    Default Matsuura on Low Power Supply

    Looking at a 1996 Matsuura MC-800VF, VMC

    The only problem is the transformer on the power pole is only 25kVa (single phase) and the machine is rated 37kVa in the book specs and 41kVa, 200-220V, 118A on the metal plate on the back of the machine. The transformer was installed 1.5 years ago with a subsidy, to upgrade would mean full cost which is out of budget.

    The RPC manufactures recommend a 40hp RPC for this machine.

    Is it possible to run a smaller RPC that would work with the 25kVa transformer? Can I just run the machine at a reduced rpm/rapids/feed etc and get away with it? Can the machine/control be damaged if it goes over the available power?

    the reason I'm asking is I put some money down without checking the transformer, assuming it was sized for multiple residences, which it's not. Otherwise I would just go to a smaller machine. But this one is low hours, a good price, and has a large envelope, plus I would lose the money down.

    I'm not cutting Inconel at max rapids/feed. Mostly aluminum low volume prototyping.

    Similar Threads:


  2. #2
    Member
    Join Date
    Jan 2013
    Location
    USA
    Posts
    128
    Downloads
    0
    Uploads
    0

    Default Re: Matsuura on Low Power Supply

    So this leads to another question. Cart before the horse scenario.

    Working from the other direction, fitting the machine to the existing available power. With a 25kVa transformer and 200 amp residential service, what is the largest maximum RPC that you could run?



  3. #3
    Community Moderator Jim Dawson's Avatar
    Join Date
    Dec 2013
    Posts
    5717
    Downloads
    0
    Uploads
    0

    Default Re: Matsuura on Low Power Supply

    Chris, you're correct, you have to start with the available power. That really sounds like too much machine for a residential service. The spindle HP is the controlling factor, and the RPC need to be sized to run the spindle. I have 100 amps, 240V, single phase available to my shop. So I limited the mill spindle HP to 7.5 running on single phase, and the lathe to 10 HP running on a 15HP RPC. You have to have enough power left over to run lighting, air compressor and other stuff.

    Jim Dawson
    Sandy, Oregon, USA


Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

Matsuura on Low Power Supply

Matsuura on Low Power Supply