Problem G540 and E-Stop


Results 1 to 6 of 6

Thread: G540 and E-Stop

  1. #1
    Registered
    Join Date
    Jul 2010
    Location
    United States
    Posts
    79
    Downloads
    0
    Uploads
    0

    Default G540 and E-Stop

    Being an electronics novice I bought a pre-built, pre-wired CNC Controller box with a Gecko G540 from Keling. Nothing worked and the Fault light would not go off until I pushed in the E-Stop button, then everything works fine. When I opened up the case put a meter on the switch I discovered it's wired so it's normally open when the button is in the out position and closed when the button is in the in, latched position. Is this backwards? Shouldn't it be wired normally closed?

    Similar Threads:


  2. #2
    Member
    Join Date
    Jul 2007
    Location
    Canada
    Posts
    1602
    Downloads
    5
    Uploads
    0

    Default

    It sounds like your switch is mis-wired. The e-stop circuit should be closed that way a wire break will trigger an e-stop rather than disable the e-stop circuit.

    If they are using the same switch I bought from them, it is a simple matter to rewire it to NC. It sounds like someone made a mistake assembling it.

    bob



  3. #3
    Member
    Join Date
    Mar 2018
    Location
    United States
    Posts
    16
    Downloads
    0
    Uploads
    0

    Default Re: G540 and E-Stop

    E stop question. Just winding up a case build using GS 540. Do I wire the E stop from the Negative - side of the PS to the E stop and then to pin 10 on the GS 540?



  4. #4

    Default Re: G540 and E-Stop

    Pin 10 and 12 will be connected when the e-stop is not pressed.

    How you do that is up to you. I believe you could connect pin 12 to the PSU and then connect the estop to 10 and then PSU v- and it would work.



  5. #5
    Member john-100's Avatar
    Join Date
    Mar 2007
    Location
    uk
    Posts
    2083
    Downloads
    0
    Uploads
    0

    Default Re: G540 and E-Stop

    from the G540 manual

    G540 and E-Stop-g540-e-stop-power-supply-wiring-jpg

    PDF manual
    G540 REV8 Manual.pdf

    John



  6. #6
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    24220
    Downloads
    0
    Uploads
    0

    Default Re: G540 and E-Stop

    Strictly speaking the G540 is not sufficient in itself to operate a legitimate E-Stop, regulations state that all motor power should be removed or turned off, this requires hard wiring and a dedicated relay to remove all power, the input to the controller can be used to advise an e-stop has taken place, but not be the primary source for it.
    e.g Contacts on the E-Stop relay can be used in place of the G540 P.B.
    Al.

    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

G540 and E-Stop

G540 and E-Stop