Hi all,
I have been getting a 414 x axis detect error alarm on my Yang ML25 lathe becoming more frequent over the last few months. When it happens it goes to a 'not ready' state and no alarm shows on the drive board. Diagnostic 720 shows an overcurrent state. It only happens in rapid travel on 100%, not 25 or 50%. I have replaced the X axis bearings as they were getting a little noisy but this made no difference. I have now replaced the motor, encoder and drive board which has made no difference. The brake is working as it should and I've tested all the cabling and no faults are showing. Yesterday I stripped the bearings back out and checked them as well as the ball screw. Everything is working smoothly with no tight spots.
I really am at a loss as to what to try next as I am running out of parts to change!
I wondered if anyone else had seen this fault and found a solution before I resort to calling Fanuc out to take a look ££££!
I don't have a Fluke 87, but both an inexpensive insulation resistance tester and inexpensive multimeter with much of the same functionality as a Fluke 87. My multimeter seems to be accurate enough at detecting leakage below 50 Megaohms. and the IR tester below 200 Megaohms.
With the motor cable plugged into the motor, but unplugged from the servo amplifier, test the resistance between any of the U,V,W and Ground cables. If your multimeter is anything similar to mine or a Fluke 87 and it gives you a reading under 50 Megaohms, that may indicate the cables are toast.