    Default Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by firebird_1995 View Post
    Hey everyone, sorry this has to be my first post but I'm having trouble setting up my Chinese VFD. I've entered in all of the parameters according to everything I've read and the unit powers but I cannot get the frequency to ramp up. It just flashes 000. It's the Huanyang HY02D223B 2.2Kw VFD. I know these questions are all over the place on these forums and I hate to beat a dead horse but I'm at my wits end here. Any help would be appreciated thank you

    Do a Factory reset, & set what I have in post 32, before you do the reset make sure you have PD000=0 for Parameter unlock set to ( 0 )

    Mactec54


  2. #50
    Member
    Join Date
    Jan 2011
    Location
    USA
    Posts
    75
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    I'm looking @ running a 2.2 kw spindle & VFD and can't find the amps required for 220 vac ? I need to make sure I have enough amps to run it.



  3. #51
    Registered Pplug's Avatar
    Join Date
    Jan 2007
    Location
    USA
    Posts
    723
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    You can use a double pull 15 amp breaker.

    http://www.glenspeymillworks.com Techno LC4896 - 2.2Kw Water Cooled Spindle | Moving Table Mill from Omis 3 CMM, 500Lb granite base | Epilog Legend 32 Laser Engraver


  4. #52
    Registered
    Join Date
    Jul 2012
    Location
    uk
    Posts
    8
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Hi guys
    I have been reading this post and have got my spindle changing spped with the pot on the vfd with the settings that mactec54 says, but only getting rpm range from 7200 to 13500??
    any suggestions please .
    thanks
    my vfd and spindle are 1.5kw
    Ton



  5. #53
    Member
    Join Date
    Jan 2005
    Location
    USA
    Posts
    10313
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    humbo3d

    Have you set PD 11 to 120 & PD144 to 3000, is your spindle 300Hz or 400 hz, if 300Hz you will have to use 300Hz were all the 400 Hz Parameters are set

    Mactec54


  6. #54
    Registered
    Join Date
    Jul 2012
    Location
    uk
    Posts
    8
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Hi
    My spindle is 400hz and i have set the pd11 to 120 and pd144 to 3000



  7. #55
    Member
    Join Date
    Jan 2005
    Location
    USA
    Posts
    10313
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    humbo3d

    You could try a Factory ReSet, then redo the Parameters, make sure PD000=0 before you do a Factory ReSet

    If this does not work you may have a faulty Drive, the Parameters below should have you running

    Huanyang Mactec54
    PD000=0 for Parameter unlock ( 1 ) for Parameter Lock

    PD001=0 (1 For Remote Control)

    PD002=0

    PD003=400

    PD004=400

    PD005=400

    PD007=20

    PD008=220

    PD009=15

    PD010=8

    PD011=120 (Minimum Setting 120)

    PD13= 08 is for Factory reset, Only use this to set VFD to Factory Default Settings

    PD014 Accel=12 ( Adjust to suit)

    PD015 Deccl=12 (Adjust to suit) ( PD15 is ignored IF PD26=1 Then the Spindle will Coast to a Stop)

    PD141=220 ( Motor Rated Voltage )

    PD142=9 ( Motor Max Amps) (Set for your motor Amp Rating 2.2Kw Spindle 9 amp Max)
    (Set for your motor Amp Rating 1.5Kw Spindle 7 amp Max)

    PD143=2 ( Motor Number of Poles)

    PD144=3000 (Max Motor RPM) =3,000= (24,000)

    For Remote Pot use

    PD002=1

    PD70=0

    PD72=400

    PD73=120

    Last edited by mactec54; 03-27-2015 at 05:20 PM. Reason: Parameter Adjustment
    Mactec54


  8. #56
    Registered
    Join Date
    Jul 2012
    Location
    uk
    Posts
    8
    Downloads
    0
    Uploads
    0

    Default

    Thanks for the quick reply. I'll try a reset tomorrow and reset it. With out the pot it does 24000 rpm so I think everything is ok but must be a setting I've Missed.
    Thanks Tony


    Quote Originally Posted by mactec54 View Post
    humbo3d

    You could try a Factory ReSet, then redo the Parameters, make sure PD000=0 before you do a Factory ReSet

    If this does not work you may have a faulty Drive, the Parameters below should have you running

    Huanyang Mactec54
    PD000=0 for Parameter unlock ( 1 ) for Parameter Lock

    PD001=0 (1 For Remote Control)

    PD002=0

    PD003=400

    PD004=400

    PD005=400

    PD007=20

    PD008=220

    PD011=120 (Minimum Setting 120)

    PD009=15

    PD010=8

    PD13= 08 is for Factory reset, Only use this to set VFD to Factory Default Settings

    PD014 Accel=12 ( Adjust to suit)

    PD015 Deccl=12 (Adjust to suit) ( PD15 is ignored IF PD26=1 Then the Spindle will Coast to a Stop)

    PD141=220 ( Motor Rated Voltage )

    PD142=9 ( Motor Max Amps) (Set for your motor Amp Rating 2.2Kw Spindle 9 amp Max)
    (Set for your motor Amp Rating 1.5Kw Spindle 7 amp Max)

    PD143=2 ( Motor Number of Poles)

    PD144=3000 (Max Motor RPM) =3,000= (24,000)

    For Remote Pot use

    PD002=1

    PD70=0

    PD72=400

    PD73=120




  9. #57
    Registered
    Join Date
    Dec 2013
    Posts
    22
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by mactec54 View Post
    humbo3d

    You could try a Factory ReSet, then redo the Parameters, make sure PD000=0 before you do a Factory ReSet

    If this does not work you may have a faulty Drive, the Parameters below should have you running

    Huanyang Mactec54
    PD000=0 for Parameter unlock ( 1 ) for Parameter Lock

    PD001=0 (1 For Remote Control)

    PD002=0

    PD003=400

    PD004=400

    PD005=400

    PD007=20

    PD008=220

    PD009=15

    PD010=8

    PD011=120 (Minimum Setting 120)

    PD13= 08 is for Factory reset, Only use this to set VFD to Factory Default Settings

    PD014 Accel=12 ( Adjust to suit)

    PD015 Deccl=12 (Adjust to suit) ( PD15 is ignored IF PD26=1 Then the Spindle will Coast to a Stop)

    PD141=220 ( Motor Rated Voltage )

    PD142=9 ( Motor Max Amps) (Set for your motor Amp Rating 2.2Kw Spindle 9 amp Max)
    (Set for your motor Amp Rating 1.5Kw Spindle 7 amp Max)

    PD143=2 ( Motor Number of Poles)

    PD144=3000 (Max Motor RPM) =3,000= (24,000)

    For Remote Pot use

    PD002=1

    PD70=0

    PD72=400

    PD73=120
    Hello everybody. Great stuff here. My spindle now rotates at 24000rpm with these settings. But it does it only with the onboard keys controls. My inverter has an onboard pot which if i set PD002 to 1 and try to use it, will only go to 15600 RPM max.
    Any suggestions on how to fix this? It would be awesome to use the pot instead of the keys.



  10. #58
    Registered Dytoven's Avatar
    Join Date
    Apr 2015
    Posts
    17
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by Streetslab View Post
    Hello everybody. Great stuff here. My spindle now rotates at 24000rpm with these settings. But it does it only with the onboard keys controls. My inverter has an onboard pot which if i set PD002 to 1 and try to use it, will only go to 15600 RPM max.
    Any suggestions on how to fix this? It would be awesome to use the pot instead of the keys.
    PD070 - 1

    For my 3KW spindle 18000rpm work



  11. #59
    Registered
    Join Date
    Apr 2011
    Location
    USA
    Posts
    31
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Hello,

    I was hoping to get some help with my Huanyang. The spindle is supposed to be 18000rpm 3kw and matched vfd. See attached pictures for info on the plates. I followed the info in this thread, attempting to figure out the differences between 24000rpm and 18000rpm settings. The spindle seems to get up to the proper RPM, however I can't get ROTT to display 18000. The hz display will show 300hz, so I assume it's getting up to speed. I'm in the US, input to the VFD is via a 20 amp 240v breaker directly from my sub panel. Spindle is connected with pin 1 = V, 2 = U, W = 3, and ground to vfd ground. Rotation is going the right way.

    Here is exactly what I did. First I reset to factory defaults, then:

    PD001 = 0
    PD005 = 300
    PD004 = 300
    PD003 = 300
    PD072 = 300
    PD006 = 2.5
    PD008 = 220
    PD009 = 15
    PD010 = 8
    PD011 = 120
    PD142 = 8.6 (Amps listed on motor plate. I thought it was 3kw spindle, shouldn't it be more?)
    PD143 = 2
    PD144 = I tried many values here, from default, to 3000, 2250, 2093 (obviously I have no idea what I'm doing). At 2250, rott reads 10800. At default, it reads 8640.

    I've been in contact with the seller, Jean, and he suggested only setting:
    Step 1: Set PD005 =300
    Step 2: Set PD004 =300
    Step 3: Set PD003 =300
    Step 4: Set PD072 =300

    I reset to factory default again, and made those settings. That is when rott read 8640. The spindle seems to speed up to the same speed as when I had originally configured. Of course, I'm concerned about pd011 not being set to 120 by default, so I won't run the spindle for more than a few seconds with only his suggested settings. Video of what that looks like:



    I assume I should put my previous settings back and will have to tweak something (pd010 and pd144) to get the right RPM via rott?

    I appreciate the help.

    Thanks,
    Bobby
    Attachment 286490 Attachment 286492

    Last edited by btsioles; 07-13-2015 at 12:04 PM.


  12. #60
    Member
    Join Date
    Jan 2005
    Location
    USA
    Posts
    10313
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    btsioles

    Have not done an 18,000RPM spindle with this drive, so if you were getting to 300 Hz then you were at max speed, It would be wise to use the settings you had put in, obvious the seller is just that & does not know how to set the drive up

    You have an air cooled spindle so it is very important, that you have the minimum speed set correct, 120 Hz will be to low, looking at the photos, they are saying that your spindle is 400 Hz max with a minimum of 300 Hz

    So is this spindle realy a 24,000 RPM or Just a 18,000 RPM spindle, very confusing motor plate information, if it is only a 18,000 RPM then you most likey need to set the Minimum Hz setting to something like 200 Hz not the 120 Hz, this setting is for the water cooled spindle

    PD011 is a parameter that is set to suit each type of motor/spindle the drive is being used for, this is the minimum speed the motor/spindle can be safely run

    Last edited by mactec54; 07-13-2015 at 02:36 PM.
    Mactec54


Page 5 of 56 FirstFirst ... 23456781555 ... LastLast

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  