You may have your parameter set so that file names are not read. Try changing the name to A.MIN to see if it reads in ok.
Hi can anyone please help
I am having trouble with rs232 comm, I can send from the CNC to PC no problem
But everytime I send from the PC to CNC I get Alarm number 5229 INPUT FILE NAME NOT THE SAME
Even if I download a file change one character in the header and try to send back to the CNC I get the same alarm
The start of my program is as below
$TEST.MIN%
G13
T0404
G97 S1000 M03
Please any assistance will be appreciated
Graham
Similar Threads:
- Need Help!- Okuma LU-35 OSP 7000L IGF
- Newbie- Okuma LT10 OSP 7000L
- Need Help!- okuma impact lu 35 with okuma osp 7000l / tool touch off
- Need Help!- Okuma OSP 7000L ALARM 352
- Screendump OPUS-7000L
You may have your parameter set so that file names are not read. Try changing the name to A.MIN to see if it reads in ok.
Experience is what you get just after you needed it.
Hi
Thanks for your reply, but still getting 5229 INPUT FILE NAME NOT SAME
Thanks
Regards
Graham
What are you typing on the command line when attempting to read?
Experience is what you get just after you needed it.
I don't believe I have seen this error, but I don't transfer to OSP7000L, only OSP5000L or OSP5020L. That said I am just using a terminal program(terra term) to do my transfers. I have found that I have to receive a file in ASCII format but have to send the file in BINARY format. I don't know why that makes a difference but it does.
Dave
Hi
I do the following
PIP - READ
Then I type in "filename".MIN
Then I press WRITE
My file header is as follows:
$"filename".MIN%
Thanks for your assistance
Regards
Graham
place a comma BEFORE the filename....
this is essentially causing it to rename it
ok.sorry Wiz.. should give examples
PIP READ ,WRITE makes incoming prog be named A.MIN
PIP READ ,ABC123 WRITE forces prog to have a new name
(.MIN is set as default extension & is not required)
Last edited by Superman; 12-01-2018 at 07:10 AM.
Try PIP - READ - WRITE. The name is already in your header.
Using the comma before the file name will rename it as Superman says.
PIP - READ - oldfilename,newfilename - WRITE
Experience is what you get just after you needed it.
Hi Guys
Thanks using the comma worked
Now I have a different alarm when trying to read in the file
5238 RS232C device not ready
Any solutions will be greatly appreciated.
Regards
Graham
More info....
At the PC, is there any echo that data is actually passing through to the control ? ....... % at the end of file to inform control to close the file, & to terminate transmission
Are you reading in the SAME file that was punched out .... no editing ?
What transfer software are you using ?
Not ready means exactly that. There is not a READY signal. Either 4-5 need to be jumpered or else connected and being used by parameter setting to turn on ready signal. Usually they are jumpered and XON/XOFF is used ( software handshaking)