    I am working with a 110v 1.5kw vfd with a pot control on the front panel. I attempted to configure to the settings in this post and the vfd will not take them. I change a pd setting from 110 to 220 and hit set. I'll check it again and it will still be at 110. I am trying to get full rpm out of my 800w 220v spindle. It currently only reaches 11520.

    Sean



  2. #22
    Member diyengineer's Avatar
    Join Date
    Feb 2010
    Location
    USA-WA STATE
    Posts
    3447
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Sounds like you need to check how many "poles" you have in your settings. I had the same problem running at half speed. I remember I had 4 pole setting for a 2 pole motor or vise versa



  3. #23
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by vbquick1 View Post
    I am working with a 110v 1.5kw vfd with a pot control on the front panel. I attempted to configure to the settings in this post and the vfd will not take them. I change a pd setting from 110 to 220 and hit set. I'll check it again and it will still be at 110. I am trying to get full rpm out of my 800w 220v spindle. It currently only reaches 11520.

    Sean
    I have no information on a 800W Spindle, I thought they were a DC motor, if they are then you can not use this VFD to run it, It has to be AC 3 Phase to be able to use the VFD you have, I see they do have some 800w spindles that are 3 phase, all the setting below will be correct except for the Amp settings, let us know what you are using for that amp setting

    If it won't take the settings you have the lock on PD000=0 you will have a (1 ) for this parameter, it needs to be 0

    Here are all the correct settings for your Drive

    Huanyang Mactec54
    PD000=0 for Parameter unlock ( 1 ) for Parameter Lock
    PD001=0 (1 For Remote Control)
    PD002=0
    PD003=400
    PD004=400
    PD005=400
    PD007=20
    PD008=220
    PD011=120 (Minimum Setting 120)
    PD009=15
    PD010=8
    PD13= 08 is for Factory reset, Only use this to set VFD to Factory Default Settings
    PD014 Accel=12 ( Adjust to suit)
    PD015 Deccl=12 (Adjust to suit) ( PD15 is ignored IF PD26=1 Then the Spindle will Coast to a Stop)
    PD141=220 ( Motor Rated Voltage )
    PD142=9 ( Motor Max Amps) (Set for your motor Amp Rating 2.2Kw Spindle 9 amp Max)
    (Set for your motor Amp Rating 1.5Kw Spindle 7 amp Max)
    PD143=2 ( Motor Number of Poles)
    PD144=3000 (Max Motor RPM) =3,000= (24,000)

    Mactec54


  4. #24
    Registered
    Join Date
    Sep 2014
    Posts
    3
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Great advice guys! Working like a champ with 24k rpm's now. Thanx again!!



  5. #25
    Registered MadeInTheShed's Avatar
    Join Date
    Jun 2009
    Location
    Australia
    Posts
    122
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Is there a way to get an "output" from these to control the cooling pump? I cant see the logic in having the cooling pump running when the spindle is not on, so was thinking that a signal could be sent to control a relay to switch the pump on if spindle was running.



  6. #26
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    24220
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Yes there are configurable outputs, depending on the model, PD050/051/052 = 5 'set frequency reach' is probably what you want, this I think is the same as the typical 'Up to speed' setting on most others.
    Al.

    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  7. #27
    Registered Christian Knüll's Avatar
    Join Date
    May 2010
    Location
    Germany
    Posts
    120
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Hi,

    you can set PD52 to 1 (if you have the same VFD I have).
    In this case the relay at FA/FB will close as soon as the VFD gets a "run" command.
    FA/FB is able to handle 3A / 250AC so you should usually be able to connect the pump directly.

    Christian

    My CAM Software and CNC Controller: www.estlcam.com


  8. #28
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    24220
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    I would use an external relay the internal ratings are for resistive load and if the internal one fails or motor overloads, you will be out of luck.
    Al.

    Last edited by Al_The_Man; 11-19-2014 at 11:35 AM.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  9. #29
    Registered MadeInTheShed's Avatar
    Join Date
    Jun 2009
    Location
    Australia
    Posts
    122
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Was planning on using a relay anyway, just wasnt sure if it could be done.

    Thanks for the advice



  10. #30
    Registered
    Join Date
    Feb 2015
    Location
    United States
    Posts
    9
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Hello World!!!
    I just installed a new Huanyang VFD and spindle on my CNC and I am having trouble. I have searched the WWW for help and no luck yet. I can press run and it will run fine, but I have to trip the breaker to shut it off. The stop button wont work, also there is no change while using the onboard pot. any help would be greatly appreciated.



  11. #31
    Registered
    Join Date
    Feb 2015
    Location
    United States
    Posts
    9
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Hello, I have set up my new Huanyang vfd with 2.2kw spindle. Firstly, the onboard potentiometer does nothing. But my big problem is that I can press RUN and it fires up and runs great, but the STOP button does nothing, I have to trip breaker to shut it off. What have I done wrong? Does it require an external on/off/for/rev switches and or pot?



  12. #32
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    phil35581

    Sounds like a parameter may be set wrong, compare these settings to what you have, these are all that needs to be set, unless you want to use some other functions

    Huanyang Mactec54
    PD000=0 for Parameter unlock ( 1 ) for Parameter Lock

    PD001=0 (1 For Remote Control)

    PD002=0

    PD003=400

    PD004=400

    PD005=400

    PD007=20

    PD008=220

    PD011=120 (Minimum Setting 120)

    PD009=15

    PD010=8

    PD13= 08 is for Factory reset, Only use this to set VFD to Factory Default Settings

    PD014 Accel=12 ( Adjust to suit)

    PD015 Deccl=12 (Adjust to suit) ( PD15 is ignored IF PD26=1 Then the Spindle will Coast to a Stop)

    PD141=220 ( Motor Rated Voltage )

    PD142=9 ( Motor Max Amps) (Set for your motor Amp Rating 2.2Kw Spindle 9 amp Max)
    (Set for your motor Amp Rating 1.5Kw Spindle 7 amp Max)

    PD143=2 ( Motor Number of Poles)

    PD144=3000 (Max Motor RPM) =3,000= (24,000)

    Mactec54


  13. #33
    Registered
    Join Date
    Feb 2015
    Location
    United States
    Posts
    9
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Mactec54
    Mine is set at 4 poles. Would that cause the pot and stopping issues?



  14. #34
    Member
    Join Date
    Jun 2013
    Posts
    443
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Hi Phil. I dont have an onboard pot on mine although with the numerous settings on these would imagine you may need to activate the unit to allow the speed to be controlled by the pot. Make sense? About the stop well that should work under all circumstances I would have thought? Mine is not just a quick press though I need to hold it down for half a second before my spindle starts to slow down. The only other reason I can see for it not working is mechanical. What ever is the easiest way, I would recommend you test it with a meter. Chinese are sometimes not very vigilant when they build stuff and a dud switch is well plausible.

    Actually mate just thinking I wonder if there is a setting that needs to be addressed there to allow the unit to be controlled by the front panel?



  15. #35
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by phil35581 View Post
    Mactec54
    Mine is set at 4 poles. Would that cause the pot and stopping issues?
    No but you need to set it to the 2 pole setting

    can you give more detail of how you have wired your pot

    PD001 needs to be set to=0 for the on/off to work

    Mactec54


  16. #36
    Registered
    Join Date
    Feb 2015
    Location
    United States
    Posts
    9
    Downloads
    0
    Uploads
    0

    Default

    Quote Originally Posted by mactec54 View Post
    No but you need to set it to the 2 pole setting

    can you give more detail of how you have wired your pot

    PD001 needs to be set to=0 for the on/off to work
    Pd001 is set to 0. I think it may be a faulty button on the inverter. I'm going to install external buttons today. Do I need to use normally open momentery buttons or full on/off toggle switches? And does the external pot need to be more than half watt rated?



  17. #37
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    phil35581

    The Pot needs to be 10K

    Mactec54


  18. #38
    Registered
    Join Date
    Feb 2015
    Location
    United States
    Posts
    9
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Hello.......I'm still having the same trouble.
    here are my settings......
    PD013=8 ( I started with this reset and did the rest in this order)
    005=400
    004=400
    003=400
    144=3000
    001=1
    002=1
    007=20
    008=220
    011=120
    009=15
    010=8
    044=2
    045=3
    046=4
    070=0
    072=400
    073=120
    141=220
    142=9
    143=2


    I am using a 10k ohm Pot with+10v on one end, ACM on the other end, and VI on the wiper.
    I am also using the 3 wire setup it shows in the manual for the FOR/REV/STOP/RUN functions. I am using 3 toggle switches.

    When I select forward it runs great......the problem is that the Pot will only let me speed it up from a slower setting, and it will not allow me to adjust it for slower speeds. meaning once it has reached a certain speed my only control is to speed it up more until max. ALSO, I still cannot stop it from running unless I trip the breaker.
    I ran the machine for several hours Friday and all went well. It barely gets warm at all. it is an air cooled spindle. I just need to figure out the speed problem and how to make it stop on command.

    Any help would be greatly appreciated. THANKS in advance.



  19. #39
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by phil35581 View Post
    Hello.......I'm still having the same trouble.
    I am also using the 3 wire setup it shows in the manual for the FOR/REV/STOP/RUN functions. I am using 3 toggle switches.
    I don't think it is a good Idea to use Toggle switches, to turn it, on/off, like you are, when using the 3 wire setup,your computer should be in control turning it on/off

    The buttons on the VFD will not function when you have the 3 wire setup connected,

    You have to use PD001=0 for the Buttons to work

    Your Pot wiring where are you getting the 10v from

    You will damage the VFD if you continue to turn it off from the Circuit Breaker

    Mactec54


  20. #40
    Registered Pplug's Avatar
    Join Date
    Jan 2007
    Location
    USA
    Posts
    723
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Even if you have computer control enabled, you can still stop the inverter by using the stop button on the inverters display.

    http://www.glenspeymillworks.com Techno LC4896 - 2.2Kw Water Cooled Spindle | Moving Table Mill from Omis 3 CMM, 500Lb granite base | Epilog Legend 32 Laser Engraver


Page 2 of 41 FirstFirst 1234512 ... LastLast

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

Huanyang Chinese VFD settings and manual here!

Huanyang Chinese VFD settings and manual here!