    Quick question: can I chain the fault output of mutlitple CS-D508 drivers like this?
    Attachment 463809


    (details on p10 of this manual: http://leadshineusa.com/UploadFile/D...-D508_m3.1.pdf)

    Thx a lot!



  2. #2
    Registered
    Join Date
    Dec 2013
    Posts
    8
    Downloads
    0
    Uploads
    0

    Default Re: chain leadshine fault outputs?

    Please somebody! Maybe my schematic isn't clear enough?



  3. #3
    Member CitizenOfDreams's Avatar
    Join Date
    Nov 2012
    Location
    USA
    Posts
    1267
    Downloads
    4
    Uploads
    0

    Default Re: chain leadshine fault outputs?

    The manual does not explicitly say whether the alarm logic is positive or negative. If it is what I think it is, you can connect all ALM+ and ALM- outputs in parallel. An alarm in any driver(s) will pull the FAULT signal low.



  4. #4
    Member
    Join Date
    Jan 2018
    Location
    United Kingdom
    Posts
    1516
    Downloads
    0
    Uploads
    0

    Default Re: chain leadshine fault outputs?

    I can't see why not.
    Your attachment file doesn't work so I can't see how you wired it. So........

    If the ALM circuit is normally closed NC when drive is active and opens the circuit NO when a fault happens, then you would wire them in series.
    If the ALM circuit is normally open NO when drive is active and closes the circuit NC when a fault happens, then you would wire them in parallel.
    It says the ALM is configurable to a certain extent so this could possibly be adjustable.
    Manual suggests the alarm circuit sinks to ground.

    This circuit can then go to one of your controllers optocoupler inputs to trigger a stop.
    Or if your controller has lots of inputs, then you could just do them individually and assign each one.
    Or even use a multi channel optocoupler module between the two.

    Depending on your controller software you could assign one of the buttons such as stop or feed hold etc.



Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

chain leadshine fault outputs?

chain leadshine fault outputs?