    Default mitsubishi meldos 310 - dnc problem

    any body help me with mitsubishi meldas 310 mill

    when i transfer a program (this program creat by power mill & send to the machine by cimco edit ) to the memory & execute this program from memory i dont have any problem & the xyz axis run very good &smooth & countiuse but when i want to run this program from pc by direct connection (dnc mode) yhe xyz axis dont run smooth & i have a step-by-step move (like this -----) two program are same and all setting in cnc are also same

    Similar Threads:


  2. #2
    Member dcoupar's Avatar
    Join Date
    Mar 2003
    Location
    USA
    Posts
    2932
    Downloads
    0
    Uploads
    0

    Default

    What baud rate are you communicating at? What feedrate are you programming? How long are the line segments you are interpolating? Sounds like the baud rate is too low for the feedrate you have programmed.



  3. #3
    Registered
    Join Date
    Jan 2008
    Location
    iran
    Posts
    7
    Downloads
    0
    Uploads
    0

    Default buadrate

    feedrate is 2000mm)min and baudrate is 9600 but in meldos catalog say the max baudrate is 1240



  4. #4
    Member dcoupar's Avatar
    Join Date
    Mar 2003
    Location
    USA
    Posts
    2932
    Downloads
    0
    Uploads
    0

    Default

    I'm not familiar with the Meldas 310, but I'm pretty sure there is no such baud rate. 110,300,600,1200,2400,4800,9600 are all pretty standard, but 1240?

    I'm also not familiar with Cimco Edit's DNC settings, but check to see if there's either "Character Send Delay", or "Line Send Delay" or anything like that that could be slowing the transmission down.



  5. #5
    Registered
    Join Date
    Jan 2008
    Location
    iran
    Posts
    7
    Downloads
    0
    Uploads
    0

    Default dnc

    sory for this typing ignore . 1200 is true . and i can find these parameters in cimco :

    delay befor each line
    handshake timeout
    breack after receiving character

    are these useful for our problem ? and do you have any good suggest for adjust this parameter ?
    do you have any good software for dnc ?


    and say again tanke you for your help



  6. #6
    Registered
    Join Date
    Jan 2008
    Location
    iran
    Posts
    7
    Downloads
    0
    Uploads
    0

    Default dnc

    sory for this typing ignore . 1200 is true . and i can find these parameters in cimco :

    delay befor each line
    handshake timeout
    breack after receiving character

    are these useful for our problem ? and do you have any good suggest for adjust this parameter ?
    do you have any good software for dnc ?


    and say again tanke you for your help



  7. #7
    Registered
    Join Date
    Jan 2008
    Location
    iran
    Posts
    7
    Downloads
    0
    Uploads
    0

    Default

    sory for this typing ignore . 1200 is true . and i can find these parameters in cimco :

    delay befor each line
    handshake timeout
    breack after receiving character

    are these useful for our problem ? and do you have any good suggest for adjust this parameter ?
    do you have any good software for dnc ?


    and say again tanke you for your help



  8. #8
    Member dcoupar's Avatar
    Join Date
    Mar 2003
    Location
    USA
    Posts
    2932
    Downloads
    0
    Uploads
    0

    Default

    Delay Before Each Line sounds like the one. If it's not already, try setting that to 0.

    I'm confused... is your baud rate set to 1200 or 9600? If it's 1200, bump it up to 4800 or 9600. If it's 9600, bump it up to 19200. If your cable is good, and the handshaking is working properly, you shouldn't get overflows.



  9. #9
    Registered
    Join Date
    Feb 2007
    Location
    usa
    Posts
    498
    Downloads
    0
    Uploads
    0

    Default

    the 310 wont handle a rate higher than 9600,what is your computer?older one,sometimes this causes a dnc problem



  10. #10
    Registered
    Join Date
    Jan 2008
    Location
    iran
    Posts
    7
    Downloads
    0
    Uploads
    0

    Default dnc

    i have a same problem in richmond machine , in richmond my baudrate is 9600 & in meldos machine 1200 , and i use new labtop for dnc



  11. #11
    Member hutch07's Avatar
    Join Date
    Sep 2007
    Location
    usa
    Posts
    122
    Downloads
    0
    Uploads
    0

    Default handshake timeout

    Go to your Parameters - in/out screen and see what the handshake time out setting is. I know Mitsubishi lets you set this. Bump it up to 200 seconds to see if this helps. check out www.meau.com

    :rainfro:



  12. #12
    Member hutch07's Avatar
    Join Date
    Sep 2007
    Location
    usa
    Posts
    122
    Downloads
    0
    Uploads
    0

    Default My problem also.

    I am also looking for a good up-load/download program. I can not communicate with the Mitsubishi Meldas L3. I have gotten a few characters using some stuff but nothing usefull,



  13. #13
    Member dcoupar's Avatar
    Join Date
    Mar 2003
    Location
    USA
    Posts
    2932
    Downloads
    0
    Uploads
    0

    Default

    mostafabagheri,

    I checked the Cimco Edit V5 documentation, and the only thing I see that could slow the transmission is the Delay Before Each Line. Did you check to see if that's set that to 0 yet?



  14. #14
    Registered
    Join Date
    Jul 2005
    Location
    usa
    Posts
    409
    Downloads
    0
    Uploads
    0

    Default Mitsubishi up/download

    Hutch o7,
    I recently aquired 2 Machning centers with Mitsu MO controls. I use Hyperterm in windows for sending/receiving files. I am running that at 19.2 and with a 50 msec. line delay, it feeds faster error free than at 9600 with no line delay.
    I messed around for a while trying different settings until I got it right. If you are still having trouble let me know and I will send you the settings I use.

    Cutmore



  15. #15
    Rathinam1's Avatar
    Join Date
    Jan 2019
    Posts
    3
    Downloads
    0
    Uploads
    0

    Default

    Better you can use micro dnc unit for transferring the program, that will save the space and accurate data transfer



Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

mitsubishi meldos 310 - dnc problem

mitsubishi meldos 310 - dnc problem