Okuma Lathe LNC8 :907 alarm C lube flow 1


Results 1 to 5 of 5

Thread: Okuma Lathe LNC8 :907 alarm C lube flow 1

  1. #1
    Member Ryansway's Avatar
    Join Date
    Mar 2022
    Posts
    1
    Downloads
    0
    Uploads
    0

    Default Okuma Lathe LNC8 :907 alarm C lube flow 1

    Hey

    Just recently I had alarm come up on my LNC8 lathe showing a 907 alarm C Lube tank flow 1, thus far what I've been told is the tank has been replaced along with the manifolds, any help in clearing this alarm would be greatly appreciated, and the last maintenance guy said the operator got into the lube parameters and changed them around so does any 1 have a source for the parameters or a manual I could down load the fix this thing lol

    Similar Threads:


  2. #2
    Member
    Join Date
    Oct 2009
    Location
    world
    Posts
    114
    Downloads
    0
    Uploads
    0

    Default Re: Okuma Lathe LNC8 :907 alarm C lube flow 1

    Oil viscosity number is correct. Check the slideway oil iso number.



  3. #3
    Member broby's Avatar
    Join Date
    Apr 2006
    Location
    Australia
    Posts
    822
    Downloads
    0
    Uploads
    0

    Default Re: Okuma Lathe LNC8 :907 alarm C lube flow 1

    check that the suction side of the pickup in the tank is clear.
    Had this same error on my machine recently and the pickup was dirty for some reason.
    A quick clean and no more alarm.



  4. #4
    Member OkumaWiz's Avatar
    Join Date
    Apr 2009
    Location
    United States
    Posts
    1262
    Downloads
    0
    Uploads
    0

    Default Re: Okuma Lathe LNC8 :907 alarm C lube flow 1

    There should be a page in the parameter Mode that specifies the lube settings...That machine should have the 700U control. I believe that the parameters are set for ON 30 seconds, OFF 5 minutes. If the system doesn't build pressure, you will get that fault. Track down why...leak, pump intake like broby says, vactra#2 or equivalant, parameter set too short.

    Experience is what you get just after you needed it.


  5. #5
    Member
    Join Date
    Jan 2009
    Location
    USA
    Posts
    55
    Downloads
    0
    Uploads
    0

    Default Re: Okuma Lathe LNC8 :907 alarm C lube flow 1

    Years back on my mid '90's Cadet...I had a 907 alarm.....and when I pulled the pump unit off the reservoir I found that the pump driveshaft drive pin had sheared...replaced the pin and it's been good for 20 years now.



Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

Okuma Lathe LNC8 :907 alarm C lube flow 1

Okuma Lathe LNC8 :907 alarm C lube flow 1