Need Help! new hypermax 65 (cpc) with fanuc 100ic robot connection guided


Results 1 to 4 of 4

Thread: new hypermax 65 (cpc) with fanuc 100ic robot connection guided

  1. #1
    Member
    Join Date
    Sep 2007
    Location
    india
    Posts
    6
    Downloads
    0
    Uploads
    0

    Default new hypermax 65 (cpc) with fanuc 100ic robot connection guided



  2. #2
    Moderator
    Join Date
    Jan 2008
    Location
    USA
    Posts
    2247
    Downloads
    0
    Uploads
    0

    Default Re: new hypermax 65 (cpc) with fanuc 100ic robot connection guided

    The Plasma interface is simple.

    -To start the plasma arc close a set of contacts on pins 3 and 4 of the CPC port. To stop the plasma, open that set of contacts.
    - For verification that the plasma arc is cutting, monitor the output of the arc transferred signal at pins 12 and 14 of the CPC port. When the arc is cutting metal, pins 12 and 14 will be connected (closed), when not cutting metal, pins 12 and 14 will be open.
    -If you need to monitor DC analog arc voltage (used for height control feedback) you can monitor this voltage at pins 5 and 6 of the CPC port. The factory default voltage setting is 1/50th of actual arc voltage. There are dip switches that allow you to set a variety of different ratios for this voltage feedback.

    All of this information is clearly covered in the Powermax65 Operators manual.

    Jim Colt Hypertherm



  3. #3
    Member
    Join Date
    Sep 2007
    Location
    india
    Posts
    6
    Downloads
    0
    Uploads
    0

    Default Re: new hypermax 65 (cpc) with fanuc 100ic robot connection guided

    I am using powermax 65 spurce with Fanuc 100ic/8l robot
    need help for setting
    cpc out put data connected to Analog input module(AAD04A)
    divider set to 50:1(hypertherm)
    on tech pendant weld IO setting (it shows graph AI-weld voltage)AI(min-max)--i set min-0 and max -10V and weld voltage 139v max and 0v minimum is it right ?
    or weld voltage max will be 139/50=2.78v max and min-0 ? or max 395v-min 0v..?
    please suggest as height controll with AVC in robot can not be optimised.
    please refer picture of ipendant.
    upowermax robotics/cnc interface-image-jpegnew hypermax 65 (cpc) with fanuc 100ic robot connection guided-image-jpeg



  4. #4
    Member
    Join Date
    Sep 2007
    Location
    india
    Posts
    6
    Downloads
    0
    Uploads
    0

    Default Re: new hypermax 65 (cpc) with fanuc 100ic robot connection guided

    Default Re: new hypermax 65 (cpc) with fanuc 100ic robot connection guided

    I am using powermax 65 spurce with Fanuc 100ic/8l robot
    need help for setting
    cpc out put data connected to Analog input module(AAD04A)
    divider set to 50:1(hypertherm)
    on tech pendant weld IO setting (it shows graph AI-weld voltage)AI(min-max)--i set min-0 and max -10V and weld voltage 139v max and 0v minimum is it right ?
    or weld voltage max will be 139/50=2.78v max and min-0 ? or max 395v-min 0v..?
    please suggest as height controll with AVC in robot can not be optimised.
    please refer picture of ipendant.
    upowermax robotics/cnc interface-image-jpegnew hypermax 65 (cpc) with fanuc 100ic robot connection guided-image-jpeg



Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

new hypermax 65 (cpc) with fanuc 100ic robot connection guided

new hypermax 65 (cpc) with fanuc 100ic robot connection guided