    I have a YL620-A VFD and an air cooled 1.5kW 220 volt spindle.
    I am able to make it run successfully and control the speed from the controller pot on the VFD panel.
    I am using Estlcam software which has speed control built in and I have made the control board to produce the variable 0-10 volts required to control the VFD.
    I can produce the 0-10 volts from the software, but am not able to get any response from the VFD using it.
    I have the variable voltage 0-10 volts connected to the Gnd and the 10V connectins on the VFD, I have also tried the GND and VI1 connections (pot rotor)
    I have had to do all the speed control from the VDF panel instead, although I am able to turn the spindle on and off with the software successfully.
    I have tried various settings in the VFD but without success in remotely controlling the speed via software.
    Does anyone on this forum have any suggestions on how to set up the settings for the remote control please?
    Jan 2005
    Default Re: YL620-A VFD setting question.
    Quote Originally Posted by regpye View Post
    VI1 and Gnd is the correct connection then you have to set a Parameter for it to work, ( P00.01 Either 1 or 2 ) if the KeyPad is working then you have not activated remote control
    You also need a Relay to turn it on FWD and XGND this is just a switch, so for a temporary connection you can jumper the FWD and XGND, This should only be temporary for a try out
    Mactec54
    Oct 2009
    Thanks for the reply.
    I have the stop/start working OK, I am using a PC217 opto isolator circuit to do the switching for that part. connected as you say between XGND and FOR.
    If I set P00.01 =0 then the speed control works by the panel speed control knob. If I set P00.01 to either 1 or 2 the panel speed control knob doesn't work any more, but also the software control also does not control the speed, it runs at full speed in both cases when I activate the software spindle on.
    There seems to be other settings that are not explained in the manual P70.08 - P70.15 enough for me to understand, and I think that may be the reason that the software is not controlling the speed.
    I have attached the PDF manual for this VFD.
    Attached Files Attached Files
    Jan 2005
    That is the way it should work when you set P00.01 You can't have the KeyPad and remote control working at the same time
    Have you got the 0-10v working by setting a speed like M3S12000 and check the voltage it should be 5v if not then you have to get that part working before you have anything to change in the VFD
    Mactec54
    Oct 2009
    Thanks for your input, yes I have checked the reference voltage.
    The reference voltage is being produced with a LM358 board that produces 0-10 volts from the 5V PWM signal. It is working fine producing 0-10 volts across the range.
    Found out the settings needed.
    P03.12 =30 (any lower the spindle will not start properly, higher will make the start RPM higher also)
    P03.13 =400 (highest RPM for the spindle)
    After setting, shut down the VFD and restart and it will work OK.
    The range is working OK except the highest frequency is around 270 instead of 400.
    Also the spindle is getting very hot while before it would run cool for hours.
    I wish I had kept a record of the original settings so that I could go back and start again.
    The original settings were not factory defaults I found out, so now another problem.
    Member hafizi5299's Avatar
    Sep 2018
    Hai there, just want to know if u have resolve the problem with YL620-A VFD? If haven't, i might be able to help. Please WhatsApp me since i might miss ur question in here..
    +6011-10212761
  7. #7
    Oct 2009
    Quote Originally Posted by hafizi5299 View Post
    +6011-10212761
    Yes thanks, I have it working fine now.