    Default Re: Any pics of cnc control cabinets?

    Finally getting around to doing this. Question on dc power distribution. should I just ground all my dc power supplies to the panel, as well as ground all components needing dc power to panel, and then just wire the positive to each component? Or is it better to actually wire the positive and negative from component to power supply? Electrically I don't think there's a difference, but not sure if one way or the other is proper. Seems like a lot less wiring if just grounding everything straight to panel.



  2. #22
    Member
    Join Date
    Oct 2004
    Location
    usa
    Posts
    178
    Downloads
    0
    Uploads
    0

    Default Re: Any pics of cnc control cabinets?

    I would not ground the DC power to the cabinet. It's just asking for problems. I keep all my DC circuitry isolated from the high voltage.



  3. #23
    Member QuinnSjoblom's Avatar
    Join Date
    Nov 2017
    Location
    bigfork
    Posts
    591
    Downloads
    0
    Uploads
    0

    Default

    Quote Originally Posted by greggv View Post
    I would not ground the DC power to the cabinet. It's just asking for problems. I keep all my DC circuitry isolated from the high voltage.
    That would mean I would need to isolate every component from the panel. The gecko g540, Ethernet smoothstepper, dmm bob, etc. Should these really not be grounded to the cabinet? Also, doesn't the a.c. ground on the power supply input already pass through to the dc ground output?



  4. #24
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    24216
    Downloads
    0
    Uploads
    0

    Default Re: Any pics of cnc control cabinets?

    A unwritten law is that the enclosure you order always ends up being at least 5% too small!
    I have often got deals on used enclosures off ebay, some came with disconnect, terminals, P.B.'s etc, I even got one that was stainless!
    I have always earth grounded my DC supplies where possible to the Star ground point, the service ground should also terminate there.
    I have even put two VFD's in the same enclosure as the rest of the control.
    For hook up wire, of course always use stranded conductor and my favorite is TR64 as the insulation is much smaller and avoids filling up the wire trough.
    Another general rule is to place heat producing items at the top of the enclosure.
    Al.

    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  5. #25
    Member QuinnSjoblom's Avatar
    Join Date
    Nov 2017
    Location
    bigfork
    Posts
    591
    Downloads
    0
    Uploads
    0

    Default Re: Any pics of cnc control cabinets?

    Sounds like I need to stop and get a better understanding of proper grounding. There seems to be some mixed opinions on whether or not to tie earth ground to dc common. I always assumed everything should be grounded to the same ground. Currently my dc components are grounded to the small enclosure I have, as well as the a.c. ground and it hasn't caused any issues, but maybe not the proper way to do it? Just wamt to make sure i have this right before spending time on the new cabinet



  6. #26
    ericks
    Guest

    Default Re: Any pics of cnc control cabinets?

    Hi, i connect the mains earth to anywhere where it is required/where there is an indicated earth connection. But i do not tie/connect the neg of any SMPSU to earth



  7. #27
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    24216
    Downloads
    0
    Uploads
    0

    Default Re: Any pics of cnc control cabinets?

    Quote Originally Posted by QuinnSjoblom View Post
    Sounds like I need to stop and get a better understanding of proper grounding.
    There are two schools of thought out there, some that say you should never ground any of the DC supply commons, the other is to earth reference all supplies, I have always followed the latter practice, with so far no problems, there was a post here a while ago where a poster was experiencing all kinds of intermittent stoppages of his system where he had followed the isolation method, I suggested that he use the ground all method, where possible, the problem went away, there have been others where it has fixed the problem.
    A star ground termination point is also very important.
    There used to be a paper on the Siemens site on Equi-potential bonding in enclosure installations, but after they changed their web site, it dissapeared, I may have a copy somewhere.
    Al.

    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  8. #28
    Member
    Join Date
    Jun 2010
    Location
    Australia
    Posts
    4252
    Downloads
    4
    Uploads
    0

    Default Re: Any pics of cnc control cabinets?

    STAR grounding: everything to a single solid ground point.
    Essential to prevent 'ground loops', which can be really disruptive.

    Cheers
    Roger



  9. #29
    Member QuinnSjoblom's Avatar
    Join Date
    Nov 2017
    Location
    bigfork
    Posts
    591
    Downloads
    0
    Uploads
    0

    Default

    Quote Originally Posted by RCaffin View Post
    STAR grounding: everything to a single solid ground point.
    Essential to prevent 'ground loops', which can be really disruptive.

    Cheers
    Roger
    I understand the importance of star grounding to avoid loops, but are you grounding both ac ground and dc common to this single point, or isolating the 2?



  10. #30
    Member
    Join Date
    Jun 2010
    Location
    Australia
    Posts
    4252
    Downloads
    4
    Uploads
    0

    Default Re: Any pics of cnc control cabinets?

    I use star grounding for all DC electronics, then I tie that star ground point to the the incoming mains ground. I do not gain or lose axis Step pulses.

    I suspect that workplace safety laws will require full connection to the mains ground in all cases unless the entire machine is double isolated - which would be pretty much impossible for a CNC machine.

    Cheers
    Roger



  11. #31
    Member QuinnSjoblom's Avatar
    Join Date
    Nov 2017
    Location
    bigfork
    Posts
    591
    Downloads
    0
    Uploads
    0

    Default

    Quote Originally Posted by RCaffin View Post
    I use star grounding for all DC electronics, then I tie that star ground point to the the incoming mains ground. I do not gain or lose axis Step pulses.

    I suspect that workplace safety laws will require full connection to the mains ground in all cases unless the entire machine is double isolated - which would be pretty much impossible for a CNC machine.

    Cheers
    Roger
    Currently I have my machine wired the same way. Dc grounded to earth. I have hundreds of hours of run time without a single lost step or any hiccup at all. I think I'll just stick to how it's been. Right now it's just kind of messy and needs to be better organised with a few things added. Servo driven mill turn spindle, multiple solenoids for brake, coller closer, and coolant lines.



  12. #32
    Member ger21's Avatar
    Join Date
    Mar 2003
    Location
    Shelby Township
    Posts
    35538
    Downloads
    1
    Uploads
    0

    Default Re: Any pics of cnc control cabinets?

    Some components require the DC supply to be isolated. Connecting the DC- to ground loses the isolation.

    Gerry

    UCCNC 2017 Screenset
    [URL]http://www.thecncwoodworker.com/2017.html[/URL]

    Mach3 2010 Screenset
    [URL]http://www.thecncwoodworker.com/2010.html[/URL]

    JointCAM - CNC Dovetails & Box Joints
    [URL]http://www.g-forcecnc.com/jointcam.html[/URL]

    (Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management)


  13. #33
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    24216
    Downloads
    0
    Uploads
    0

    Default Re: Any pics of cnc control cabinets?

    Quote Originally Posted by ger21 View Post
    Some components require the DC supply to be isolated. Connecting the DC- to ground loses the isolation.
    And often component suppliers will stress not to earth ground the common of their equipment, from what I have personally gleaned it is often not because of a technical reason, but to avoid any blame if you do ground it and if something inadvertently goes wrong with the installation you can blame their equipment.
    If there is no technical reason otherwise, I have always ignored it and grounded anyway, with no ill results.
    Al.

    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  14. #34
    Community Moderator Jim Dawson's Avatar
    Join Date
    Dec 2013
    Posts
    5717
    Downloads
    0
    Uploads
    0

    Default Re: Any pics of cnc control cabinets?

    A little late to the discussion, but I have been running the DC return to earth ground for years, works for me. One instance of where you would not want to do this is in the case of direct rectified line power without an isolation transformer, Anilam built a lot of systems like this. Grounding that would cause a dead short. As Gerry noted there are some other exceptions, but normally it is a good practice IMHO

    Jim Dawson
    Sandy, Oregon, USA


  15. #35
    Member QuinnSjoblom's Avatar
    Join Date
    Nov 2017
    Location
    bigfork
    Posts
    591
    Downloads
    0
    Uploads
    0

    Default

    Quote Originally Posted by Jim Dawson View Post
    A little late to the discussion, but I have been running the DC return to earth ground for years, works for me. One instance of where you would not want to do this is in the case of direct rectified line power without an isolation transformer, Anilam built a lot of systems like this. Grounding that would cause a dead short. As Gerry noted there are some other exceptions, but normally it is a good practice IMHO
    Ok, I know you've set up a lot of control cabinets so I'll just continue to do it this way. It's how I'm set up currently and my machine has been 100% reliable.



  16. #36
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    24216
    Downloads
    0
    Uploads
    0

    Default Re: Any pics of cnc control cabinets?

    Also one publication aimed at machine/enclosure wiring is NFPA79, you most likely can find a copy out there in PDF.
    I would add that just about anything used in a PC desktop/tower environment is going to be earth grounded simply because it is automatically done in the PC, e.g. P.ports, USB ports. Kmotion etc as well as any card that plugs into a PC slot, Galil, Acroloop, etc. are all connected to the PC ground plane that is earth grounded via the service supply.
    Al.

    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  17. #37
    Member
    Join Date
    Jan 2010
    Location
    USA
    Posts
    44
    Downloads
    0
    Uploads
    0

    Default Re: Any pics of cnc control cabinets?

    Hey Guys,
    I realize this thread has been on vacation for a month, but I have a couple of related questions.
    I've been running desktop CNC's for 5 years or so and have always tried to keep my wiring neat and isolated, but I'm getting ready to upgrade my machine from a Gecko G540 and open loop steppers to LeadShine controllers and closed loop steppers, so I need to design and build a new control cabinet. I'd like to use DIN rails and components.
    My question(s) are:
    Where is a good reference for general (or more specific) design standards? I appreciate Al_the_Man's link to the NFPA79 document and will search that out. Without going back to school and getting an electronic engineer's degree, are there others?
    Where can I find direction on which components to use for specific functions? I know that's kind of vague, but for instance, it looks to me like a Contactor and a Relay both perform the same general function - turning an electrical component on or off - but when do you use one over the other? Or do I have that functionality wrong?
    I also have questions about when and where to use circuit breakers - only on 120V supply circuits or others in addition?
    Thanks in advance for any guidance,
    Gary



  18. #38
    Community Moderator Jim Dawson's Avatar
    Join Date
    Dec 2013
    Posts
    5717
    Downloads
    0
    Uploads
    0

    Default Re: Any pics of cnc control cabinets?

    Gary, you ask hard questions. This arcane knowledge is normally only passed down from the master to the apprentice, over a period of years. I don't know of any books on the subject other than NFPA, NEMA and UL codes.

    In general you want supplementary protection (fuses or breakers) on both sides of a power supply or transformer.

    Motor loads and drives should be individually protected on the power input side. Normally follow the device manufacturers guidelines for proper protection sizing and type, wire size will be determined by the protection device rating.

    A contactor and a relay are functionally the same. But a contactor is normally directly switching the load (motor or other higher energy device), and a relay is switching the control side of things.

    I hope this makes sense. There is a lot more, but it's pretty hard to try to condense 50 years of experience into a post.

    Jim Dawson
    Sandy, Oregon, USA


  19. #39
    Member
    Join Date
    Jan 2010
    Location
    USA
    Posts
    44
    Downloads
    0
    Uploads
    0

    Default Re: Any pics of cnc control cabinets?

    Jim,
    Thanks for the quick reply.
    Your advice helps me make a better start.
    Gary



  20. #40
    Member
    Join Date
    Jun 2010
    Location
    Australia
    Posts
    4252
    Downloads
    4
    Uploads
    0

    Default Re: Any pics of cnc control cabinets?

    What Jim said: it is a matter of experience and judgement, not of 'rules' (apart from things like the UL guidelines, which are mainly for safety rather than 'good practice').

    Contactors are usually 'bigger' than relays - in voltage and current.

    I have over-current cutouts on each motor driver. You should NOT turn them off that way under normal circumstances, but they do handle cases where the axis has run into a hard limit and the motor current tries to go skywards.

    Neat and tidy, with adequate protection, is always good. GOOD documentation is a pain to create, but utterly vital later on.

    Cheers
    Roger



Page 2 of 3 FirstFirst 123 LastLast

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

Any pics of cnc control cabinets?

Any pics of cnc control cabinets?