    Default HAAS SL-20 ALARM 292 320V POWER SUPPLY

    Hi all,

    i have a Haas SL-20 2007, when i power up a have the alarms below:

    102 SERVO OFF
    292 320 POWER SUPPLY FAULT
    107 EMERGENCY OFF

    There in no other alarm and it doesn't come off when I cycle the power.
    when I measure the dc power output is 325v and the DC BUSS in the dignosys is the same 325v
    when called my HFO (ho is 600km away ) he told me to change the regen and i did it without any change.

    do you have any ideas please???????

    thank you in advance

    Similar Threads:


  2. #2
    Member Turbo442's Avatar
    Join Date
    May 2011
    Location
    United States
    Posts
    308
    Downloads
    0
    Uploads
    0

    Default Re: HAAS SL-20 ALARM 292 320V POWER SUPPLY

    I’m not an expert on this but…

    Will the error clear if you hit the reset button rapidly 3 or 4 times in a row?

    What is your parameter 294 set to? Is it 270 ? You could temporarily try setting this value to 0 and see if that works after a power cycle. The vector drive might be reporting the wrong voltage to the maincon.


    Sent from my iPhone using Tapatalk



Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

HAAS SL-20 ALARM 292 320V POWER SUPPLY

HAAS SL-20 ALARM 292 320V POWER SUPPLY