    Hello,
    So I am in the processes of upgrading an old plasma table. We are in a rented shop and are unable to put in a true earth ground for the table. There is a structural beam that goes 10' to 15' into the earth near by. Am I able to tie into that as an earth ground? Any advice would be much appreciated.
    Thank you for your time
    Kacey

    Similar Threads:


  2. #2
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    24220
    Downloads
    0
    Uploads
    0

    Default Re: Earth Ground

    Yes, you should be able to use this as a earth ground source, but it is also typical to include the service GND at this point.
    I am assuming that a earth conductor exists in the service supply?
    Al.

    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  3. #3
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: Earth Ground

    Quote Originally Posted by Kgarety View Post
    Hello,
    So I am in the processes of upgrading an old plasma table. We are in a rented shop and are unable to put in a true earth ground for the table. There is a structural beam that goes 10' to 15' into the earth near by. Am I able to tie into that as an earth ground? Any advice would be much appreciated.
    Thank you for your time
    Kacey
    The True Earth Ground is at your building service Panel that is what you should be using any structural building member should be ok as well, but is not normal that you would use them, so check with your local electrical code requirements or an industrial electrician

    Mactec54


  4. #4
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    24220
    Downloads
    0
    Uploads
    0

    Default Re: Earth Ground

    Just to clarify my post on #2 it was to indicate that the earth ground via the structural beam was the normal practice of grounding a Plasma table with a local ground rod, not to use it as the principle earth ground.
    Any local ground rod at the table should always be bonded to the service earth ground.
    Al.

    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  5. #5
    Member
    Join Date
    Sep 2011
    Location
    Italy
    Posts
    11
    Downloads
    0
    Uploads
    0

    Default Re: Earth Ground

    if you have a plasma with high frequency you may have problems with noise or even failures on electronic boards
    Regards
    Alfonso AQ TECNO



Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

Earth Ground

Earth Ground