    Default How to show Rpm instead of frequency? FVD yl620-a

    Hello, sorry my english (google translator).
    I really need your help.
    I bought a Fvd and I can't show the Rpm on the display, just shows the frequency. In the manual does not say where to change this option, and already read in several places to change the parameter p144, but in my model this parameter does not have.


    https://pt.aliexpress.com/item/32807...2742b90atvjpGQ

    110v 2.2kw

    Thanks a lot if anyone can help me

    Similar Threads:
    Attached Thumbnails Attached Thumbnails How to show Rpm instead of frequency? FVD yl620-a-yl620-png  


  2. #2
    Member agflex's Avatar
    Join Date
    Oct 2019
    Posts
    3
    Downloads
    0
    Uploads
    0

    Default

    Hello. I am sending 2 pdf manuals to see if anyone can help me adjust what I need.

    Attached Files Attached Files


  3. #3
    Community Moderator Jim Dawson's Avatar
    Join Date
    Dec 2013
    Posts
    4488
    Downloads
    0
    Uploads
    0

    Default Re: How to show Rpm instead of frequency? FVD yl620-a

    Looks like set P00.24 = 6

    Maybe also need to adjust P00.23, but I think not.

    Jim Dawson
    Sandy, Oregon, USA


  4. #4
    Member agflex's Avatar
    Join Date
    Oct 2019
    Posts
    3
    Downloads
    0
    Uploads
    0

    Default Re: How to show Rpm instead of frequency? FVD yl620-a

    Thanks, I did that what you said, I had tried that too.
    But it still didn't work.
    In P00.23 it only adjusts from 0 to 100.
    in P00.24 I put in 6. Now shows on the display SP 1.
    There must be somewhere else to change, but I don't know where, this is hard.



  5. #5
    Member
    Join Date
    May 2016
    Location
    Canada
    Posts
    3
    Downloads
    0
    Uploads
    0

    Default Re: How to show Rpm instead of frequency? FVD yl620-a

    Hello, I have the same vfd did some one find out how to display rpm instead frequency on yl620-a?



  6. #6
    Member
    Join Date
    Jan 2005
    Location
    USA
    Posts
    11568
    Downloads
    0
    Uploads
    0

    Default Re: How to show Rpm instead of frequency? FVD yl620-a

    Quote Originally Posted by agflex View Post
    Hello, sorry my english (google translator).
    I really need your help.
    I bought a Fvd and I can't show the Rpm on the display, just shows the frequency. In the manual does not say where to change this option, and already read in several places to change the parameter p144, but in my model this parameter does not have.


    https://pt.aliexpress.com/item/32807...2742b90atvjpGQ

    110v 2.2kw

    Thanks a lot if anyone can help me
    The DISP should select the RPM, just Press it until the RPM led is on then it will show the RPM

    You could try P00.24=9 this will give you all the options

    Mactec54


  7. #7
    Member
    Join Date
    May 2016
    Location
    Canada
    Posts
    3
    Downloads
    0
    Uploads
    0

    Default Re: How to show Rpm instead of frequency? FVD yl620-a

    Quote Originally Posted by mactec54 View Post
    The DISP should select the RPM, just Press it until the RPM led is on then it will show the RPM

    You could try P00.24=9 this will give you all the options
    Hi mactec54, Really appreciate for the reply,
    I press DISP button 50 or more times no response, and I tried P00.24=9 displays u 9, and P00.24=6 displays SP 1, and there is no RPM display



  8. #8
    Member
    Join Date
    Jan 2005
    Location
    USA
    Posts
    11568
    Downloads
    0
    Uploads
    0

    Default Re: How to show Rpm instead of frequency? FVD yl620-a

    Quote Originally Posted by shakil1740 View Post
    Hi mactec54, Really appreciate for the reply,
    I press DISP button 50 or more times no response, and I tried P00.24=9 displays u 9, and P00.24=6 displays SP 1, and there is no RPM display
    Set it back to the default=0 and try the DISP again I'm not a fan of this VFD Drive as many users have had problems with them

    Mactec54


  9. #9
    Member Cosimino71's Avatar
    Join Date
    Sep 2020
    Posts
    11
    Downloads
    0
    Uploads
    0

    Default Foto giri del motore

    Enter on 00.23 = 50/60HZ it depends on where you are in Italy and 60hz
    Enter on 00.24=0
    Press the program button to return to the frequency, then press nine times on set until you reach RPM spindle on the display there is a lowercase u on the bottom left with the engine running you will see the engine rpm

    Last edited by Cosimino71; 09-25-2020 at 06:34 PM.


  10. #10
    Member
    Join Date
    Jan 2005
    Location
    USA
    Posts
    11568
    Downloads
    0
    Uploads
    0

    Default Re: Foto giri del motore

    Quote Originally Posted by Cosimino71 View Post
    Enter on 00.23 = 50/60HZ it depends on where you are in Italy and 60hz
    Enter on 00.24=0
    Press the program button to return to the frequency, then press nine times on set until you reach RPM spindle on the display there is a lowercase u on the bottom left with the engine running you will see the engine rpm
    This is an old thread

    He can not use 50Hz or 60Hz Parameter settings with his motor they must be set to 400Hz or he will damage his spindle motor

    Mactec54


  11. #11
    Member Cosimino71's Avatar
    Join Date
    Sep 2020
    Posts
    11
    Downloads
    0
    Uploads
    0

    Default

    Quote Originally Posted by mactec54 View Post
    This is an old thread

    He can not use 50Hz or 60Hz Parameter settings with his motor they must be set to 400Hz or he will damage his spindle motor
    If on 00.23 you put 400hz the spindle marks 6000 rpm as the maximum speed, if you put 60hz the spindle reaches 24000 rpm



  12. #12
    Member
    Join Date
    Jan 2005
    Location
    USA
    Posts
    11568
    Downloads
    0
    Uploads
    0

    Default Re: How to show Rpm instead of frequency? FVD yl620-a

    Quote Originally Posted by Cosimino71 View Post
    If on 00.23 you put 400hz the spindle marks 6000 rpm as the maximum speed, if you put 60hz the spindle reaches 24000 rpm
    The P0023 you have a choice as to what you want and how to use it ( it is a % setting ) it has nothing to do with the main frequency

    Attached Thumbnails Attached Thumbnails How to show Rpm instead of frequency? FVD yl620-a-p00-23-jpg  
    Mactec54


  13. #13
    Member Cosimino71's Avatar
    Join Date
    Sep 2020
    Posts
    11
    Downloads
    0
    Uploads
    0

    Default

    Quote Originally Posted by mactec54 View Post
    The P0023 you have a choice as to what you want and how to use it ( it is a % setting ) it has nothing to do with the main frequency
    Hello as I am new in this forum and I would like to understand my cnc machine well I followed the discussion regarding the vision of the spindle speed and I set those parameters to be able to see it the main parameters are on 400hz but I notice that the spindle heats up after 15 minutes even if I take it over six thousand turns my spindle and the one in the attached photo and I have a YL620-A vfd

    Attached Thumbnails Attached Thumbnails How to show Rpm instead of frequency? FVD yl620-a-d8438d47-651c-45cf-b3a1-5ae7e3cfea5d-jpg  


  14. #14
    Member
    Join Date
    Jan 2005
    Location
    USA
    Posts
    11568
    Downloads
    0
    Uploads
    0

    Default Re: How to show Rpm instead of frequency? FVD yl620-a

    Quote Originally Posted by Cosimino71 View Post
    Hello as I am new in this forum and I would like to understand my cnc machine well I followed the discussion regarding the vision of the spindle speed and I set those parameters to be able to see it the main parameters are on 400hz but I notice that the spindle heats up after 15 minutes even if I take it over six thousand turns my spindle and the one in the attached photo and I have a YL620-A vfd
    Air cooled spindles most can not run at 6000 RPM the minimum speed is normally in the 12,000 RPM to 18,000 RPM or they will over heat from low air flow

    Some Parameters may help, what Parameters have you set

    Mactec54


  15. #15
    Member Cosimino71's Avatar
    Join Date
    Sep 2020
    Posts
    11
    Downloads
    0
    Uploads
    0

    Default

    Quote Originally Posted by mactec54 View Post
    Air cooled spindles most can not run at 6000 RPM the minimum speed is normally in the 12,000 RPM to 18,000 RPM or they will over heat from low air flow

    Some Parameters may help, what Parameters have you set
    Which parameters determine the heating of the spindle and its good functioning so I check and let you know the ones that I have set



  16. #16
    Member Cosimino71's Avatar
    Join Date
    Sep 2020
    Posts
    11
    Downloads
    0
    Uploads
    0

    Default

    Quote Originally Posted by Cosimino71 View Post
    Which parameters determine the heating of the spindle and its good functioning so I check and let you know the ones that I have set
    These are the parameters stored on my Vfd

    P00.00=400

    P00.01 = 0

    P00.02=0

    P00.03=0

    P00.04 = 400

    P00.05 = 400

    P00.06 = 100.0

    P00.07 = 400

    P00.08 = 146

    P00.09 = 0.2

    P00.10 = 2.0

    P01.00 = 0

    P01.01=0.0

    P01.02=140

    P01.03 = 140

    P01.04 = 200

    P01.05=130

    P01.06=120

    P01.07=80

    P01.08 = 150

    P03.08 = 40.0

    P03.09 = 400

    P06.01 = 10

    P06.02 = 10

    P0700 = 0.1

    P07.08 = 0

    P11.01 = 220

    P11.02 = 7.0

    P11.03 = 400

    P12.00 = 5.0

    P12.01 = 220

    P12.02 = 2

    P12.03 = 30

    P12.04=5

    P12.05=6,5

    P12.06=220

    P12.07=140

    Attached Thumbnails Attached Thumbnails How to show Rpm instead of frequency? FVD yl620-a-c38f7bf6-5d72-4ded-a362-c09656ffaa18-jpg  


  17. #17
    Member Cosimino71's Avatar
    Join Date
    Sep 2020
    Posts
    11
    Downloads
    0
    Uploads
    0

    Default

    Quote Originally Posted by Cosimino71 View Post
    Which parameters determine the heating of the spindle and its good functioning so I check and let you know the ones that I have set
    These are the parameters stored on my Vfd

    P00.00=400

    P00.01 = 0

    P00.02=0

    P00.03=0

    P00.04 = 400

    P00.05 = 400

    P00.06 = 100.0

    P00.07 = 400

    P00.08 = 146

    P00.09 = 0.2

    P00.10 = 2.0

    P01.00 = 0

    P01.01=0.0

    P01.02=140

    P01.03 = 140

    P01.04 = 200

    P01.05=130

    P01.06=120

    P01.07=80

    P01.08 = 150

    P03.08 = 40.0

    P03.09 = 400

    P06.01 = 10

    P06.02 = 10

    P0700 = 0.1

    P07.08 = 0

    P11.01 = 220

    P11.02 = 7.0

    P11.03 = 400

    P12.00 = 5.0

    P12.01 = 220

    P12.02 = 2

    P12.03 = 30

    P12.04=5

    P12.05=6,5

    P12.06=220

    P12.07=140



  18. #18
    Member
    Join Date
    Jan 2005
    Location
    USA
    Posts
    11568
    Downloads
    0
    Uploads
    0

    Default Re: How to show Rpm instead of frequency? FVD yl620-a

    Quote Originally Posted by Cosimino71 View Post
    Which parameters determine the heating of the spindle and its good functioning so I check and let you know the ones that I have set
    By your list you have all the important Parameters set correct, some of these air cooled spindles do get hot, that is why the water cooled spindles are better have you been able to check what the temperature gets too

    Mactec54


  19. #19
    Member Cosimino71's Avatar
    Join Date
    Sep 2020
    Posts
    11
    Downloads
    0
    Uploads
    0

    Default

    Quote Originally Posted by mactec54 View Post
    By your list you have all the important Parameters set correct, some of these air cooled spindles do get hot, that is why the water cooled spindles are better have you been able to check what the temperature gets too
    So my parameters are fine my spindle motor and 0,8KW 220v 6,5A 400HZ is my VFD 1,5kw 220v 7,0A 2,8KVA



  20. #20
    Member Cosimino71's Avatar
    Join Date
    Sep 2020
    Posts
    11
    Downloads
    0
    Uploads
    0

    Default

    Quote Originally Posted by mactec54 View Post
    By your list you have all the important Parameters set correct, some of these air cooled spindles do get hot, that is why the water cooled spindles are better have you been able to check what the temperature gets too
    Since you are very kind and prepared I would like to ask you how to install a diode laser that I had on my cnc 3018, I would like to put it on my new cnc with mach3 system the spindle I command it with the Vfd panel but I would like to control the laser from the system but I don't know what I need.The 15w laser has three wires and is equipped with ttl that you can control with pwm I am sending you the photo of the controller attached

    Attached Thumbnails Attached Thumbnails How to show Rpm instead of frequency? FVD yl620-a-43455c0f-5879-4c8c-ab14-2043e67d06ff-jpg  


Page 1 of 2 12 LastLast

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

How to show Rpm instead of frequency? FVD yl620-a

How to show Rpm instead of frequency? FVD yl620-a

How to show Rpm instead of frequency? FVD yl620-a