Heidenhain 355 controller

Results 1 to 2 of 2

Thread: Heidenhain 355 controller

  1. #1

    Default Heidenhain 355 controller

    Good morning,
    I have recently purchased an old bridgeport machining centre which has heidenhain contol. The controller is a TNC 355.
    I am currently using TNC server (a heidenhain program) to drip feed the program into my machine.
    The issue i am facing is that it will quickly state "wrong data input" on my machine after only a few lines of program.
    I have been told that my program data needs to start and end with a particular code or number for the machine to recognize? of which i am not sure.
    Also, i am using solidcam post processer which only gives me and option to export it into a H file of for TNC 426 controller , could this be the issue? Does my 355 controller need read the program data differently ?
    Any help would be greatly appreciated.
    Thankyou guys.
    Max
    Sydney AUS

    Similar Threads:


  2. #2
    Member machinehop5's Avatar
    Join Date
    Aug 2009
    Location
    United States
    Posts
    1567
    Downloads
    5
    Uploads
    2

    Default Re: Heidenhain 355 controller

    ...Search for "HEIDENHAIN TNC355 service manual" I see something about "Blockwize Transfer" MP223 would be 1 and for "Standard interface" set to 0. Look in Chapter 11 for more settings.
    good luck

    Attached Files Attached Files


Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

Heidenhain 355 controller

Heidenhain 355 controller