    Has anyone seen this during startup? Last 2 times I turned on the machine this came on. Turning it off and on makes it start up fine. Not sure why the error? This machine spends most of it's time turned off and has very few hours of cutting time on it.
    1206181438 by JAMES ANDERSON, on Flickr
    RH19plate by JAMES ANDERSON, on Flickr

    Similar Threads:


  2. #2
    Member
    Join Date
    Jul 2010
    Location
    USA
    Posts
    548
    Downloads
    0
    Uploads
    0

    Default Re: Error Message on startup

    Hi gunmaker, Error 187 is saying that the NCB board and the interface panel has lost communication.

    1st thing to check is the 5VDC power supply and check / set to 5.2VDC. if the 5V falls to 4.999999999V it will drop the communications. that is why it should be set to 5.2V.

    There are other possible problems, bad NCB board, interface problem. but lets check the easy stuff 1st.

    Give me a call 952-288-6340

    sportybob



  3. #3
    Member
    Join Date
    Feb 2007
    Location
    usa
    Posts
    68
    Downloads
    0
    Uploads
    0

    Default Re: Error Message on startup

    Thanks Bob. I'll get back to you after this weekend. Gotta maintain my kids car to get him back to college.
    James



Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

Error Message on startup

Error Message on startup