Check the connections with SBP module(s).
No point to check the spindle drive unit before the SBP monitor error gone.
We recently purchased a MC-50VA machining center that has not run in several years. I know that I have an issue with the VAC 3 spindle drive because no power light comes on the drive when I power up. The controller (OSP5020M) loads files from memory and then come up with an error 82 VAC start 1001FFFF. It then halts with the controller saying "SBP monitor". (See attached picture of monitor and error codes) My question is will this error prevent the controller from starting up or do I have other problems that I am not aware of?
Thanks in advance for any help or ideas.
Check the connections with SBP module(s).
No point to check the spindle drive unit before the SBP monitor error gone.
When the control starts it attempts to communicate with all the drives and if it fails it will show alarm and go into SBP monitor failure mode. It will not boot until the communication error is cleared.
If possible swap out the drive unit with another to see if control will boot with the new drive.
Best regards
Experience is what you get just after you needed it.
Thanks for the input. Unfortunately I don't have another spindle drive to switch out with my current drive so it looks like I am going to have to get it powered up so it can communicate before I can go any further.