    Default Torus Pro Servo E-Stop Question.

    Hi folks, its been a while since my Torus Pro Servo edition has been assembled and working. So long, that I forgot how things operate...

    If I remeber correctly, when I physically haulted the E-Stop (Button) not software side. I recall the main power being shut off to the drivers and VFD. A reset of the E-Stop enabled the power and the Servo drives rebooted along with the VFD.

    Can anyone comfirm with me if this true?

    Right now I need to confirm this and see if I can use another Pin on the driver for a fault etc.

    Thanks,

    Crosshatch

    Similar Threads:


  2. #2
    Member
    Join Date
    Aug 2007
    Location
    usa
    Posts
    359
    Downloads
    0
    Uploads
    0

    Default Re: Torus Pro Servo E-Stop Question.

    ...

    Last edited by mklotz70; 04-12-2018 at 11:43 PM. Reason: incorrect info
    Don't have to be too bright to be me :)
    bluehandsvideo on youtube


  3. #3
    Member
    Join Date
    Feb 2006
    Location
    USA
    Posts
    7063
    Downloads
    0
    Uploads
    0

    Default Re: Torus Pro Servo E-Stop Question.

    With the stock wiring, the FAULT outputs from the servo drives are wire-ORed into the one of the E-Stop circuits on the BOB. Whenever E-Stop is asserted, whether due to hitting a limit, hitting one of the E-Stop switches, or a servo fault, ALL of the Step/Dir outputs from the BOB are disabled by logic on the BOB. The drives are left powered, but no longer receive step pulses, so the axes all stop as quickly as they can. Similarly, the spindle drive outputs (control voltage and FWD/REV signals) are also de-activated by the same logic on the BOB, so the spindle also stops as quickly as it can.

    Regards,
    Ray L.



  4. #4
    Member CROSSHATCH's Avatar
    Join Date
    Sep 2006
    Location
    US
    Posts
    1738
    Downloads
    0
    Uploads
    0

    Default

    Quote Originally Posted by SCzEngrgGroup View Post
    With the stock wiring, the FAULT outputs from the servo drives are wire-ORed into the one of the E-Stop circuits on the BOB. Whenever E-Stop is asserted, whether due to hitting a limit, hitting one of the E-Stop switches, or a servo fault, ALL of the Step/Dir outputs from the BOB are disabled by logic on the BOB. The drives are left powered, but no longer receive step pulses, so the axes all stop as quickly as they can. Similarly, the spindle drive outputs (control voltage and FWD/REV signals) are also de-activated by the same logic on the BOB, so the spindle also stops as quickly as it can.

    Regards,
    Ray L.
    Good to know, thinking I'm going to change to that setup and not cut all the power.

    Regards,

    Jason



Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

Torus Pro Servo E-Stop Question.

Torus Pro Servo E-Stop Question.