    Default Alarm messages

    Good morning,
    Some alarms have come up on our doosan S700 and i am struggling to find any information about them and unsure how these can be resolved.

    Its not allowing me to attach images to this forum but i will list the alarms below:

    *1006 CP/Q1 OFF ALARM
    *950 PMC SYSTEM ALARM
    *07 DATA NOT FOUND

    If anyone can help at all i will be very greatful.

    Thanks

    Similar Threads:


  2. #2
    Member Michael82's Avatar
    Join Date
    Nov 2007
    Location
    usa
    Posts
    361
    Downloads
    0
    Uploads
    0

    Default Re: Alarm messages

    at first glance, there is a problem with your spindle amplifier. Error 1006 is very likely an error that is output from the PMC, which sets signal G8.4 to "0", which results in an EMERGENCY STOP / EMG. As a result, the hydraulic system does not start up and the axes cannot be moved



  3. #3
    Member DannyGR's Avatar
    Join Date
    Nov 2021
    Posts
    3
    Downloads
    0
    Uploads
    0

    Default

    Quote Originally Posted by Michael82 View Post
    at first glance, there is a problem with your spindle amplifier. Error 1006 is very likely an error that is output from the PMC, which sets signal G8.4 to "0", which results in an EMERGENCY STOP / EMG. As a result, the hydraulic system does not start up and the axes cannot be moved
    Thanks for the reply and i have just read that in a book but it doesn't explain how to fix this issue, do you know of anyway of doing so?

    Thanks



  4. #4
    Member freakycnc's Avatar
    Join Date
    Apr 2012
    Location
    USA
    Posts
    85
    Downloads
    0
    Uploads
    0

    Default Re: Alarm messages

    The 950 means something is wrong with the PMC.
    Go to SYSTEM/PMC MAINT/PMC ALARM to get details.
    More than likely with the weird alarms that something is wrong with the I/O communication ie: ER97



  5. #5
    Member DannyGR's Avatar
    Join Date
    Nov 2021
    Posts
    3
    Downloads
    0
    Uploads
    0

    Default

    Quote Originally Posted by freakycnc View Post
    The 950 means something is wrong with the PMC.
    Go to SYSTEM/PMC MAINT/PMC ALARM to get details.
    More than likely with the weird alarms that something is wrong with the I/O communication ie: ER97
    Thanks for the reply we noticed that one of the three io boards was not lit up and replaced the fuse and blew straight away so we are waiting on some more fuses to arrive and we are going to see if the board needs replacing pr there is a short some where along the line,

    Thanks



Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  