    Machine Macturn350 OSP100

    4035 ALARM- D Memory board/battery change 2
    2) A a certain period has passed since the software was initialised installed

    Has anyone instructions for this? Is there date in parameters which should be change after battery replace?

    Thanks,

    GB

    Similar Threads:


  2. #2
    Member OkumaWiz's Avatar
    Join Date
    Apr 2009
    Location
    United States
    Posts
    1102
    Downloads
    0
    Uploads
    0

    Default Re: OSP 100 Battery alarm 4035

    The battery has a set timer on it that will go off weather the bat is going dead or not. You can go to the battery page in your parameters and advance it a bit to get rid of the alarm temporarily but it’s best to replace it and set the date ahead by the several years as recommended. Was it seven? I forget...maybe my battery is getting weak... ;-)

    You will probably have to unhide the parameter page using display change.



    Best regards,

    Experience is what you get just after you needed it.


  3. #3
    Member
    Join Date
    Sep 2006
    Location
    Finland
    Posts
    202
    Downloads
    0
    Uploads
    0

    Default Re: OSP 100 Battery alarm 4035

    I have not found battery info page on OSP100 ? Which parameter page is it ?
    Thanks,
    GB



  4. #4
    Member kurmay's Avatar
    Join Date
    Aug 2011
    Location
    Haiti
    Posts
    266
    Downloads
    1
    Uploads
    0

    Default Re: OSP 100 Battery alarm 4035

    What is the OSP100?

    U100 , E100 or P100, which?

    Nothing.


  5. #5
    Member
    Join Date
    Sep 2006
    Location
    Finland
    Posts
    202
    Downloads
    0
    Uploads
    0

    Default Re: OSP 100 Battery alarm 4035

    it's U100L
    Model year:2003



  6. #6
    Member
    Join Date
    Sep 2006
    Location
    Finland
    Posts
    202
    Downloads
    0
    Uploads
    0

    Default Re: OSP 100 Battery alarm 4035

    Designer of this battery system has drinked sake. A lot.
    I found instructions here:
    https://www.cnczone.com/v...cedure-277828/
    Biggest problem was to found 3,5 inch floppy...
    Good luck to anyone with this problem.



Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

OSP 100 Battery alarm 4035

OSP 100 Battery alarm 4035

OSP 100 Battery alarm 4035