    Default Hurco bmc 40/20 ultimax 3 control boot issues?

    Hello all,
    Hopefully someone has run across this problem! I power up the machine has no issues runs through the normal boot process until we get to where I should be powering the control up. Sometimes it will show a bunch of errors like heat sink,motor over temp, sometimes it will say all that then it will go away and say way lube low (it’s full?) or say low air pressure (has good air?) so not sure where to start. My guess is it is in the drive? It has Siemens simodrive 611.Anyone ever had this problem? Thanks in advance!!!

    Similar Threads:


  2. #2
    Community Moderator Jim Dawson's Avatar
    Join Date
    Dec 2013
    Posts
    5717
    Downloads
    0
    Uploads
    0

    Default Re: Hurco bmc 40/20 ultimax 3 control boot issues?

    Bad connection on the sensor common maybe? 24 volt power supply getting a bit weak, slow to come up to voltage?

    Jim Dawson
    Sandy, Oregon, USA


  3. #3
    Registered
    Join Date
    Oct 2009
    Location
    usa
    Posts
    4
    Downloads
    0
    Uploads
    0

    Default

    That is my other guess is power supply. We had a guy that worked on hurco’s at the last place I worked every time something was wrong seemed like he changed the power supply that would seem to be the cheaper route to start with. We took the I/r module out and tested what we could but we are limited on knowledge lol



  4. #4
    Member
    Join Date
    May 2017
    Location
    United States
    Posts
    58
    Downloads
    0
    Uploads
    0

    Default

    [QUOTE=hack&wack;2197232]
    I had a very similar problem that was occuring on a hawk 5m with max 3. Here is what I did and iether the combination or the last few steps fixed my issue. I pulled and cleaned contacts on all boards and seating conectors. Cleaned all plugs. Then relays. It still would throw lube error now and then so I next swapped out RAM and cleaned conector to the hard drive. Ensure a good ground to all components.



Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

Hurco bmc 40/20 ultimax 3 control boot issues?

Hurco bmc 40/20 ultimax 3 control boot issues?