Help..Stuck at relay ext dc voltage missing but dc voltage OK ?


Page 1 of 2 12 LastLast
Results 1 to 20 of 26

Thread: Help..Stuck at relay ext dc voltage missing but dc voltage OK ?

  1. #1
    Member
    Join Date
    Sep 2007
    Location
    Canada
    Posts
    69
    Downloads
    0
    Uploads
    0

    Default Help..Stuck at relay ext dc voltage missing but dc voltage OK ?

    I have a series 2 interact 2. I have rebuilt the failed dc voltage regulator. I now have both the unregulated 29-30 volts dc and the 24 volts regulated....but the dang MDI control (Heidenhain 151) is still not happy and wont let me past this error message....what am I missing....please list any thoughts you have on what would cause this error prompt if not the regulator.

    Similar Threads:


  2. #2
    Member
    Join Date
    Jan 2005
    Location
    us
    Posts
    1121
    Downloads
    0
    Uploads
    0

    Default re

    follow the emo string



  3. #3
    Member
    Join Date
    Sep 2007
    Location
    Canada
    Posts
    69
    Downloads
    0
    Uploads
    0

    Default

    Ya Thanks gus......where would I find that piece of string and what color is it ??? 8-O........LoL......Unfortunately I don"t have a flow chart for the emergency
    off circuit.......so I am not fully certain that I have tested all the components on the circuit.....all the limits are of course obvious. But I am not certain of all the other checks this control does yet.....oil...air pressure....etc.....I gotta be overlooking one somewhere...........common Gus........ you said this would be easy......8-)



  4. #4
    Member
    Join Date
    May 2004
    Location
    United Kingdom
    Posts
    402
    Downloads
    0
    Uploads
    0

    Default

    Did the 24v DC fail in a mode that put significantly higher, or maybe AC, volts onto the TNC - if so has the 24v input on the TNC let the magic smoke out?

    Andrew Mawson
    East Sussex, UK


  5. #5
    Member
    Join Date
    Jan 2005
    Location
    us
    Posts
    1121
    Downloads
    0
    Uploads
    0

    Default

    It's right there on the wiring diagram.

    I'm sorry, but a 24v issue is pretty easy to trace



  6. #6
    Member
    Join Date
    Jan 2005
    Location
    us
    Posts
    1121
    Downloads
    0
    Uploads
    0

    Default

    vertical line "11" on the diagram. the power enable button bypasses some of it. look for 24 volts at every single point.

    respond AFTER you have done that



  7. #7
    Moderator
    Join Date
    Nov 2004
    Location
    USA
    Posts
    3028
    Downloads
    0
    Uploads
    0

    Default

    Just in case, I found a scan of the wiring.

    George

    Attached Thumbnails Attached Thumbnails Help..Stuck at relay ext dc voltage missing but dc voltage OK ?-int2-s2-tnc151-wiring-pdf  
    (Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management)


  8. #8
    Registered
    Join Date
    Nov 2006
    Location
    Scotland
    Posts
    925
    Downloads
    0
    Uploads
    0

    Default

    According to George`s PDF the e-stop line is 110v.Nice clear drawing that, better than the one in the book.
    Mark.



  9. #9
    Member
    Join Date
    Jan 2005
    Location
    us
    Posts
    1121
    Downloads
    0
    Uploads
    0

    Default re

    Nope 24V



  10. #10
    Registered
    Join Date
    Nov 2006
    Location
    Scotland
    Posts
    925
    Downloads
    0
    Uploads
    0

    Default

    Gus
    Going by the schematic that George posted the E-stop buttons are quite clearly 110v



  11. #11
    Member
    Join Date
    Sep 2007
    Location
    Canada
    Posts
    69
    Downloads
    0
    Uploads
    0

    Default Aaarrrrggggggg

    Quote Originally Posted by gus View Post
    It's right there on the wiring diagram.

    I'm sorry, but a 24v issue is pretty easy to trace
    GUS...BUDDYYY >>>PALLLL I cant read the schematic ? I can not see the text, it is too low a res....remember you were going to send me a hi res copy ???.....I dont have a manual for this machine...I do not have a "readable" copy of the dc circuit............and sadly if it is as easy as you imply....the MDI dc voltage sensing circuit is cooked...remember I dont know why they chopped this machine up....



  12. #12
    Member
    Join Date
    Sep 2007
    Location
    Canada
    Posts
    69
    Downloads
    0
    Uploads
    0

    Default

    THANKS GEORGE this is the first bridgeport schematic I have been able to actually READ......yay THANK YOU>>>>>



  13. #13
    Member
    Join Date
    Sep 2007
    Location
    Canada
    Posts
    69
    Downloads
    0
    Uploads
    0

    Default

    Another point guys.....dont forget where I am...eh...CANADA........this is a 600 volt machine.....so I still do not have a fully accurate diagram.....I have found circuits on my mill that do NOT appear in ANY schematic I have seen so far...including the most recent sent by George "machintek"



  14. #14
    Member
    Join Date
    Sep 2007
    Location
    Canada
    Posts
    69
    Downloads
    0
    Uploads
    0

    Default Line 11 ?????????????????????

    Quote Originally Posted by gus View Post
    vertical line "11" on the diagram. the power enable button bypasses some of it. look for 24 volts at every single point.

    respond AFTER you have done that
    Gus.....please tell me you mean line 116. Line 116 Unregulated 30v dc to various switches AND to regulator........Line 90 from reg to ground.....and line 65 from regulator with 24v dc to MDI unit ?



  15. #15
    Registered
    Join Date
    Nov 2006
    Location
    Scotland
    Posts
    925
    Downloads
    0
    Uploads
    0

    Default

    Dirky,here`s a link to the service manual for the 151.I notice the inputs are protected by what Heid call fuse resistors.Worth a look at.

    http://filebase.heidenhain.de/doku/o...b/sa151155.pdf

    Mark.



  16. #16
    Member
    Join Date
    Jan 2005
    Location
    us
    Posts
    1121
    Downloads
    0
    Uploads
    0

    Default

    I was mistaken Gridley, it is in fact 110, nonetheless it is where he must start to find the lost 24v.



  17. #17
    Member
    Join Date
    Sep 2007
    Location
    Canada
    Posts
    69
    Downloads
    0
    Uploads
    0

    Default

    Thanks for the link Mark....Yes I see that...they have many of the cicuits protected with a 47ohm fuse/resistor.....this is exactly what I expect to find....



  18. #18
    Member
    Join Date
    Sep 2007
    Location
    Canada
    Posts
    69
    Downloads
    0
    Uploads
    0

    Default respond AFTER you have done that[/QUOTE]

    Quote Originally Posted by gus View Post
    vertical line "11" on the diagram. the power enable button bypasses some of it. look for 24 volts at every single point.

    respond AFTER you have done that
    OUCH kaboom smokin meter....hows that for a response.



  19. #19
    Member
    Join Date
    Sep 2007
    Location
    Canada
    Posts
    69
    Downloads
    0
    Uploads
    0

    Default

    just screwin around Gus.....thanks for the heads up
    I will look into all the points on that circuit soon as Im home....



  20. #20
    Registered
    Join Date
    Nov 2006
    Location
    Scotland
    Posts
    925
    Downloads
    0
    Uploads
    0

    Default

    Dirky,
    vertical line 11 on the drawing is 110 volts.When you get to the stage of having the "ext 24v missing" message is 2CR and 10CR energised?
    10CR coil is energised with 24v dc and 2CR is 110v ac.
    Provided the e-stop buttons are out,the oil level switch is made and the fuse on the 110v line and the fuses supplying the transformer are ok 2CR should be energised.
    CR10 needs 24v dc from the TNC to energise it.
    Can you check this?
    Mark.



Page 1 of 2 12 LastLast

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

Help..Stuck at relay ext dc voltage missing but dc voltage OK ?

Help..Stuck at relay ext dc voltage missing but dc voltage OK ?