as 3 so anywhere from 3 and up should work fine

    PD015= you seem to have a high setting for this normally you can go as low as 3 so anywhere from 3 and up should work fine


    Jumper J1 also must be set for Remote Control This is located next to the Terminal Block


    PD002=1

    PD011=120 Not 40 this is below the minimum speed for your spindle

    PD70=0 ( This may need to be set to 1 if Control Voltage is 0-5v )

    PD72=300

    PD73=120

    PD120=120 (Stall Prevention )

    PD174=?? ? ( Your VFD Drives Max Amp Output Rating )

    Mactec54


  5. #5
    Member Velikivrh's Avatar
    Join Date
    Nov 2019
    Posts
    1
    Downloads
    0
    Uploads
    0

    Default Re: problem with Huanyang 4kw vfd

    Way pd 144 =3000 ist this max rpm of motor?



  6. #6
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: problem with Huanyang 4kw vfd

    Quote Originally Posted by Velikivrh View Post
    Way pd 144 =3000 ist this max rpm of motor?
    Yes that is the max setting for that Parameter PD144=3000=Max Spindle RPM what ever it is

    Mactec54


Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

problem with Huanyang 4kw vfd

problem with Huanyang 4kw vfd