- Error Pin and the JMC iHSS60 Close Loop Motor Alarm Signal
-
Member
Error Pin and the JMC iHSS60 Close Loop Motor Alarm Signal
I am right in the assumption that I can connect the alarm signal (ALM + / Alm) of the Motos drivers with the Err pin of the Mk3 board. And if a fault in the Motor then stops the entire machine?
Alarm Signal: OC output signal, activated when one of the following protection is activated:
over- voltage and over current error.
They can sink or source MAX 8 mA current at 24 V, respectively 200 mW.
The impedance between ALM+ and ALM- is high for normal operation and becomes low when any protection is activated.
Can I pin it like that? Or do I need an optocoupler?
Similar Threads:
-
-
Member
Re: Error Pin and the JMC iHSS60 Close Loop Motor Alarm Signal
Have it as suspected clamped and configured in TNGv2. It works as desired.
-
Member
Re: Error Pin and the JMC iHSS60 Close Loop Motor Alarm Signal
I'm glad you figured this out.