RPC = rotary phase converter
Braking resistor = that big gray thing in the first picture ( the long gray tube). I'll try to give a simple explanation of its purpose without getting too technical. This will not be exactly technically correct and only applies to electric motors connected to VFDs and similar drives. When the motor is told to stop, it becomes a generator and the power needs to go some where, so rather than feeding the power back into the VFD, the VFD shunts off that excess power to the braking resistor which in turn converts the excess power into heat. Very much like the brakes in your car work, they convert the momentum of your car into heat.
That CIMR-PCU40P2 VFD is a 460V, 1/2 HP rated. It
will not work for your spindle motor. If your motor is rated at 7.5 HP then you need a VFD rated at 7.5HP, and in this case you need 230V (200 - 240) input, not 460V (380 -460)
If you need help choosing a VFD, we'll be happy to help. And Mactec54 and I will argue about it
But my favorite vendor is Automation Direct.
https://www.automationdirect.com/adc...rpose/gs3-27p5