    Question Error 439 overvoltage DC circuit

    Good to all, first introduce myself, I am dedicated to the programming of PLC's and industrial instrumentation, I also perform maintenance of CNC machines.

    I have a SERVO AMPLIFIER BiSVSP equipment, Model A06B-6164-H344, with error on screen "439 overvoltage DC circuit", on the servo display I see the red LED error indicator on and the code 73.

    The equipment has an autotransformer at the input, and its voltages are approximately 210VAC, if I disconnect the input and feed the control board with 24VDC the error still appears.

    I think that may be damaged the LM339 integrated LM339 that carries the control board but I'm not sure yet, before doing anything I would like to know if anyone has had this error or if you can help me in something.

    Greetings to all!

    Similar Threads:
    Attached Thumbnails Attached Thumbnails Error 439 overvoltage DC circuit-img_20221103_184403-jpg   Error 439 overvoltage DC circuit-img_20221103_184434-jpg  


  2. #2
    Member
    Join Date
    Jan 2013
    Location
    england
    Posts
    474
    Downloads
    0
    Uploads
    0

    Default

    Quote Originally Posted by bismael View Post
    Good to all, first introduce myself, I am dedicated to the programming of PLC's and industrial instrumentation, I also perform maintenance of CNC machines.

    I have a SERVO AMPLIFIER BiSVSP equipment, Model A06B-6164-H344, with error on screen "439 overvoltage DC circuit", on the servo display I see the red LED error indicator on and the code 73.

    The equipment has an autotransformer at the input, and its voltages are approximately 210VAC, if I disconnect the input and feed the control board with 24VDC the error still appears.

    I think that may be damaged the LM339 integrated LM339 that carries the control board but I'm not sure yet, before doing anything I would like to know if anyone has had this error or if you can help me in something.

    Greetings to all!
    The DC link voltage are the DC bus straps across the drives. Power off, allow PSU time to discharge
    And disconnect the DC link from the amplifiers then power on to see if error is still there.
    Is the red led still on.
    Suspect PSU.



  3. #3
    Member
    Join Date
    Dec 2009
    Location
    ROMANIA
    Posts
    952
    Downloads
    0
    Uploads
    0

    Default Re: Error 439 overvoltage DC circuit

    The alarm 73 is on the spindle side and say that the motor sensor is disconnected,maybe the cable is not fit corectly on JY2/JY4
    The 439 alarm indeed is from the power supply



  4. #4
    Member bismael's Avatar
    Join Date
    Jan 2023
    Posts
    3
    Downloads
    0
    Uploads
    0

    Default Re: Error 439 overvoltage DC circuit

    what`s voltage must be present in the DC bus power?



  5. #5
    Member
    Join Date
    Jan 2013
    Location
    england
    Posts
    474
    Downloads
    0
    Uploads
    0

    Default

    Quote Originally Posted by bismael View Post
    what`s voltage must be present in the DC bus power?
    Depends on the system, but could be 600vdc. Check the manufacturer information.

    Supply voltages determine the DC bus voltage.



  6. #6
    Member
    Join Date
    Dec 2009
    Location
    ROMANIA
    Posts
    952
    Downloads
    0
    Uploads
    0

    Default Re: Error 439 overvoltage DC circuit

    hm 600vdc????
    from your drive picture the input is 200-240 V AC that means the DC LINK will be between 283-325V DC
    On the right low side of the combo beta drive you will find 2 terminals named TB1 TB2 where you can measure the DC LINK voltage

    if the drive have 400-440 V AC input indeed the DC LINK will be 565-679 V DC



  7. #7
    Member
    Join Date
    Jan 2013
    Location
    england
    Posts
    474
    Downloads
    0
    Uploads
    0

    Default

    Quote Originally Posted by zavateandu View Post
    hm 600vdc????
    from your drive picture the input is 200-240 V AC that means the DC LINK will be between 283-325V DC
    On the right low side of the combo beta drive you will find 2 terminals named TB1 TB2 where you can measure the DC LINK voltage

    if the drive have 400-440 V AC input indeed the DC LINK will be 565-679 V DC
    Yes indeed, I know. 240vac has 660v peak to peak.
    220vac around 600v.

    I did say, consult the manufacturer information because it depends what transformer is connected from the mains to to drives PSU.



  8. #8
    Member bismael's Avatar
    Join Date
    Jan 2023
    Posts
    3
    Downloads
    0
    Uploads
    0

    Default

    Quote Originally Posted by servtech View Post
    Yes indeed, I know. 240vac has 660v peak to peak.
    220vac around 600v.

    I did say, consult the manufacturer information because it depends what transformer is connected from the mains to to drives PSU.
    I have 226vac at the input but when I measure at TB1-TB2 I have 380vdc and in 1 second it disconnects the magnetic contact.



  9. #9
    Member
    Join Date
    Dec 2009
    Location
    ROMANIA
    Posts
    952
    Downloads
    0
    Uploads
    0

    Default Re: Error 439 overvoltage DC circuit

    so your DC LINK from the power supply section is overvoltage indeed
    you need to repair or change the A20B-2102-0301



Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

Error 439 overvoltage DC circuit

Error 439 overvoltage DC circuit