    Default Mitsubishi MR-J2s-A Help needed - alarm prob

    Hi

    got a MR-J2S-70A

    i have wired it up per manual on Single phase 230v
    it turns on fine, gives error "Servo Emergency Stop warning" AL E6
    which is fine.

    but when i close the estop switch for drive input it then comes up with

    Al E9 - "Main Circuit off warning"
    both main and control have power supplied and charge led is on
    not sure what main problem is here, something i have over looked probly?

    thank for any helps
    Rob

    Similar Threads:


  2. #2
    Registered
    Join Date
    Apr 2011
    Location
    Indonesia
    Posts
    1
    Downloads
    0
    Uploads
    0

    Default

    Need Help

    I am facing problem with Servo Drive MR-J2S-60B, MR-J2S-200B, MR-J2S-20B, MR-J2S-40A.
    The problem is =

    Al E9 - "Main Circuit off warning"
    both main and control have power supplied and charge led is on.

    I suspect there is abnormal chip on control board but don't know which one abnormal chip.
    I ever change only control board MR-J2S-200B with another servo drive in same type and the result is ok.

    I need help some body to find out abnormal chip cause Al E9.

    Thank you for any helps
    Best Regards


    harlin71@yahoo.com

    Last edited by harlin; 04-23-2011 at 04:40 AM.


  3. #3
    Registered
    Join Date
    Apr 2011
    Location
    Russia
    Posts
    2
    Downloads
    0
    Uploads
    0

    Default

    Hi

    I also have such trouble with J2S-10A/20A/60A amps.
    Al.E9 is displayed.
    The J2S software shows that main curcuit voltage is 160-170V. But actually it's 306-320V. It can be measured between N and P pins on 6-pin connector.



  4. #4
    Registered
    Join Date
    May 2011
    Location
    Malaysia
    Posts
    1
    Downloads
    0
    Uploads
    0

    Default

    hi there,
    I'm facing a installation problem which is the "AL E6" , do you all know how to solve this alarm occur?



  5. #5
    Registered
    Join Date
    Apr 2011
    Location
    Russia
    Posts
    2
    Downloads
    0
    Uploads
    0

    Default

    Quote Originally Posted by JLouis_Xabi View Post
    hi there,
    I'm facing a installation problem which is the "AL E6" , do you all know how to solve this alarm occur?
    It's fine.
    Connect EMG pin, see page 87 here http://www.hitex.se/robot/Manuals/MR...%20-%20ENG.pdf



  6. #6
    Member
    Join Date
    May 2006
    Location
    UK
    Posts
    107
    Downloads
    0
    Uploads
    0

    Default

    any one find a solution to the E9 problem as i did not and gave up in the end went with adifferent drive and motor

    rob



  7. #7
    Registered
    Join Date
    Jan 2009
    Location
    Australia
    Posts
    1
    Downloads
    0
    Uploads
    0

    Default Re: Mitsubishi MR-J2s-A Help needed - alarm prob

    Just had the same problem with my Mitsubishi MR-J2S 40A Servos. I had the AL-E6 and AL-E9 parameter codes
    - AL-E6 is the EMG stop (PIN 15 of CN1B) is not connected to SG ( PIN 10 of CN1B)
    (note these may be different on other models - check the MR-J2S manual in section 3.1)

    - AL-E9 is that the mains power is not connected to L1, L2, L3 ( just L1, L2 in single phase connection) as well as L11 and L21.

    In my case I am using single phase power so I connected the 240VAC single phase to L1 and L2 (and then Linked L1 to L11, and L2 to L21)
    This eliminated the AL-E9 Fault.

    Hope this helps,

    Cheers Rusty



  8. #8
    Registered
    Join Date
    Dec 2014
    Posts
    1
    Downloads
    0
    Uploads
    0

    Default Re: Mitsubishi MR-J2s-A Help needed - alarm prob

    hi
    i have the same problem with MR-J2S-40A.
    i have AL E6 alarm and what ever i do it dose not solve!!!
    even i connected the EMG to SG but it dose not solved!!
    is there any other solution for me??
    thanks



  9. #9
    Registered
    Join Date
    Sep 2015
    Posts
    1
    Downloads
    0
    Uploads
    0

    Default Re: Mitsubishi MR-J2s-A Help needed - alarm prob

    hi
    I have this problem, too.
    But i think i know something.
    I have a MR-J2S-40A amplifier. And my socket has 6 pin. P - C - D - L11 - L21 - N.
    My jack is 5 pin. And i pushed wrong area. I made a short circuit...
    I hope i can find the bad part of my amplifier.

    Do somebody have a wiring diagram for the ampifier?
    Great help for me...

    thx
    borcz



  10. #10
    Registered
    Join Date
    Mar 2013
    Location
    USA
    Posts
    6
    Downloads
    0
    Uploads
    0

    Default

    Quote Originally Posted by rusty1300 View Post
    Just had the same problem with my Mitsubishi MR-J2S 40A Servos. I had the AL-E6 and AL-E9 parameter codes
    - AL-E6 is the EMG stop (PIN 15 of CN1B) is not connected to SG ( PIN 10 of CN1B)
    (note these may be different on other models - check the MR-J2S manual in section 3.1)

    - AL-E9 is that the mains power is not connected to L1, L2, L3 ( just L1, L2 in single phase connection) as well as L11 and L21.

    In my case I am using single phase power so I connected the 240VAC single phase to L1 and L2 (and then Linked L1 to L11, and L2 to L21)
    This eliminated the AL-E9 Fault.

    Hope this helps,

    Cheers Rusty
    Please remember that on the 110v single phase driver you use L1 and L3 and leave the middle power terminal empty



  11. #11
    Registered
    Join Date
    Mar 2013
    Location
    USA
    Posts
    6
    Downloads
    0
    Uploads
    0

    Default

    Quote Originally Posted by kudos View Post
    any one find a solution to the E9 problem as i did not and gave up in the end went with adifferent drive and motor

    rob
    Yes if running on single phase leave the middle terminal empty and connect power to the two outside terminals



  12. #12
    Registered
    Join Date
    Mar 2013
    Location
    USA
    Posts
    6
    Downloads
    0
    Uploads
    0

    Default

    Quote Originally Posted by harlin View Post
    Need Help

    I am facing problem with Servo Drive MR-J2S-60B, MR-J2S-200B, MR-J2S-20B, MR-J2S-40A.
    The problem is =

    Al E9 - "Main Circuit off warning"
    both main and control have power supplied and charge led is on.

    I suspect there is abnormal chip on control board but don't know which one abnormal chip.
    I ever change only control board MR-J2S-200B with another servo drive in same type and the result is ok.

    I need help some body to find out abnormal chip cause Al E9.

    Thank you for any helps
    Best Regards


    harlin71@yahoo.com
    L1 is the far left and L2 is the far right terminal if using single phase



  13. #13
    Registered
    Join Date
    Mar 2013
    Location
    USA
    Posts
    6
    Downloads
    0
    Uploads
    0

    Default

    When hooking up single phase if you see an E9 error it’s because L1 is the far left terminal and L2 is the far right. Leave the middle terminal empty!!



  14. #14
    Registered
    Join Date
    Mar 2013
    Location
    USA
    Posts
    6
    Downloads
    0
    Uploads
    0

    Default

    Quote Originally Posted by harlin View Post
    Need Help

    I am facing problem with Servo Drive MR-J2S-60B, MR-J2S-200B, MR-J2S-20B, MR-J2S-40A.
    The problem is =

    Al E9 - "Main Circuit off warning"
    both main and control have power supplied and charge led is on.

    I suspect there is abnormal chip on control board but don't know which one abnormal chip.
    I ever change only control board MR-J2S-200B with another servo drive in same type and the result is ok.

    I need help some body to find out abnormal chip cause Al E9.

    Thank you for any helps
    Best Regards


    harlin71@yahoo.com
    L1 is the far left and L2 is the far right terminal if using single phase



  15. #15
    Registered
    Join Date
    Mar 2013
    Location
    USA
    Posts
    6
    Downloads
    0
    Uploads
    0

    Default

    Quote Originally Posted by kudos View Post
    any one find a solution to the E9 problem as i did not and gave up in the end went with adifferent drive and motor

    rob
    Yes if running on single phase leave the middle terminal empty and connect power to the two outside terminals



  16. #16
    Member servomotors's Avatar
    Join Date
    Feb 2020
    Posts
    6
    Downloads
    0
    Uploads
    0

    Default Re: Mitsubishi MR-J2s-A Help needed - alarm prob

    MR-J2S-40A is most best sale model for mitsubishi servo motors. J2S always have the problem when they run about 4-5 years, that means the servo driver need change a new one.



  17. #17
    Member mohamed_bayoudh's Avatar
    Join Date
    Dec 2020
    Posts
    1
    Downloads
    0
    Uploads
    0

    Default Re: Mitsubishi MR-J2s-A Help needed - alarm prob

    Salut

    j'ai un MR-J2S-60A

    Je l'ai câblé par manuel sur 230v monophasé,
    il s'allume bien, mais il donne l'erreur
    Al E9 - "Avertissement de circuit principal hors tension"
    je ne sais pas d'ou provient l'alarme.

    mercie d'avance pour tout vos aides.



Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

Mitsubishi MR-J2s-A Help needed - alarm prob

Mitsubishi MR-J2s-A Help needed - alarm prob