    Thanks Mark....if i followed Gus,s advice I would be in flames right now...tee..heee.heee 8-)......just jokin Gus.....Well guys...here it is....found the fault....It was in the heidenhain control itself.....One of the resistor-fuses that are used to protesct the control circuits was burnt "open".....replaced it...and now that all the other things are repaired....ITS ALIVE!!!!



  2. #22
    Member
    Join Date
    May 2004
    Location
    United Kingdom
    Posts
    402
    Downloads
    0
    Uploads
    0

    Default

    Glad you are now working at last. I do recall saying quite some while back:

    "Did the 24v DC fail in a mode that put significantly higher, or maybe AC, volts onto the TNC - if so has the 24v input on the TNC let the magic smoke out?"

    Andrew Mawson
    East Sussex, UK


  3. #23
    Member
    Join Date
    Sep 2007
    Location
    Canada
    Posts
    69
    Downloads
    0
    Uploads
    0

    Default

    you certainly did look at that post or your pm messages...I replied to it and thanked you for the direction



  4. #24
    Registered
    Join Date
    Nov 2007
    Location
    USA
    Posts
    6
    Downloads
    0
    Uploads
    0

    Default voltage

    Did you ever figure this problem out?



  5. #25
    Member
    Join Date
    Sep 2007
    Location
    Canada
    Posts
    69
    Downloads
    0
    Uploads
    0

    Default

    Yes I did...with the help of my huge brain.....no...seriously.....with the help of all the folks here. How can I help you ?



  6. #26
    Member moto-guy93's Avatar
    Join Date
    May 2021
    Posts
    6
    Downloads
    0
    Uploads
    0

    Default Re: Help..Stuck at relay ext dc voltage missing but dc voltage OK ?

    I have the same problem on a tnc 145 i cant find diagrams for it though, any idea where these resistor-fuses are found?



  7. #27
    Member moto-guy93's Avatar
    Join Date
    May 2021
    Posts
    6
    Downloads
    0
    Uploads
    0

    Talking Re: Help..Stuck at relay ext dc voltage missing but dc voltage OK ?

    Found it all on my own!
    Resistor next to J1/8 blown although didn't look black meter caught it.
    all working!



Page 2 of 2 FirstFirst 12

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

Help..Stuck at relay ext dc voltage missing but dc voltage OK ?

Help..Stuck at relay ext dc voltage missing but dc voltage OK ?