Originally Posted by
jaideepshinh
You would need to check the bus voltage on the main power supply- the Error 14 shows that its either too high or too low. If this bus voltage is normal, there could be an issue between the input terminals (where the bus connects) and the Drive PCB inside (i had this issue on a Simodrive 611 where i kept on getting alarms due to a slightly burnt DC link connection on one of the drives. Cleaned, soldered direct to the PCB with removal bolts and its working fine since)
When you remove emergency, are you able to move the other axes? I am assuming you are unable to because the Spindle drive would directly give the alarm regarding the voltage
Err 83- I am not sure what this is. If i remember correctly its a wrong command input to the drive by the user, and this may not be the cause of your problem
Best of luck and keep us posted!