    Quote Originally Posted by PWoolson View Post
    Hi All, I'm really struggling with my new spindle. I had a 1.5kW spindle running fine but wanted to be able to use 1/2" mills so I upgraded to a 2.2kW ER20 spindle with the Huanyang VFD. Model Hy02D211B AC110 50Hz/60Hz+/-5Hz (that makes no sense to me, is it 50Hz or 60Hz?)
    The spindle is 2.2kW 110v 8.5A 400 Hz
    Can someone please tell me what to enter in the VFD? I've looked through almost all of this thread and can't make sense of much of it, I also didn't see any settings for 110v.
    Thanks much! Paul
    Set your VFD drive to all the same settings in the above posts

    The only different Parameters to set different are
    PD008=110 If this is your Spindle motor Rated voltage

    PD141=110

    You might be disappointed buying this 2.2Kw as the 1.5Kw will most likely run better on this voltage

    Mactec54


  2. #762

    Default Re: Huanyang Chinese VFD settings and manual here!

    Thanks! So here's what I'm entering. Let me know if it's not right.
    Also, this will be used totally manually, I don't hook it through the controller. Would that change PD001 and PD002?

    PD000=0
    PD001=1
    PD002=1
    PD003=400
    PD004=400
    PD005=400
    PD007=20
    PD008=110
    PD009=15
    PD010=8
    PD011=120 (Minimum Setting 120)
    PD014 Accel=10
    PD015 Deccl=10
    PD070=0
    PD072=400
    PD073=120
    PD141=110
    PD142=8.5
    PD143=4 my motor has one of the aircraft plugs with 4 wires. One is a ground though, so should this be 4 or 3?
    PD144=3000 (Max Motor RPM) =3,000= (24,000)



  3. #763
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by PWoolson View Post
    Thanks! So here's what I'm entering. Let me know if it's not right.
    Also, this will be used totally manually, I don't hook it through the controller. Would that change PD001 and PD002?

    PD000=0
    PD001=1
    PD002=1
    PD003=400
    PD004=400
    PD005=400
    PD007=20
    PD008=110
    PD009=15
    PD010=8
    PD011=120 (Minimum Setting 120)
    PD014 Accel=10
    PD015 Deccl=10
    PD070=0
    PD072=400
    PD073=120
    PD141=110
    PD142=8.5
    PD143=4 my motor has one of the aircraft plugs with 4 wires. One is a ground though, so should this be 4 or 3?
    PD144=3000 (Max Motor RPM) =3,000= (24,000)

    Not quite right for manual control

    PD001=0
    PD002=0 ( if you have a pot to control the speed then this would be PD002=1 )

    J1 Jumper may need changing also

    PD002=1 These ( 2 )Parameters are for Pot / Manual Speed Control
    PD073=1

    PD143=2 ( This is the number of motor Poles this has nothing to do with wiring )

    The output from the VFD Drive to the spindle is 3Ph so you have 3 Hot wires and a Ground so 4 wires are required

    Mactec54


  4. #764

    Default Re: Huanyang Chinese VFD settings and manual here!

    Well, I got closer. I entered everything as you told me 002=1, 073=1, 143=2. Pushed the run button and dialed up the speed. I heard the high pitch of the spindle and got all excited only to see it make about one full revolution and stop with an error on the screen EoUA. Any thoughts?



  5. #765
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by PWoolson View Post
    Well, I got closer. I entered everything as you told me 002=1, 073=1, 143=2. Pushed the run button and dialed up the speed. I heard the high pitch of the spindle and got all excited only to see it make about one full revolution and stop with an error on the screen EoUA. Any thoughts?
    This is telling you you don't have enough voltage / Amps to run it, this is a common problem when someone tries to run these 2.2Kw spindles on 120v single phase, set the pot to the lowest speed and see it can start at the low speed

    So press Reset ( Stop Button ) and try at the lowest speed turning the pot right back

    I guess you are using a standard 120v 15A outlet

    How do you have the main Power supply connected to the VFD Drive this is important

    Mactec54


  6. #766

    Default Re: Huanyang Chinese VFD settings and manual here!

    Update. I punted. Went back to my old 1.5kW setup and it's working perfectly. Thanks for your help though! I really appreciate the effort.



  7. #767

    Default Re: Huanyang Chinese VFD settings and manual here!

    do you think you can help me with my vfd settings
    https://www.cnczone.com/forums/spind...ml#post2468956



  8. #768
    Member maki's Avatar
    Join Date
    Feb 2011
    Location
    Slowenia
    Posts
    138
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Hi to all,
    I also have this VFD (HY02D223B) for 2.2kw motor, question is, can be water pump connected to relay inside of VFD? Maybe some input? Which "code" shoud be adjusted?
    Thanks in adwance,



  9. #769
    Member
    Join Date
    Jan 2007
    Location
    gr
    Posts
    31
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    But why do you want to do this, the pump could be running continously without causing an issue.



  10. #770
    Member maki's Avatar
    Join Date
    Feb 2011
    Location
    Slowenia
    Posts
    138
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    I know but it shoud be turned on/off somehaw, and I don't want an extra switch. Untill now I have that throu software, but now is luck of free output's...
    So, looking for some soution and it will be nice if VFD will do that for me.



  11. #771
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by maki View Post
    Hi to all,
    I also have this VFD (HY02D223B) for 2.2kw motor, question is, can be water pump connected to relay inside of VFD? Maybe some input? Which "code" shoud be adjusted?
    Thanks in adwance,
    Yes, you can, and a lot do this just make sure the Amp rating of the pump is less than the max rating of the built in VFD Drive relay.

    Mactec54


  12. #772
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by maki View Post
    I know but it shoud be turned on/off somehaw, and I don't want an extra switch. Untill now I have that throu software, but now is luck of free output's...
    So, looking for some soution and it will be nice if VFD will do that for me.
    Just check with a meter to see which relay connection is N/O and that it closes when you start the VFD Drive, this should be FC to FB, Parameter PD052=01 to change for these Relays to be working as a Relay, Default is 02 which may work also but this is normally for fault detection, pump must be less than 3Amps

    Mactec54


  13. #773
    Member maki's Avatar
    Join Date
    Feb 2011
    Location
    Slowenia
    Posts
    138
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Thank you mactec54, I'll check the pump, it comes with VF as bundle and is submurssable I think is 75W.....kind a akvarium pump



  14. #774
    Member maki's Avatar
    Join Date
    Feb 2011
    Location
    Slowenia
    Posts
    138
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    I have take a look to the manual of VFD, and under"PD052"= 0-invalid, 1-Run, 2-Zerro speed, 3-Fault indication, 4-Braking indication, 5-Set Frequency reach, 6-In Accel, 7-In Decel, 8-Arbitrary Frequency 1 reach, 9-Arbitrary Frequency 2 reach.

    My question is if I put it to Nr.:5, will turn ON WHEN rpm is reached? Or just put it on Nr.:1 ....just my toughts...



  15. #775
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by maki View Post
    I have take a look to the manual of VFD, and under"PD052"= 0-invalid, 1-Run, 2-Zerro speed, 3-Fault indication, 4-Braking indication, 5-Set Frequency reach, 6-In Accel, 7-In Decel, 8-Arbitrary Frequency 1 reach, 9-Arbitrary Frequency 2 reach.

    My question is if I put it to Nr.:5, will turn ON WHEN rpm is reached? Or just put it on Nr.:1 ....just my toughts...
    No, you want it on as soon as the spindle starts

    You need to set it PD052=01 as I said in what I posted

    Attached Thumbnails Attached Thumbnails Huanyang Chinese VFD settings and manual here!-pd052-png  
    Mactec54


  16. #776
    Member maki's Avatar
    Join Date
    Feb 2011
    Location
    Slowenia
    Posts
    138
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Thank you mactec54, will do that as you suggested.



  17. #777

    Default Re: Huanyang Chinese VFD settings and manual here!

    I'm hoping this thread is still viewed and someone can help.
    I have a HY inverter Model 02D223B and a 2.2KW 220v 400hz spindle

    The spindle and VFD were running ok with a XHC MKX-V Mach3 Breakout Board and Mach3 but had issues with the stepper motors so i have reconfigured the CNC with a CSMIO IP-S and SIM CNC software and have now eliminated that issue but after re wiring the VFD to the new controller i'm now having issues with it and the VFD. Unfortunately en-labs are not the best for communication or help with set up issues

    The VFD works fine via the operator control panel and speed can be controlled but when trying to control it via the CSMIO IP-S i get nothing

    The VDF parameters are as follows

    PD000=0
    PD001=1
    PD002=1
    PD003=400
    PD004=400
    PD005=400
    PD007=20
    PD008=220
    PD009=15
    PD010=8
    PD011=120
    PD014 Accel=10
    PD015 Deccl=10
    PD070=0
    PD072=400
    PD073=120
    PD141=220
    PD142=11
    PD143=2
    PD144=3000
    I have checked all other parameters against the manual are all ok/ factory settings

    The above settings seem to be correct as per previous posts. I have wired the VFD as per diagram provided by en-labs whiuch is below ( i now know Reverse is not needed and can be dangerous and willl remove after posting this)

    Huanyang Chinese VFD settings and manual here!-vfd-wiring-jpg

    the VFD is wired
    VI 0-10v Analog
    ACM - GND

    FOR - Digital output 1 (24v supply)
    REV - Digtail outout 3 (24v supply)
    DCM - 0v supply

    FA & FB is wired into the CSMIO IP-S and the spindle fault relay is working ok
    The Software and controller i think are working ok as when i turn the spindle on via the controller i get 0-10v across VI and ACM which can be controlled, the query i have is that i get 22.5v across either FOR or REV and DCM when in idle or estop state but when i switch the spindle on the controller the voltage increases to 24v. I'm waiting to here back from en labs to see if this is correct.



  18. #778
    Member
    Join Date
    Jun 2012
    Location
    SA
    Posts
    153
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Where is this 24V coming from ? I'm not sure the digital inputs will like 24V.

    CSMIO IP-S show 24V as an example that does not mean it requires 24V. It says output driver is VNQ860

    Each group is controlled by specialized
    chip VNQ860. These chips work in PNP
    logic, thus the active state is a high state
    (+24V).
    VNQ860 Datasheet pdf - QUAD CHANNEL HIGH SIDE DRIVER - SGS Thomson Microelectronics

    VNQ860 can work from 5.5 to 36V supply. This should match what you need to send to the VFD.

    The VFD manual does not seem to specify the voltage of the input pins but against DCOM is says it is the ground for "digital and control signals, 12v power, EV, IPV, P24 ground".

    Chinese clarity of course but possibly means they need 12VDC signals.

    What tension was the MACH3 board sending ?

    The VFD works fine via the operator control panel and speed can be controlled but when trying to control it via the CSMIO IP-S i get nothing
    Do you have a potentiometer control on your VFD or are you using the programmable speed control ?



  19. #779

    Default Re: Huanyang Chinese VFD settings and manual here!

    thanks for the reply

    yes i have a potentiometer on my VFD and works perfectly in operator mode PD001 - 0

    On the previous controllor the digital output to the VFD was also 24v but because this worked ok i never measured active and inactive state so unsure if this was also the case.
    Each set of digital ouputs are optoisolated and require their own power supply, en-labs have stated for this to be 24V

    manual_csmioip-s_en_v3 (1).pdf

    manual_csmioip-s_en_v3 (1).pdf
    I have expanded the diagram to show this

    simcnc-csmioip-s-hy VFD.pdf



  20. #780
    Member
    Join Date
    Jun 2012
    Location
    SA
    Posts
    153
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Hi,

    when I looked at the CSMIO IP-S manual I did not see a specification of 24V , this seemed to indicated in wiring diagrams , often in brackets. From the chip datasheet we see this is NOT a required voltage. However, if you previous set up was using 24V apparently that is safe. I made my own hardware and used 12V for control lines .

    In a heavy industrial context with a lot of RFI, 24V will give more noise immunity.

    I'll try to dig out my PCB design for use of these lines.

    the query i have is that i get 22.5v across either FOR or REV and DCM when in idle or estop state but when i switch the spindle on the controller the voltage increases to 24v. I'm waiting to here back from en labs to see if this is correct.
    I would suggest taking the e-stop out of the equation until you track this down. Also you leave the inputs floating when relays not activated and say you get 24V when activated and in this case they should be grounded. That looks like a wiring fault unless I misunderstand what you described there.

    Last edited by reg.miller; 08-30-2022 at 05:06 AM.


Page 39 of 41 FirstFirst ... 29363738394041 LastLast

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

Huanyang Chinese VFD settings and manual here!

Huanyang Chinese VFD settings and manual here!