    Angry Fanuc O-md Lube Time Alarm!!!!

    I have two Hardinge VMC1000II's.
    They were built in sept of 2000 and have the Fanuc OM-D controller.

    Here is my problem......

    The lube timer always seems to run out when I am drip feeding programs and running "Lights Out", and always runs out right in the middle of a tool change (carousel over to spindle, etc...) Anyways this ends up costing me up to 12hrs of machining time. Is there any way I can turn off the lube timer? Or a way I could reset the timer? I need to solve this problem, there must be a way to shut it off or reset it in the parameters. It seems like it shouldn't alarm out until it finishes the program, not the current tool. I had it running a 8 tool program last night, and when I got there this morning it had alarmed out when tool 2 was done and it was going to get tool 3. If it wouldn't have alarmed out it would be done, now it won't be till tomorrow!!!!

    Someone please Help!!!

    Thanks

    Similar Threads:


  2. #2
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    24221
    Downloads
    0
    Uploads
    0

    Default

    It seems like poor programming by whoever wrote the ladder, normally I would, as you say, monitor the end of cycle start sequence until end of program and then disallow any further program start until the alarm was reset.
    Depending on how it was done, you may have to get the ladder modified, unless you can fool it by other means, Some lube systems will set a timer to run and if the lube pressure is not made withing that time then it will alarm.
    A way to defeat this one may be to put an overide switch across the P.S. while unattended, but this is open to forgetting to open the switch again.
    A study of the ladder may be needed to work something out.
    Al.

    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  3. #3
    Registered
    Join Date
    Apr 2007
    Location
    USA
    Posts
    14
    Downloads
    0
    Uploads
    0

    Default

    Quote Originally Posted by Al_The_Man View Post
    It seems like poor programming by whoever wrote the ladder, normally I would, as you say, monitor the end of cycle start sequence until end of program and then disallow any further program start until the alarm was reset.
    Depending on how it was done, you may have to get the ladder modified, unless you can fool it by other means, Some lube systems will set a timer to run and if the lube pressure is not made withing that time then it will alarm.
    A way to defeat this one may be to put an overide switch across the P.S. while unattended, but this is open to forgetting to open the switch again.
    A study of the ladder may be needed to work something out.
    Al.
    I want to override the alarm, or disable it. I will keep a maintence log for greasing. How do I disable or override this alarm?



  4. #4
    Registered
    Join Date
    Feb 2007
    Location
    United States
    Posts
    38
    Downloads
    0
    Uploads
    0

    Default

    If you have a description of the PMC parameters try to find the timer that controls the lube time. It should be in your diagnostic settings not the parameters. They will start around DGN 300. One DGN will control the timer if you are monitoring it and keeping a maintenance log then put a maximum value in the DGN for the timer and it shouldn't alarm out.
    There could also be a keep relay for the option to totally turn it off but once again you need the machine tool builder's PMC parameters (DGN) descriptions to know which one.



  5. #5
    Registered
    Join Date
    Apr 2007
    Location
    USA
    Posts
    14
    Downloads
    0
    Uploads
    0

    Default

    Quote Originally Posted by not an expert View Post
    If you have a description of the PMC parameters try to find the timer that controls the lube time. It should be in your diagnostic settings not the parameters. They will start around DGN 300. One DGN will control the timer if you are monitoring it and keeping a maintenance log then put a maximum value in the DGN for the timer and it shouldn't alarm out.
    There could also be a keep relay for the option to totally turn it off but once again you need the machine tool builder's PMC parameters (DGN) descriptions to know which one.
    I take a look at all my manuals hopefully I can find the pmc parameters, if not I guess I will have to call Hardinge and maybe they could tell me how to turn it off.

    Also if I do find out which DGN it is do I need turn on PWE to change it?



  6. #6
    Registered
    Join Date
    Feb 2007
    Location
    United States
    Posts
    38
    Downloads
    0
    Uploads
    0

    Default

    Yes turn on PWE, MDI mode. If that doesn't work depress the E-stop (still with PWE on) and it should change for you.



  7. #7
    Registered Kittisak's Avatar
    Join Date
    Sep 2018
    Posts
    1
    Downloads
    0
    Uploads
    0

    Default Re: Fanuc O-md Lube Time Alarm!!!!

    Fanuc 0-T AL lubricant insufficient
    Ladder (Edit Ladder modify)how to do



Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

Fanuc O-md Lube Time Alarm!!!!

Fanuc O-md Lube Time Alarm!!!!