    Default Overcurrent Protection

    Dear Experts

    We have a SPM. Spindle motor is thro Star Delta contactor and overload relay with Main Contactor
    Spindle stopped running as its bearing sieged very badly

    Request to suggest better protective device having faster response to trip and avoid such seizure of bearings etc

    Thanks and Regards

    Similar Threads:


  2. #2
    Member CitizenOfDreams's Avatar
    Join Date
    Nov 2012
    Location
    USA
    Posts
    1267
    Downloads
    4
    Uploads
    0

    Default Re: Overcurrent Protection

    There should be a thermal overload relay between the contactor and the motor. The relay should be selected and adjusted for the nominal current of the motor.









  3. #3
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: Overcurrent Protection

    Quote Originally Posted by M.RISHIKESH View Post
    Dear Experts

    We have a SPM. Spindle motor is thro Star Delta contactor and overload relay with Main Contactor
    Spindle stopped running as its bearing sieged very badly

    Request to suggest better protective device having faster response to trip and avoid such seizure of bearings etc

    Thanks and Regards
    A Bearing can seize at any time, a thermocouple can be added to the bearing housing and set for to trip the contactor once it reaches it's max operating temperature most large AC motors already have overtemperature protection with built in thermistors if wired in to the system they to would of protected the motor

    If you are running a VFD Drive this is easy to setup to shut down if it see an over current, so as the bearing was getting hotter it would of been drawing a higher current and the VFD Drive would of shut down as an over current fault

    Mactec54


Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

Overcurrent Protection

Overcurrent Protection