    Exclamation Coolant and Blow air issue in VMC -Fanuc oi

    Hello all,

    I have worked a few years in maintenance, but I faced a technical problem in milling machine VMC-Fanuc-oi, which is the "Blow air and Coolant" not working, I checked the keeprelays but the button in manual still not working. what is a parameter for coolant and blow air? any help !

    mus

    Similar Threads:


  2. #2
    Member
    Join Date
    Jun 2021
    Posts
    25
    Downloads
    0
    Uploads
    0

    Default

    Quote Originally Posted by DrMustafa View Post
    Hello all,

    I have worked a few years in maintenance, but I faced a technical problem in milling machine VMC-Fanuc-oi, which is the "Blow air and Coolant" not working, I checked the keeprelays but the button in manual still not working. what is a parameter for coolant and blow air? any help !

    mus
    Start by looking in the wiring diagram of the machine. Find the signal address for that button and then watch the ladder or signal status page to see if the contact/address is changing when you physically press the button.

    If the button works, you’ll have to look into the ladder logic to see what is/isn’t turning on/off and is preventing it

    Last edited by bumzag; 12-10-2021 at 09:20 AM.


  3. #3
    Member DrMustafa's Avatar
    Join Date
    Feb 2020
    Posts
    2
    Downloads
    0
    Uploads
    0

    Default Re: Coolant and Blow air issue in VMC -Fanuc oi

    actually , I am not into ladder programming, is there a parameter number for the coolant and blow air?



  4. #4
    Member
    Join Date
    Jun 2021
    Posts
    25
    Downloads
    0
    Uploads
    0

    Default

    Quote Originally Posted by DrMustafa View Post
    actually , I am not into ladder programming, is there a parameter number for the coolant and blow air?
    There won’t be a CNC parameter for “coolant and blow air” but there probably will be a PMC parameter for it in the form of a keep relay, timer, counter, etc. Those PMC parameters are used by the ladder so no matter what, you have to work out the logic for the coolant and blow air in order to figure out why it isn’t turning on or how to bypass it.



Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

Coolant and Blow air issue in VMC -Fanuc oi

Coolant and Blow air issue in VMC -Fanuc oi