Sounds like the tuning is not quite right.
So i've swapped out my steppers for Clearpath Servos. I've run the through 'autotune' and they're and moving fine.
I've noticed that unlike steppers, when enabled, the servos don't lock hard, I can moved the gantry servo (master and slave) about 1/4" without too much effort. When jogging the gantry, I can see the slave servo move just a little bit after the master has stopped.
The steppers they replaced locked the gantry in place quite hard and it took some effort to jar it out of the place.
Is this normal???
UCCNC 2017 Screenset
I would agree Gerry!
The auto tune feature is pretty simple to go through, not sure what I might have screwed up.
About 14:34 into this video the host shows how hard it is to move the servo. That's what I would expect to see.
I'll have to try re-tuning in the morning.
when steppers are energized but idle they are locked, or rather they are at maximum 'holding' torque. They can be dislodged from their position
but it takes considerable effort.
A servo when energized but idle occurs when the controller is not issuing position commands, ie the last position command entered is the position the
controller expects the servo to stop. The servo stops at that position and actively tries to maintain that position. If some external force attempts to
shift the axis the servo/drive will try to counter that force so that it remains in its commanded (stationary) position.
Modern AC servos like your Clearpaths have a 'zero window'. It will vary by manufacturer but the same general idea applies.
My Allen Bradley servo for instance has a 2000 line/rev encoder for 8000 counts/rev. The default 'zero window' is 4 counts wide. That is to
say the drive will attempt to close the error between the commanded input and the actual position as measured by the encoder until it gets
to within 4 counts, thereafter it stops trying....in effect saying that within 4 counts is 'good enough'. Note I can program the 'zero window' to what I
like. It would not make sense to reduce it to zero or one though. That would mean the drive would keep trying to achieve perfect position even when it was
already very close and would 'buzz' as possibly get warm. On the other hand if I programmed the 'zero window' to 2000 say, to give a wild example, then
the drive would get to within 1/4 turn of its commanded position and then stop trying.....not especially useful for an axis servo.
From what you have described I believe your 'zero window' is too wide. What is happening, my guess, is that when you try to deflect the servo when its
at rest it moves a distance with little or no resistance because the drive deems that it is still 'good enough'. Only when you exceed that 'zero window' does the drive
start to apply a counter force.
I think amongst the different downloads I have a manual for Clearpaths. I will take a look...I think you have some programmatic control over the 'zero window'.
Craig
I've been running to auto tune on the gantry servo, it had the same problem. Going on a few hours, still doing something, but this is WAY beyond the normal auto tune run time.
I rather doubt AutoTune sets the 'zero window'. AutoTune is good but there are a lot of things that it does not do.
Craig
This is from the Clearpath manual. It is clear that there is programmatic control over the zero window or as Tecknics call it ASG.ASG-POSITION
ASG-Position mode is typically used as a “move done” signal. In this
mode, the HLFB output asserts (conducts) when ClearPath is enabled and
settled within X counts of the target position, for at least Y milliseconds
(you set X and Y in MSP via the Move Done Criteria dialog).
Craig
from page 67 of the manual.Move Done Criteria
Move Done status is used to determine when the All Systems Go-Position
signal should be asserted at the HLFB output. The Move Done Criteria
consist of two parameters: the “In-Range Window” and the “Verify Time”.
These parameters are explained in the screen capture, taken from MSP,
below.
Move Done Criteria Setup
How Move Done Works
Move Done status is achieved when the Move Done criteria are met. In the
above figure, Move Done occurs when the motor is within +/-10 encoder
counts of the commanded position (the In-Range Window) for a
minimum of 10.1 milliseconds (the Verify Time).
Note: If the encoder leaves the In-Range window during the time
qualification period, the Move Done timer automatically resets. The timer
will begin a fresh countdown as soon as the motor comes back in range.
Because encoder resolution, mechanical systems, and settling
performance requirements vary by application, you may need to
15 10 5 0 5 10 15
Move Direction
Encoder Scale
(1 line = 1 count)
Commanded Position (0) Actual Position (count 5)
In-Range Window +/- 10 counts
ENCODER
Craig
Servo's should be capable of zero movement under control of the PID loop up to the manuf rated continuous torque level when tuned correctly.
I've played with those settings and don't see any difference. I'm still able to move the servo.
I'll contact Teknic tomorrow and see if they can provide any assistance.
Hi everyone,
I'm an applications engineer for Teknic and I came across this post. I thought it might be helpful to provide some more information regarding ClearPath servos. (Bobmagnuson, you may have spoken with one of our other engineers already and hopefully solved this issue, but I figured I'd post more information in case anyone with the same problem comes across this post in the future.)
ClearPath motors (and all servo motors) will lock and hold position when energized and enabled. Even though you aren't actively sending steps to the servo, the motor will interpret the lack of new steps as a command to hold the current position. The servo will use as much torque as required (up to the motor's peak torque) to hold position and fight any external forces that are trying to move the motor off its commanded position.
Depending on how well the motor has been tuned, the motor's disturbance rejection will vary (i.e. how quickly the motor applies torque to counteract a sudden change in outside force such as you suddenly pushing on the mechanics). Greater disturbance rejection results in the mechanics feeling much stiffer. You would not be able to move the motor shaft very far before the motor uses its full peak torque to return to its commanded position. Low disturbance rejection can result in mechanics feeling "spongy". In that case, you'd be able to move the motor shaft farther before the motor uses torque to return to its commanded position.
In this situation, it sounds like you may have been trying to auto-tune a dual driven gantry. Unfortunately, auto-tune was not designed for these types of axes because there is no way to sync the auto-tune of two motors at the same time. Attempting to tune a dual-driven gantry by means of auto-tune could result in poor tuning since one motor will see the full load of the gantry.
If you were able to successfully complete auto-tune on a dual gantry, it's likely that the auto-tune did not achieve the proper gains for the system which could be causing the issue you are seeing. There are different, more optimal ways to tune a dual-driven gantry and Teknic would be happy to help you with that. (Here is a link to an application note to get you started: https://www.teknic.com/files/downloa...Motor-Axis.pdf )
I also wanted to touch on what joeavaerage mentioned. While some other servo motors may have a "zero window" or deadband, ClearPath motors will use full torque to return to the last commanded position (to the encoder count). The Move Done Criteria previously mentioned does not refer to how well the motor holds its position but instead refers to the motor's digital output called "HLFB" or "High Level Feedback". This output can be configured to alert the user/controller when ClearPath has reached its commanded position (this configuration is called "All Systems Go - Position").
Part of setting up the HLFB involves defining an "in-range" window, which is a number of position counts that the motor can be within to be considered "at target position". Even though the motor is "at target position" from the application's perspective, the motor understands that there is one specific encoder count that it was commanded to, and will still fight within its torque capability to reach and hold that exact position. As long as the motor is properly tuned, the motor will hold the commanded position.
I hope this information is useful. Please feel free to contact Teknic with any questions or if you need any help with tuning/troubleshooting this situation.
Best regards,
Bridgette G.
Teknic Inc.
Thanks Bridgette!
I was seeing the issue on both the Y axis (single servo) and the X axis (dual servos). They had been Auto-tuned per Teknic's recommendations and I was still seeing issues.
I've been working with Zach on the Teknic support team. We tried a few things and it appears that the Nema 23 Clearpath Servo's may be undersized for what I need.
I've got a big Nema 34 on order to see if it help resolve the issue.
Bob,
Were you bale to find a solution with this? I just installed Teknic servos and am running into the same issue. Thy are actually a little oversized and I have ran Auto tune with various settings but cannot get rid of the spongy feeling. Like yo, at rest I can move the carriage 1/4" each way but if I push gently with force it engages quickly.
This was part of a change out to Masso controller.
Any insight you have since would be appreciated.
One of the main problems with these servos is the cost and that they are only 3 Pole, most servos of the same class are from 6 to 12 Pole with the quality servos being 12 Pole so it does not matter what you do they are not going to hold the position very well, no amount of tuning can solve this problem
When you look at what is available for the same price and cheaper today these servo's don't stack up to be suitable for CNC machines no matter what the tec. guys say they can't solve these problems
Mactec54
So I am in the selection phase for a servo to drive a lathe. I would like the chuck to lock fairly absolutely for milling operations. Do you think given all the feedback so far that the difference between direct drive vs pulley drive and ratio, or the addition of a jack shaft to multiply/divide output rotation to servo rotation would be effective? Are any of the servo models better than others at locking position? Just throwing this out there. I want to buy once and set up once. Thanks.
the ability of a servo to resist deflection under an externally applied torque is exactly the same as the servos ability to produce torque against a load when commanded
to do so.
For instance my Delta servos have a rated torque of 2.4Nm, and an overload torque (10 sec) of 7.2Nm. Thus I would expect that the servo might resit deflection, in short
bursts, of torques up to 7.2Nm or 2.4Nm continuously.
You might consider a braked servo. Again using my 750W Delta servo as an example its rated brake holding torque is 2.5Nm. It seems quite common in industrial practice to
design a servo brake having a holding torque somewhat in excess of the rated servo torque.
As Matec pointed out multi-pole servos often have higher torque than a similar sized three pole servo and will do a better job of resisting deflection under applied torqe.
All-in-all I agree with Mactec, Clearpath servos while good quality and well designed for ease of use for new-comers are rather more expensive relative to their performance.
Delta and DMM are Taiwanese and Canadian brands respectively, both manufactured in China. Both are good quality and well supported at fair prices.
Yaskawa is deservedly the worlds leading servo manufacturer but are 150% and more the cost of Delta and DMM. Whether you can justify the extra cost depends on you,
or perhaps your wife...lol.
I would say that any gear or belt reduction between the servo motor and spindle will improve the holding capacity within the torsional rigidity of the gears/belts. Any torsional flex will
result in angular displacement of your workpiece.
Craig
I agree with everything you said. On my lathes jackshaft, which I had hoped to eliminate, is a drum wheel brake. It utilizes a lever actuated shoe and locks rotation absolutely. As a conundrum when you engage the shoe it rotates the jackshaft about 1 degree. Unfortunately I think that would cause the servo to begin to oppose the position change. To what effect I don't know. An absolute lock would appear to be illusive. My purpose/goal is machine turning. Absolute division is mandatory. I think I need to take another look at the original dividing head machines. Perhaps the chuck rotation is not the correct application for servos but the pattern cutting where position is mechanical and movement is a glancing cut. Thank you. Your insights have been helpful for me thinking this through.
EZ1