Need Help! Acramatic 850sx SIBA 1 Error 00268


Results 1 to 6 of 6

Thread: Acramatic 850sx SIBA 1 Error 00268

  1. #1
    Member SlickPimp's Avatar
    Join Date
    Oct 2020
    Posts
    1
    Downloads
    0
    Uploads
    0

    Default Acramatic 850sx SIBA 1 Error 00268

    Hello,
    I have recently purchased a used Cincinnati Milacron 20vc - 2000, it was a fire sale and i knew i would have some issues to deal with. Im not proficient in working on control issues with these machines but i always take a stab at it before i call in a tech to work on it. I powered up the machine , host control initializes just fine. When i press the master start key the hydraulics fire up for a second and then i get an alarm. SIBA 1 error alarm # 00268. I have scoured the manuals and wiring schematics for hours and i cannot find a single piece of information about the alarm or the module itself. I see a NIBA module next to the I/O modules on the rack but again for some reason its not in the manuals or the schematics. Has anybody had this error before or is anyone able to shed some light on what SIBA or NIBA means and what it does. Any information would be greatly appreciated .
    Thanks,
    Trevor.

    Similar Threads:


  2. #2
    Member
    Join Date
    Mar 2011
    Location
    USA
    Posts
    463
    Downloads
    0
    Uploads
    0

    Default Re: Acramatic 850sx SIBA 1 Error 00268

    The 850SX MIA Rack would have a SIBA (Serial Interface Bus Adapter) or NIBA board right next to the power supply but not both.

    On the 850SX, Alert Code 00268 indicates -
    No I/O Racks connected
    Cause: No SIBAs are connected via HSSL to the PCA in its set time
    Correction: Check High speed serial link connections, Replace SIBA(s)

    What you are seeing could be as simple as an HSSL cable that has come loose - is the serial link cable plugged into your NIBA Board and your PCA?



  3. #3
    Member Davemartinez's Avatar
    Join Date
    Sep 2021
    Posts
    16
    Downloads
    1
    Uploads
    0

    Default

    Quote Originally Posted by SlickPimp View Post
    Hello,
    I have recently purchased a used Cincinnati Milacron 20vc - 2000, it was a fire sale and i knew i would have some issues to deal with. Im not proficient in working on control issues with these machines but i always take a stab at it before i call in a tech to work on it. I powered up the machine , host control initializes just fine. When i press the master start key the hydraulics fire up for a second and then i get an alarm. SIBA 1 error alarm # 00268. I have scoured the manuals and wiring schematics for hours and i cannot find a single piece of information about the alarm or the module itself. I see a NIBA module next to the I/O modules on the rack but again for some reason its not in the manuals or the schematics. Has anybody had this error before or is anyone able to shed some light on what SIBA or NIBA means and what it does. Any information would be greatly appreciated .
    Thanks,
    Trevor.
    Hi were you able to solve the problem, i have the same type of alarm on my saber 1000 1995 , regards



  4. #4
    Member Rotech's Avatar
    Join Date
    Jul 2022
    Posts
    8
    Downloads
    0
    Uploads
    0

    Default Re: Acramatic 850sx SIBA 1 Error 00268

    Check your power supply. Make sure you're getting power to all the boards



  5. #5
    Member Davemartinez's Avatar
    Join Date
    Sep 2021
    Posts
    16
    Downloads
    1
    Uploads
    0

    Default

    Quote Originally Posted by Rotech View Post
    Check your power supply. Make sure you're getting power to all the boards
    hello, as seen in the images, 2 of the cards in the I/O do not turn on. I will check the power supply. Thank you!

    Attached Thumbnails Attached Thumbnails Acramatic 850sx SIBA 1 Error 00268-screenshot_2022-07-29-00-29-09-133_com   Acramatic 850sx SIBA 1 Error 00268-screenshot_2022-07-29-00-29-18-076_com   Acramatic 850sx SIBA 1 Error 00268-screenshot_2022-07-29-00-30-29-721_com   Acramatic 850sx SIBA 1 Error 00268-screenshot_2022-07-29-00-31-35-789_com  

    Acramatic 850sx SIBA 1 Error 00268-screenshot_2022-07-29-00-31-03-140_com  


  6. #6
    Member
    Join Date
    Mar 2011
    Location
    USA
    Posts
    463
    Downloads
    0
    Uploads
    0

    Default

    Quote Originally Posted by Davemartinez View Post
    hello, as seen in the images, 2 of the cards in the I/O do not turn on. I will check the power supply. Thank you!
    The cards you mention not "turning on" are output cards. If the control is not loading properly i wouldn’t expect the outputs to turn on (i.e. would you want the hydraulics to turn on if it is not safe to do so?).
    If you have the same alarm as the OP, it is based on communication failure with the SIBA board, you should start with identifying why they are not communicating.



  7. #7
    Member Davemartinez's Avatar
    Join Date
    Sep 2021
    Posts
    16
    Downloads
    1
    Uploads
    0

    Default Re: Acramatic 850sx SIBA 1 Error 00268

    Thanks maver1ck , i Will check tomorrow morning .

    ????



Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

Acramatic 850sx SIBA 1 Error 00268

Acramatic 850sx SIBA 1 Error 00268