Need Help! Amplifier fault on X-axis


Results 1 to 3 of 3

Thread: Amplifier fault on X-axis

  1. #1
    Member
    Join Date
    Jun 2006
    Location
    U.S.A
    Posts
    240
    Downloads
    0
    Uploads
    0

    Default Amplifier fault on X-axis

    This all started a couple weeks ago with a relatively warm day.

    My 1993 VMC20 tends to overheat when the temperature approaches 80°. It will restart the computer. I forget what the error message would say. I would just open the back side cabinet and let it cool off for half an hour or so.

    On this particular day, I ran it with the cabinet open and a fan blowing into it. Toward the end of the day, it stalled and gave me Error #16 Resolver fault. I checked the resolver and was getting no voltage. I found that the motor bearings were shot, so I ordered a reman motor with reman resolver on it. Installed it today, but got a strange squeal from the amplifier area of the cabinet and an error message showing an x-axis amplifier fault. I reset it over and over and over to see if it was just the process of the mill adjusting to the new motor. The message kept coming back. The 1st and 3rd LEDs light up on the amp board too.

    So I switched the x and y axis amplifiers as suggested by tech support. The error stayed on the x-axis and the LEDs lit up the same. I switched them back.

    Then I pulled the new resolver and installed it on the old motor. Same error.

    Then I pulled a resolver from my VMC 4020 and installed it on the old motor. Same error.

    I should note that it is possible sometimes to jog the x-axis motor slightly. It seems to begin to work if I leave the mill on before disengaging the emergency stop. Sometimes it will not throw the error right away. I jog it about .050" with the pendant wheel and then it throws the same x-axis amplifier fault code.

    Stumped and frustrated.

    Similar Threads:


  2. #2
    Member
    Join Date
    Jun 2006
    Location
    U.S.A
    Posts
    240
    Downloads
    0
    Uploads
    0

    Default

    So the problem was that I didn't realize that the red and black armature wires coming from the machine are shielded. You have to strip the red or black rubber insulation and the braided silver wire sheath away from the white plastic about 7/8" and then strip down to the copper wire 3/8" to insert into the connector.



  3. #3
    Member
    Join Date
    Sep 2017
    Location
    United States
    Posts
    143
    Downloads
    0
    Uploads
    0

    Default

    I ran into same issue on 4020 after rebuilding my x axis servo, regluing magnets, swapping tach, etc.., didn’t strip the shielded cable back far enough and a little solder dripped down and made contact. Thankfully these machines are durable to not fry out when you over look something so simple. When I look at all the last fadal issues they definitely have a commonality between all of the machines.

    Quote Originally Posted by Fadal Error View Post
    So the problem was that I didn't realize that the red and black armature wires coming from the machine are shielded. You have to strip the red or black rubber insulation and the braided silver wire sheath away from the white plastic about 7/8" and then strip down to the copper wire 3/8" to insert into the connector.




Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

Amplifier fault on X-axis

Amplifier fault on X-axis