Update and current status...
There were two ways I was able to monitor the problem: False triggers of buttons from the operator panel and my Scope. Being that the false triggers appeared to come from the buttons and switches attached to the I-PAC (keyboard emulator), I figured I would connect my scope to that device which is located inside the operator panel.
Here is a trace that was captured with the spindle running. The spikes were about 3.8 volts as measure on one of the inputs to the I-PAC. With about 30 inputs on the I-PAC, I was getting some really strange things happening.
Trying to determine if the noise is conducted or radiated, I removed the cable from between the electrical cabinet and the operator panel. The voltage spike is reduced to about 2 volts. Being that, aside from the AC power, there was no mechanical connection and the voltage spikes are still present, I could only assume I had both, conductive and radiated noise. At this level, there were no problems of false triggers and the machine ran fine. Here is the trace showing that.
From the advice of Mactec, I purchased and installed a line filter. At first I didn't understand how that would even help this problem, but then I realized this device is very similar to a "Reactor" which is used on industrial CNC machines for preventing noise issues. This is the link to the line filter
https://www.amazon.com/gp/product/B0...?ie=UTF8&psc=1. Once installed, there was an immediate improvement in the noise levels...
However, the presumably radiated noise was still there. As this did not affect operation of the machine, I wasn't too worried about it.
I continued to tidy up the wires and prepare to close up the electrical cabinet and the operator panel. I performed one last check with the scope. During my tidy up process, more improvement occurred, unfortunately, I have no idea what changed to remove the radiated noise. I know I pushed all the wires back into the plastic conduit, I recall reattaching the 220VAC ground wire be (from source) and at the line filter and I am sure I did a few more things but can't recall all the details. Here is the trace before I closed everything up..
Knowing that I had a working system at one point, then this noise issue came up, I am not 100% certain the problem isn't fixed. The problem very well could come back again but for now I am a happy camper.
Here is a photo inside the electrical cabinet just before closing. The Line filter was attached to the 35 Volt power supply, probably not the best thing to do, but currently there are no ill effects and it was a handy place to mount it. As mentioned in an earlier post, I was worried about accidental shocks being that the posts on this thing are fully exposed, I designed and 3D printed a red cover for it so that it would be a bit more safe then being fully exposed.
What a nightmare this problem was and to deal with. I am hoping that it is over and I learned a few things along the way.
Thank you to all of you guys for your help and guidance!
Chris D